    I am reading posts about micron gauges to get an idea which one to buy and thought I would put in my 2 cents as to why they are necessary.
    I am still new at HVAC and recently put a small system together in the shop. I pressure tested the system and it seemed to hold the pressure so I pulled a vacuum. I could not get the vacuum gauge to hit 500um. I found a verrrry small leak in a flare joint that needed tightening. I then got down to 500um in a couple of minutes.
    In my opinion if you're not using a micron gauge you don’t care about the quality of your work.

  2. #82
    Join Date
    Mar 2006
    Posts
    186
    Post Likes

    Appion

    Vacuum rated core removal tools
    http://www.appioninc.com/products/vctfeatures.html

    Anybody used them yet and how do they hold up?
    TANSTAAFL - There ain't no such thing as a free lunch!

  3. #83
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Quote Originally Posted by clarkkent View Post
    Vacuum rated core removal tools
    http://www.appioninc.com/products/vctfeatures.html

    Anybody used them yet and how do they hold up?
    Yes I do. They hold up well and the bore through the core remover has a larger opening than C&D's, Yellow Jackets or Cliplights. The JB's have a larger bore but the flare end has the sharpness of a hole punch and will chew up your hose gaskets in short order.


    Appion on left JB on the right.

    The Appion has double O-rings in the coupler and for the lever shaft for a good seal.

    Worth the price? Yes they are.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.

  4. #84
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Mech if you look at all J/B hoses and fittings designed specifically for pulling vacuum they use O-Rings and not gaskets.
    I believe the J/B VCRT's are designed to work with O-Rings.
    I am in the process of switching all my vacuum equipment over to O-Ring equipped
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #85
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Quote Originally Posted by itsiceman View Post
    Mech if you look at all J/B hoses and fittings designed specifically for pulling vacuum they use O-Rings and not gaskets.
    I believe the J/B VCRT's are designed to work with O-Rings.
    I am in the process of switching all my vacuum equipment over to O-Ring equipped

    Was not aware of that. Thanks.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.

  6. #86
    Join Date
    Apr 2011
    Location
    Florida
    Posts
    150
    Post Likes
    so how do you find a leak with a vacuum? and what are some other things to look for when you have a vacuum pulled? Thanks every one for all the input.

  7. #87
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Leak test, then vacuum.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  8. #88
    Join Date
    Feb 2009
    Location
    Bend OR
    Posts
    15
    Post Likes

    vacuums

    Remember, the micron guage can malfunction too. I've seen some that read 300 microns when I know there's a leak. Electronic gizmos can be unreliable... got a computer? Still, it's very important. Change the oil in your vacuum pump after every job, make sure seals are good, especially low loss fittings that have had 410a pressures on them or are just old. If you still think it's your vacuum pump, check it with another micron guage to be sure. Also, if you have moisture in a system that doesn't leak, it can take a long time. The water has to boil out (water will boil at 0 degrees in a complete vacuum) which causes expansion then the vapor must be removed. Keep your copper clean and dry.

    I once spent 6 hours looking for a leak that turned out to be in my manifold set. Boy was I mad

  9. #89
    Join Date
    Jul 2011
    Posts
    2
    Post Likes
    love the apion mega flow kit. the time savings in amazing! too much $$ though. but then ain't it all

  10. #90
    Join Date
    Jul 2011
    Location
    northern Minnesota
    Posts
    36
    Post Likes
    my digital gauge set has microns right on it, and i us it everytime the vac is on. mine starts at 0 and goes negative from there. like to see at least -600 the best i've ever seen was -755.

  11. #91
    Join Date
    Jul 2011
    Posts
    354
    Post Likes

    Confused

    Quote Originally Posted by qwerty hvac View Post
    Leak test, then vacuum.
    agreed!!!!!!!!!!!!!!

  12. #92
    Join Date
    Jun 2007
    Location
    Pigeon Forge, TN
    Posts
    329
    Post Likes
    I've been using a Yellow Jacket 69080 Digital LCD Vacuum Gauge. It has bars that go from 500 to 750 to 1000, etc. I like it. It seems to work well enough.
    The more you know, the more you realize how much you don't know.

  13. #93
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Quote Originally Posted by JumpSteady View Post
    I've been using a Yellow Jacket 69080 Digital LCD Vacuum Gauge. It has bars that go from 500 to 750 to 1000, etc. I like it. It seems to work well enough.
    Yellow Jacket only lists the accuracy of their 69075. Which is +/- 20% and it is a digital readout. They do not list the accuracy of the 69080. Have you checked it against other electronic vacuum gauges?
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.

  14. #94
    Join Date
    Oct 2004
    Location
    Annapolis, MD: ragboat capitol of the world
    Posts
    499
    Post Likes
    After you have done your best pressure leak test, a good vacuum gage can be the final test of system integrity.

    Static vacuum and not running vacuum is the real test.
    Sam

    Know-it-all? Nope, not even half!

  15. #95
    Join Date
    Jan 2005
    Location
    Veterans Home Yaphank, NY
    Posts
    2,309
    Post Likes
    Not that I have a clue about things.

    Amprobe Ultrasonic Leak Detector, TMULD-300


    In areas where leaking gases are not sufficiently pressurized, there is no ultrasonic sound for detection. The area can be pressurized with the ultrasonic sound waves created by Amprobe's UT-300 Ultrasonic Transmitter. This will allow the detection of cracks which would not normally be possible. Locates arcing in an electrical system. Useful in finding the ends of buried PVC pipes.
    RAM Teaching Tomorrows Technicians Today.

  16. #96
    Join Date
    Oct 2004
    Location
    Annapolis, MD: ragboat capitol of the world
    Posts
    499
    Post Likes
    I have found ultra sonic devices helpful at times when other methods were failing, but I've had less success with it than with refrigerant detectors in general. The ultrasonic transmitter is not useful for our work, its for structural cracks like roofs, etc. I've never tried it in an open pipe, but I guess it would work well. I've had a receiver and transmitter on my truck for almost 20 years, but rarely use them. I don't know if you can rig up the transmitter to spray sound waves into a pipe smaller than the 3/4" horn on the transmitter either ... a pain in the butt if you had to anyway.

    I even accidentally discovered that soap enhances the chances of finding a leak with ultra sound ... the repeated forming and popping of bubbles picks up better than a dry stream of gas. Ultra sound device also showed me that pin holes take time to ramp up ... it might be 5 minutes after you apply pressure that the pin hole is really flowing. Be patient and retest.

    The down side of ultrasonic ... extremely directional. You can be directly adjacent to a leak, but not pointing in the direction of the sound propagation, and miss it entirely. I do not know of another detection method that is as picky about pointing straight in at the leak.
    Sam

    Know-it-all? Nope, not even half!

  17. #97
    Join Date
    Jun 2007
    Location
    Pigeon Forge, TN
    Posts
    329
    Post Likes
    Quote Originally Posted by MechAcc View Post
    Yellow Jacket only lists the accuracy of their 69075. Which is +/- 20% and it is a digital readout. They do not list the accuracy of the 69080. Have you checked it against other electronic vacuum gauges?
    No. I only have one, don't have anything to compare it to. It seems to work as it should.
    The more you know, the more you realize how much you don't know.

  18. #98
    Join Date
    Jul 2011
    Posts
    2
    Post Likes
    My new setup (which I haven't used through a full vac yet) is JB Platinum 7CFM vac pump (shop supplied), two YJ vac hoses (3/8 hose with 1/4 fittings on one end) straight off of pump (has 3/8 - 3/8 - 1/4 port, why not a 1/2" on a 7CFM pump is unknown to me) to two 1/4" YJ core removal tools (with side port). Off of one of the side ports is a YJ ball valve shut off connected to a JB DV220 micron gauge.

    I work primarily in residential service and install, but do commercial as well.

    I have only fully used this setup on a test, on a 26 lb reclaim bottle, but this vs my old setup (1/4" charging hoses off of a vac pump tree, micron gauge at top of tree) was a world of difference. 8m 45s to 200 micron with new, 50 minutes to get to 277 with old (had to break it down to head to a job). We'll see real results tomorrow (service valve on a 20lb 5 ton system.

    As far as the DV220, I dislike them. They are very slow to read, and I've been through 2 of them, last one only lasted 11 months. both of them ended up that I could take them completely out of the system and they'd read a vac for minutes before they'd start to show a change. This last one (a few weeks ago), I wanted the shop to get me a BluVac, but cheaper cost and availability (needed it then and there) won. I'll be buying myself a BluVac sometime in the near future.

  19. #99
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    The J/B Super7 I saw had 1/2, 3/8 and 1/4 but FWIW you can pull 7cfm with that pump thru one 1/2" hose with 3/8 and 1/4 fittings on either end.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  20. #100
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    To be clear you can pull 7 with your platinum and one 1/2 hose
    “If You Can Dodge A Wrench You Can Dodge A Ball”

+ Reply to Thread
Page 5 of 9 FirstFirst 123456789 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •