Thread: Tower water temps

  1. #1
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes

    Tower water temps

    Looking for a little chiller help... I have a Carrier 30HR050-B150 with water IN from the tower at 110 degrees and leaving the chiller at 122 degrees. The outside temp was 98 yesterday. How much of a delta should I expect to see? The water leaving the chiller was only 52 degrees.
    Last edited by air2spare; 08-27-2009 at 12:37 PM.

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Why was your tower water so hot should be about 85 or so?

  3. #3
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    Quote Originally Posted by thegoodlistener View Post
    Why was your tower water so hot should be about 85 or so?
    I'm thinking something is restricting water flow or a weak pump, I really have no way of determining GPM

  4. #4
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Your delta T is not too bad could be alittle better but your condenser water loop is not transfering much heat from what I can tell.

  5. #5
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Whow! Tower loop is way way way too hot. You need to confirm the tower and tower fan are in good working order before you do anything else. Then check your pumps, pull strainers, check circuit setters, and lastly condenser barrel water pressure controls if you have them.

    I suspect you either have flow issues or your tower fan is not working.
    UA LU189

  6. #6
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    the fan appears to be fine but I did notice alot of algae in the tower

  7. #7
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    is the water treatment best left to a 3rd party to maintain?

  8. #8
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by air2spare View Post
    is the water treatment best left to a 3rd party to maintain?
    Yes it would in my opinion. Does there appear to be a sufficient flow in the tower ?

  9. #9
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    not really. is there a method for measuring GPM w/o a flow meter?

  10. #10
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    You need the PD across the heatexchanger. Then you will have to know the performance curve for that model chiller .At least that is how I do it other people may have a better way of doing it.
    Ifyou shoot me a M# I will try to find something on it.

  11. #11
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    the M# is on the first post, thanks

  12. #12
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    727
    Post Likes
    What kind of tower do you have? Is water going over the top of the tower? Or maybe running through a bypass? Hot deck plugged up? 110*h20 pretty darn hot. Not to sound like an a$$ but is the fan going the right direction?
    Sic Semper Tyrannis.

  13. #13
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    "Lots of algae" will cause the tower not to make capacity. Based on rule of thumb, your condenser delta T looks good (should go down when problem is corrected) assuming you're at full load, but you're not removing the heat from the cooling water. Your tower ain't makin' capacity......

  14. #14
    Join Date
    Mar 2003
    Location
    Brooklyn, Ohio
    Posts
    102
    Post Likes
    It sounds like you might have a bypass somewhere in the piping. Can you check the suction and discharge of the pump and look up the curve? I would also want to know what pressure drop is reguired across the barrel.

  15. #15
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,664
    Post Likes
    I'd start with cleaning the strainers at the pump and in the tower.

    You should be able to get within 6-8 degrees of wet bulb.

    Maybe there's a tower by pass for minimum temp, and it's not modulating.
    God Bless our Veterans

    God Bless the USA

  16. #16
    Join Date
    Oct 2007
    Location
    california
    Posts
    57
    Post Likes
    Might also want to check if tower has modulating dampner on fan..is it open?

  17. #17
    Join Date
    Jan 2008
    Location
    pennsylvania
    Posts
    132
    Post Likes
    Quote Originally Posted by air2spare View Post
    not really. is there a method for measuring GPM w/o a flow meter?
    GPM2 equals GPM1 times square root (deltaP2 divided by deltaP1)

    gpm1 equals design
    gpm2 equals actual
    delta p1 equals design pressure drop
    delta p2 equals actual pressure drop

  18. #18
    Join Date
    Jan 2008
    Location
    pritzberg
    Posts
    4,641
    Post Likes
    don't forget to also check the spray heads and trees for blockage. and if you're growing algae, you may have other bacteria thriving - i.e. legionella - be careful!!!!!!!!!!

  19. #19
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes
    Thread Starter
    Quote Originally Posted by txhvac View Post
    What kind of tower do you have? Is water going over the top of the tower? Or maybe running through a bypass? Hot deck plugged up? 110*h20 pretty darn hot. Not to sound like an a$$ but is the fan going the right direction?
    lol, funny you mentioned that. it was one of the things I checked when I looked at the tower.

  20. #20
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    what is the brand of tower and model...your looping tower return water with towering entering to the chiller someplace.the tower will only do its 10F as you have typically.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •