evaporator td
what is the proper way to check ? i thought it was to check temp at incoming evap and outgoing but the guy i am working with said it was to shop so i dont want tyo check at supply and return air temp. i am new and this is my first shop and i am training with this guy but i think he is wrong. can you guys help me?
-
-
Box temp minus boiling point of ref being checked.
I.E. Air temp minus PT
404a
Box temp at 32
Suction pressure @ 60psig (22 deg)
10deg td
sent from my Samsung Galaxy Note
Member of the "Work Exchange Program"
"Will work for knowledge"
"Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
A Einstein
-
Evaporators are designed to run at a certain TD depending on its design and application. What are you trying to accomplish by taking a TD of a refrigeration evap coil? You should be able to diagnose refrigeration problems thru other means. Verify the coil is clean and fans are running properly.
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
-
Originally Posted by
2sac
Evaporators are designed to run at a certain TD depending on its design and application. What are you trying to accomplish by taking a TD of a refrigeration evap coil? You should be able to diagnose refrigeration problems thru other means. Verify the coil is clean and fans are running properly.
this was a procedure for a pm
-
it was a way of knowing if the unit was operating correctly ?
-
what is the correct way of checking this ?
-
the coil was clean and fans were running proper. this weas on an ac roof top unit. does that make a difference ?
-
i also wondered why i would need a td on an evap. but i am new and dont want to rock the boat.
-
Originally Posted by
royd2
the coil was clean and fans were running proper. this weas on an ac roof top unit. does that make a difference ?
This thread is posted in the refrigeration section, not commercial a/c.
An evap TD is more beneficial in an a/c package unit for troubleshooting. Take a temp at the return and suply near the evap coil by drilling a small hole. A tek screw will work with most probes. Not a big deal. Somewhere between 15-25 degrees is usually normal.
Officially, Down for the count
YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET
I know enough to know, I don't know enough
Why is it that those who complain the most contribute the least?
MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING
-
Originally Posted by
2sac
This thread is posted in the refrigeration section, not commercial a/c.
An evap TD is more beneficial in an a/c package unit for troubleshooting. Take a temp at the return and suply near the evap coil by drilling a small hole. A tek screw will work with most probes. Not a big deal. Somewhere between 15-25 degrees is usually normal.
This would be more of a Delta-T
A TD is used when you are taking the temperature difference between 2 different mediums such as...
(Return Air - SST = Evaporator TD) RA - SST = TD
or
(SCT - Ambient = Condenser TD)
A Delta-T is when you are measuring the temperature difference between the same medium, such as...
(Return Air - Supply Air = A/C Delta-T) RA - SA = dT
or
(Filter Drier Inlet - Filter Drier Outlet = Filter Drier Delta-T)
-
Post Likes - 1 Likes, 0 Dislikes
-
2sac thanks for the help also phase loss it makes much better sense now. and we were doing the pm on a lennox rooftop unit. sorry i posted this in the refrigeration section but we work on refrigeration hvac and hot side, so sometimes i forget some things should be in another section. thanks you guys are great
-
Originally Posted by
royd2
2sac thanks for the help also phase loss it makes much better sense now. and we were doing the pm on a lennox rooftop unit. sorry i posted this in the refrigeration section but we work on refrigeration hvac and hot side, so sometimes i forget some things should be in another section. thanks you guys are great
It is important to know the evap TD as described by phase loss when checking and or adjusting super heat on expansion valves. The method applies to all evaps, water , air . Airconditioning and refrigeration to maximise evaporator operation.
-
dears, i am new in HVAC and trying to practice it.
am reading about condenser and evaporator temperature approach.
is it only terms used for chillers? or for rooftop package units also?
how to calculate them?
what recommended value should be?
what the effect if high or low approach values?
thanks