    evaporator td

    what is the proper way to check ? i thought it was to check temp at incoming evap and outgoing but the guy i am working with said it was to shop so i dont want tyo check at supply and return air temp. i am new and this is my first shop and i am training with this guy but i think he is wrong. can you guys help me?

  2. #2
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Box temp minus boiling point of ref being checked.
    I.E. Air temp minus PT
    404a
    Box temp at 32
    Suction pressure @ 60psig (22 deg)
    10deg td

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Evaporators are designed to run at a certain TD depending on its design and application. What are you trying to accomplish by taking a TD of a refrigeration evap coil? You should be able to diagnose refrigeration problems thru other means. Verify the coil is clean and fans are running properly.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  4. #4
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    Quote Originally Posted by 2sac View Post
    Evaporators are designed to run at a certain TD depending on its design and application. What are you trying to accomplish by taking a TD of a refrigeration evap coil? You should be able to diagnose refrigeration problems thru other means. Verify the coil is clean and fans are running properly.
    this was a procedure for a pm

  5. #5
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    it was a way of knowing if the unit was operating correctly ?

  6. #6
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    what is the correct way of checking this ?

  7. #7
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    the coil was clean and fans were running proper. this weas on an ac roof top unit. does that make a difference ?

  8. #8
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    i also wondered why i would need a td on an evap. but i am new and dont want to rock the boat.

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by royd2 View Post
    the coil was clean and fans were running proper. this weas on an ac roof top unit. does that make a difference ?
    This thread is posted in the refrigeration section, not commercial a/c.
    An evap TD is more beneficial in an a/c package unit for troubleshooting. Take a temp at the return and suply near the evap coil by drilling a small hole. A tek screw will work with most probes. Not a big deal. Somewhere between 15-25 degrees is usually normal.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by 2sac View Post
    This thread is posted in the refrigeration section, not commercial a/c.
    An evap TD is more beneficial in an a/c package unit for troubleshooting. Take a temp at the return and suply near the evap coil by drilling a small hole. A tek screw will work with most probes. Not a big deal. Somewhere between 15-25 degrees is usually normal.
    This would be more of a Delta-T

    A TD is used when you are taking the temperature difference between 2 different mediums such as...

    (Return Air - SST = Evaporator TD) RA - SST = TD

    or

    (SCT - Ambient = Condenser TD)

    A Delta-T is when you are measuring the temperature difference between the same medium, such as...

    (Return Air - Supply Air = A/C Delta-T) RA - SA = dT

    or

    (Filter Drier Inlet - Filter Drier Outlet = Filter Drier Delta-T)

  11. Likes fv_tom liked this post.
  12. #11
    Join Date
    Jan 2012
    Location
    ohio
    Posts
    144
    Post Likes
    Thread Starter
    2sac thanks for the help also phase loss it makes much better sense now. and we were doing the pm on a lennox rooftop unit. sorry i posted this in the refrigeration section but we work on refrigeration hvac and hot side, so sometimes i forget some things should be in another section. thanks you guys are great

  13. #12
    Join Date
    Sep 2012
    Location
    Auckland , South Pacific.
    Posts
    193
    Post Likes
    Quote Originally Posted by royd2 View Post
    2sac thanks for the help also phase loss it makes much better sense now. and we were doing the pm on a lennox rooftop unit. sorry i posted this in the refrigeration section but we work on refrigeration hvac and hot side, so sometimes i forget some things should be in another section. thanks you guys are great
    It is important to know the evap TD as described by phase loss when checking and or adjusting super heat on expansion valves. The method applies to all evaps, water , air . Airconditioning and refrigeration to maximise evaporator operation.

  14. #13
    Join Date
    Oct 2018
    Location
    saudi arabia
    Posts
    45
    Post Likes
    dears, i am new in HVAC and trying to practice it.

    am reading about condenser and evaporator temperature approach.

    is it only terms used for chillers? or for rooftop package units also?
    how to calculate them?
    what recommended value should be?
    what the effect if high or low approach values?

    thanks

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •