    To anyone with advice,

    I've had 2 refrigeration compressors go bad because of too much voltage from panel to condensing unit. Currently 246v. I've solved the problem with a transformer but have this question for all you electricians.

    Why does the power company say "they are within their range" at 120v plus/minus 5% which puts each leg at 126v or 252v for 1phase? Compressors are 208/230 and can't handle that kind of constant power.

    Any thoughts are appreciated!

    Thx,
    Refrigeration nut

    Leroy driver

  2. #2
    Join Date
    Nov 2007
    Location
    Texas
    Posts
    237
    Post Likes
    246 is fine. I was told on 208/230-240 equipment 197-255 was acceptable. Heck the voltage at my house is 253 and I don't have any problems. Most problems occur from the voltage dropping too low. I'd be more worried if it was 197. Don't think 246 VAC is causing your problems

  3. Likes lions_lair, Bob-Brr, YOUNG FROSTY liked this post.
  4. #3
    Join Date
    Mar 2010
    Posts
    5
    Post Likes
    Thread Starter
    Well, they don't make compressors like they did 20yrs ago! Lol built like tanks back in the day. Thanks for the response, I will continue to investigate.

  5. #4
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    In my area, 246 to 252v is the norm.
    It falls within the maximum voltage specs of every compressor I've bothered to look at the specs for.
    It does give you a little extra capacity over the manufacturers rating.

  6. Likes ksefan liked this post.
  7. #5
    Join Date
    Dec 2008
    Location
    NW Iowa
    Posts
    250
    Post Likes
    I would not think 246 volts is a problem. It's the norm around here.

  8. Likes Bob-Brr liked this post.
  9. #6
    Join Date
    Feb 2013
    Posts
    6
    Post Likes
    Nominal voltage in New Zealand is 230V but I have had problems with it going over 254V and equipment failing. The biggest problem however is that the voltage is no longer purely sinusodial due to the switched power supplies to computers, LED and halogen lights, washing machines using DC motors etc etc. If you put an osciloscope then you might well see that the voltage spikes are far higher than that your 246V indicates especially if your voltmeter is not a pure RMS meter. I suspect that it might have to do with insualtion breakdown of the windings. The earlier failing is the same as when you control the speed of a motor with a cheap speed controller, motors will hum and fail earlier.

    For computer equipment I use a UPS that first transforms the power and then generates a pure sinusoidial voltage. There are cheaper solutions that stabilise the voltage and transform it in a pure sinus without having a UPS built in. Unfortunately those are not much use if you have trouble with bad brown outs where the mains falls away to very low voltages where a UPS may be required instead. (I recently looked into those because my daughter has trouble with "brown outs" too low voltage when all the hot water cylinders are turned on through ripple control. The computer controlled radio and washing machine were going silly).

  10. Likes David Goodman, Pajal liked this post.
  11. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by AmadeusMozart View Post
    Nominal voltage in New Zealand is 230V but I have had problems with it going over 254V and equipment failing. The biggest problem however is that the voltage is no longer purely sinusodial due to the switched power supplies to computers, LED and halogen lights, washing machines using DC motors etc etc. If you put an osciloscope then you might well see that the voltage spikes are far higher than that your 246V indicates especially if your voltmeter is not a pure RMS meter. I suspect that it might have to do with insualtion breakdown of the windings. The earlier failing is the same as when you control the speed of a motor with a cheap speed controller, motors will hum and fail earlier.

    For computer equipment I use a UPS that first transforms the power and then generates a pure sinusoidial voltage. There are cheaper solutions that stabilise the voltage and transform it in a pure sinus without having a UPS built in. Unfortunately those are not much use if you have trouble with bad brown outs where the mains falls away to very low voltages where a UPS may be required instead. (I recently looked into those because my daughter has trouble with "brown outs" too low voltage when all the hot water cylinders are turned on through ripple control. The computer controlled radio and washing machine were going silly).
    I would need to know more about power distribution practices in new Zealand to help you.v
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by LeroyDriver View Post
    Well, they don't make compressors like they did 20yrs ago! Lol built like tanks back in the day. Thanks for the response, I will continue to investigate.
    How long has each compressor lasted?

    246 is fine.

  13. Likes lions_lair, Bob-Brr liked this post.
  14. #9
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by beenthere View Post
    How long has each compressor lasted?

    246 is fine.
    Agreed, time to start looking for a system problem......

  15. Likes lions_lair liked this post.
  16. #10
    Join Date
    Oct 2010
    Location
    Utah
    Posts
    51
    Post Likes
    Higher voltage within specs on nameplate equal lower amps, which would be better for compressor and electric bill usually lower voltage is what would cause you problems.
    If it aint broke don't fix it!!!

  17. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by brettrobbins View Post
    Higher voltage within specs on nameplate equal lower amps, which would be better for compressor and electric bill usually lower voltage is what would cause you problems.

    219 volts at 18.26 amps is 4000 watts, 246 volts at 16.26 amps is 4000 watts. So no savings because of the higher voltage and lower amp draw.

  18. Likes ckartson, YOUNG FROSTY liked this post.
  19. #12
    Join Date
    Nov 2004
    Posts
    1,438
    Post Likes
    I remember reading that something like 50 % of all field compressors fail. Due tobad install practices. Maybe that is the problem

    On the electric side unless you are getting some really high voltages like 140 on what is suspose to be 125 u will be fine. Like others have said.

    Dang old post op probably will not return to this site

  20. Likes Bob-Brr liked this post.
  21. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by LeroyDriver View Post
    To anyone with advice,

    I've had 2 refrigeration compressors go bad because of too much voltage from panel to condensing unit. Currently 246v. I've solved the problem with a transformer but have this question for all you electricians.

    Why does the power company say "they are within their range" at 120v plus/minus 5% which puts each leg at 126v or 252v for 1phase? Compressors are 208/230 and can't handle that kind of constant power.

    Any thoughts are appreciated!

    Thx,
    Refrigeration nut

    Leroy driver
    There is one standard for the power company, and then there is the voltage standard acceptable to equipment manufacturers. They may be different. Let's start at the beginning.

    IF the compressor is actually rated with the 208/230 volt rating (the "slash rating") then you are fine at that 246 voltage. Being 16 volts above 230 should be withing manufacturer's specs. You can ask them to be certain. I would ask.

    HOWEVER, if you are using equipment that is rated "208" on the label, you are above the intended voltage rating and in fact are in violation of the NEC.

    Does that help?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  22. #14
    Join Date
    Dec 2012
    Location
    The dark side of the moon.
    Posts
    14
    Post Likes
    Our nominal voltage single phase 50Hz is 230 VAC. 246v is not really much out of spec to be honest. There might be more to the situation, dirty voltage or bad transient voltage problems.

  23. Likes Ernest Crossman liked this post.
  24. #15
    Join Date
    Jun 2013
    Posts
    67
    Post Likes
    In the USA , 120 VAC devices are actually rated 125 VAC . Same , 240 -> 250 VAC . I gave actually seen 255 VAC . Some of this depends on if you ate close to the " end of the line " or the head of the line " , of a run of primary ?

    Some transformers have or had taps , the power company could adjust the secondary voltage , to some extent ?

    I have also seen voltage vary with time of day , with load . In the summer , around 05:00 PM , when A/C's get turned to max , electric ranges , washing machines , clothes dryers , water heaters and every thing in the house gets turned on .

    God bless
    Wyr

  25. Likes Ernest Crossman liked this post.
  26. #16
    Join Date
    Jun 2013
    Posts
    53
    Post Likes
    In the US if you have had to replace equipment due to overvoltage, you can make the power company put a voltage monitor on your line, this is a portable device that records voltage levels for a month or so. This will also record spikes and so on. If an isolation transformer solved it then very likely there's distribution problems. If your in the US and the power company balks then threaten to go to the PUC as all of them are regulated. My father sold high voltage power distribution gear for all his life and quite often power companies find things like failing step down transformers in their distribution systems due to industrial users complaining.

  27. Likes Ernest Crossman liked this post.
  28. #17
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    You need to "pay" the the utility to put "their" voltage spike, transient arrestor(s) on your panel(s). I did that years ago after repeated small motor losses, I'm now covered under their insurance. BTW don't expect to make a claim and get paid for damages without this. They have more ways of getting out of paying than a mongoose getting out of a paper bag.

  29. #18
    Join Date
    Apr 2016
    Posts
    67
    Post Likes
    I would look at what kind of compressor they were if the voltage was 246 and that killed them. Run all kinds of compressors all day long here on 255.


    Sent from my iPhone using Tapatalk

  30. #19
    Join Date
    Apr 2016
    Posts
    67
    Post Likes
    Quote Originally Posted by WyrTwister View Post
    In the USA , 120 VAC devices are actually rated 125 VAC . Same , 240 -> 250 VAC . I gave actually seen 255 VAC . Some of this depends on if you ate close to the " end of the line " or the head of the line " , of a run of primary ?

    Some transformers have or had taps , the power company could adjust the secondary voltage , to some extent ?

    I have also seen voltage vary with time of day , with load . In the summer , around 05:00 PM , when A/C's get turned to max , electric ranges , washing machines , clothes dryers , water heaters and every thing in the house gets turned on .

    God bless
    Wyr
    Nearly everything around here is at 255. We are at the head of the grid and that's the usual reading. Anything that says 208-230 runs fine on that. I would look at who installed the equipment or the brand of compressor first. In the summer most things run all day long unless they are well insulated or inside a building. And the extra money to switch to a scroll upon failure is always worth it. I would be more likely to believe something was not done. Like a crankcase heater left out or something before I would blame voltage less than the max I have seen. Even the compressor I just installed on a rare delta three phase system is running fine on 244. What you have to watch for there is it has a wild leg at 214. That will kill refrigerators or anything else if someone that doesn't know installs a circuit in a three phase panel that is single phase. The only place you can be certain it is safe is on leg #1 2 or three are the only legal place to put it but it will be 1 coming in. It took weeks for me to figure out this power system and no one will give me information. It's really frustrating.

  31. #20
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    If a compressor fails and the cause isn't found a repeat failure is likely.
    Failures are almost always external to the compressor. If possible open the compressor
    because often the evidence will be there. I've even opened hermetics at times.

    One of the best classes I've gone to was Carrier's tear down school analyze failures.
    A voltage problem will be obvious.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  32. Likes Ernest Crossman, ksefan liked this post.
+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •