Thread: New Heat Pump, completely frozen over- any concerns I should have?

  1. #1
    Join Date
    Feb 2013
    Posts
    4
    Post Likes

    New Heat Pump, completely frozen over- any concerns I should have?

    I just had a new American Standard 3 ton unit installed Wednesday, by Friday night it was making such a noise that I shut off, went to heat strips so we could sleep. I inspected on Saturday morning, had been raining for two days, temps in upper 30s, unit was covered in ice, in fact the fan blade froze to side of unit after I shut it off.

    So, it is obvious the defrost cycle never triggered. Technician arrives to inspect my 3 day old unit, and yes, the wire 'came loose' on the connection under the house, no signal was sent to trigger defrost.

    Now, understand, this isn't my first rodeo. I had problems with previous company on a unit install 10 years ago. This time, I went with a highly regarded company with a fair price, that advertises "its not the equipment that matters so much, but the quality of the install". So much for that. When paying my bill at the end of install Wednesday, I even let them know I'd be checking it out, as the previous company years back did a shoddy job of electric hookup, such that it was a fire hazard. (Not sure why inspectors never caught that). I realize that problems happen, and I didn't unload on anyone-we're all human, but hey, if you screwed up, you pay-no need to get emotional.

    Question is, should I be concerned about with the complete ice over on my unit- the components on the side of the coil/condensor were solidly encased in 1/2 to 1" of ice. I do have a standard 10 year parts warranty. Thanks for any advice you can share.

  2. #2
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    Connection under the house not triggering defrost.... I can't relate to how that would cause it to not defrost. The defrost circuit is 100% inside the outdoor unit.

    As far as damage caused.... I doubt it.

    Need to figure out about the defrost circuit though. I'm not convinced. Where are you located? We've had rain the past two days too.

  3. #3
    Join Date
    Feb 2013
    Posts
    4
    Post Likes
    Thread Starter
    maybe i heard wrong, but thought he said there are 3 wires to hook up under house, and one was loose. Either way, the install wasn't done right, even after certified tech showed up at end of day to ensure all was set up proper. Tech on Saturday had defrost cycle going in a matter of a few minutes-here in NC.

  4. #4
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,890
    Post Likes
    I agee that the defrost function should be controlled by the board located in the condenser not by anything wired "under the house".

  5. #5
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Unless its power to the board.....
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  6. #6
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,626
    Post Likes
    The OP's issue suggests not only defrost issues but also a possible refrigerant leak, both probable install issues.

    Upper 30s, raining with bad icing issues like OP describes. That in itself is highly unlikely. Not saying it couldn't happen but unlikely with Trane/AmStd heat pumps that have EDD.

    Seems to me both defrost function should be checked as well as refrigerant charge.

    Fan blade damage should be checked.

    What is model of HP? Heritage series?

    IMO

  7. #7
    Join Date
    Jun 2004
    Location
    St Paul, minnesota
    Posts
    1,527
    Post Likes
    Quote Originally Posted by heaterman View Post
    I agee that the defrost function should be controlled by the board located in the condenser not by anything wired "under the house".
    this has nothing to do with defrost controls. If one of the 3 wires between indoor and outdoor units became disconnected then effectively this turned the outdoor unit into a straight a/c unit then the defrost controls would never be energized

  8. #8
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    Quote Originally Posted by superfittertech View Post
    this has nothing to do with defrost controls. If one of the 3 wires between indoor and outdoor units became disconnected then effectively this turned the outdoor unit into a straight a/c unit then the defrost controls would never be energized
    And then it would be cooling instead of heating, and the outdoor unit would not be frozen up.

  9. #9
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Should be 5 wires. If the 24v (red) wire is what wasn't connected, you would have heat pump operation but no defrost. Unless the blade was damaged by ice, I wouldn't expect any issues.

  10. #10
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    Should be 5 wires. If the 24v (red) wire is what wasn't connected, you would have heat pump operation but no defrost. Unless the blade was damaged by ice, I wouldn't expect any issues.
    x2
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  11. #11
    Join Date
    Feb 2013
    Posts
    4
    Post Likes
    Thread Starter
    Thanks for the replies- it's an AS Gold XI 15 heat pump. No damage to fan blades fortunately. The unit was functioning properly as Heatpump for the 48 hours I had it running, just no defrost mode. Tech checked all pressures yesterday after fix, told me all was good. I do have two free maintenance visits in next 12 months, so if anything comes up, I'll be paying attention.

  12. #12
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Sounds like they got it fixed.

    One question though, does water runoff from the roof fall on or near the heat pump, or is there a gutter/deflector to prevent it?

    If rainwater runoff from the roof is falling on the unit, in the weather conditions you mentioned, the unit can ice up faster than even a properly functioning demand defrost can deal with.

  13. #13
    Join Date
    Feb 2013
    Posts
    4
    Post Likes
    Thread Starter
    to answer above question, unit is on side of house with no water runoff from roof. I guess the main point in all of this is please check all electrical connections on installs, double, triple- an extra ten minutes on day of install would have saved the approx $200 in cost incurred by the company to come back. Do installers use a final checklist? I don't like to see anyone waste time and money, even if I'm not paying for it- I'm happy to do business with a good service company and want them to make a profit!
    Last edited by port111; 02-24-2013 at 02:27 PM. Reason: edit

  14. #14
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    Quote Originally Posted by port111 View Post
    to answer above question, unit is on side of house with no water runoff from roof. I guess the main point in all of this is please check all electrical connections on installs, double, triple- an extra ten minutes on day of install would have saved the approx $200 in cost incurred by the company to come back- I don't like to see anyone waste time and money, even if I'm not paying for it- I'm happy to do business with a good service company and want them to make a profit!
    This can't be what I'm hearing from a consumer!!!! Lol.

    Are you applying for a management position here? If you are, you're hired.

    Seriously though, as a business owner, I live and breathe just your above statement daily. Hopefully the company has a process that will define the problem and take measures to eliminate ones like that one from happening.

    It hurts everyone involved when they happen.

  15. #15
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by port111 View Post
    I'm happy to do business with a good service company and want them to make a profit!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •