    Water temp

    Hope someone can help me, Have a customer in which they have about 15 water source heat pumps on a water loop with no boiler to heat the water. Water is fed and cooled from a tower and holding pond and also serves to cool many other water cooled machinery. Now the return water tempature from the entire loop varies depending on the # of differant equipment it is currently serving and outside air temp. Supply Water temp is recorded sometimes as low as 39 dg. during shutdowns.

    So obviously I am having problems with freeze protection lockouts (carrier RHR060 units) when the water gets cold and units running in heat. Any suggetions ?(besides adding a boiler)

    Also,water has no additives for freeze protection.

  2. #2
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    if you have dedicated WC units that aren't HPs and cooling only....refer boxes ,straight cooling units 24/7 that is your only SOURCE of HEAT.work the tower fan if you have control there to keep the fan on it off as long as possible to build up your supply to the WSHPs.you need to have a load coming off that tower that the WSHPs can see as aload when there in the heating mode..right.if you can add up all the straight cooling loads or machinery that will heat the tower water for your HPs and the compare it to your HPs total and work that tower fan...can you bypass the holding pond that will drain your heat build-up your trying to make for your loop in the heating mode.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Jan 2007
    Location
    in my lumpy chair
    Posts
    1,975
    Post Likes
    add a boiler
    I dont warranty Tinkeritus

  4. #4
    Join Date
    Nov 2007
    Location
    Oregon
    Posts
    12
    Post Likes
    Thread Starter
    Thanks for the help. At this time I don't believe I can bypass holding tank, But I will look into it further. I see where your going here though by using cooling water return to raise temp. Maybe some sort of 3 way mixing valve?

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    try to keep that tower fan off as long as possible so what heat is coming from those water cooled straight A/C units can be used to temp up your WSHPs loop.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Aug 2007
    Location
    Puget Sound, western wash.
    Posts
    32
    Post Likes
    no way to cheat physics. your going to need a way to add heat to the loop,PERIOD. as for water treatment the same rule applies.

  7. #7
    Join Date
    Sep 2004
    Location
    Georgia
    Posts
    103
    Post Likes
    Instead of a boiler, you might be able to get by with a small water-to-water heat pump designed specifically for those low temperature days to feed warmer water to the loop.

  8. #8
    Join Date
    Nov 2007
    Location
    Oregon
    Posts
    12
    Post Likes
    Thread Starter
    Thanks for the suggestions guys, Lately I have been thinking of some sort of tankless water heater to heat up the loop. Maybe have it cycle it off and on according to water temp? don't know if it would work just throwing it out there.

  9. #9
    Join Date
    Jan 2008
    Location
    Queens NYC
    Posts
    21
    Post Likes
    this might be a little extreme but how about some heat trace cables with a temperture controller and a relay whatever

  10. #10
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Quote Originally Posted by aNtHoNyNoZ View Post
    this might be a little extreme but how about some heat trace cables with a temperture controller and a relay whatever
    Extreme...nope...1/2 a$$ yep!

    You should keep the loop between 100F-60F typically. 39F I can't imagine any of those units are going to be running for long.

    Sounds like they have change things since the design. If the water cooled equipment cannot keep the loop warm, you need another source of heat.

  11. #11
    Join Date
    Aug 2006
    Location
    ohio
    Posts
    286
    Post Likes
    You say that you have "water cooled machinery." You really ought to consider adding a 3-way valve and using the heat produced from the machinery to heat the hp loop rather than trying to get rid of heat through a pond or tower. I would think in the Oregon winter that you would only be cooling the loop more by running through a pond. Is the machinery heat load constant, to rely on it for the heat. Try the 3-way if so if not then add the boiler but it sounds like you need the 3-way regardless.

  12. #12
    Join Date
    Nov 2007
    Location
    Oregon
    Posts
    12
    Post Likes
    Thread Starter
    Quote Originally Posted by michael26 View Post
    You say that you have "water cooled machinery." You really ought to consider adding a 3-way valve and using the heat produced from the machinery to heat the hp loop rather than trying to get rid of heat through a pond or tower. I would think in the Oregon winter that you would only be cooling the loop more by running through a pond. Is the machinery heat load constant, to rely on it for the heat. Try the 3-way if so if not then add the boiler but it sounds like you need the 3-way regardless.
    Thanks for the help. The heat load on the water is not constant, When machinery is running their seems to be no problems it is only during shutdowns of machniery for maintenance that water temp gets that low.
    I am begining to think that they must add a boiler to solve this problem.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •