Thread: Condenser fan

  1. #1
    Join Date
    Dec 2008
    Posts
    8
    Post Likes

    Condenser fan

    I have a used Traulsen URS-36-DT and the consenser fan does not seem to be behaving correctly. Essentially, it is always running, regardless of whether either of the compressors is running. I know this is not standard, but is it possible that it is designed that way for this unit? The other odd thing is that it only runs if both the refrigerator and freezer are switched on (at the switches, not the cold control). So I cannot turn the freezer off and have the condenser fan run for the refrigerator for instance. (Actually, I can, by turning off the freezer with the thermostat, but not with the switch). Is this wired incorrectly, or is there a part that is not working correctly?

  2. #2
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Post a picture of it.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    How about checking or posting the wiring print?

    Certain DPDT stats function that way. ON closes one contact and the second contact closes at setpoint.

    If the ON contacts are wired in series, then what you are describing is exactly correct.



  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    This is the domestic model Traulsen, 2 compressors and 1 condenser.

    There is a relay that brings on the fan if either switch is on.

    I have a wiring diagram on PDF if you need it

  5. Likes trippintl0 liked this post.
  6. #5
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    If I understand the wiring diagram, the condenser fan does indeed run all of the time, although it should come on with either switch on, so I would guess there is something wrong with the relay. It is no big deal unless one side gets left on for a while with the other side off.

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Any SPDT 110V coil relay will work. That’s a 9 or 16W motor.

  8. #7
    Join Date
    Nov 2008
    Location
    Hudson Valley, NY
    Posts
    219
    Post Likes
    If this is a resadentle it is probly not a lot of air flow through condensor
    I would keep it runing all the time
    two compressor's one condensor and not much air flow

  9. #8
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Running the condenser fan without a compressor is pointless unless you're trying to get your electric bill up. Surely that cannot be what the engineer planned. Is there maybe a pressure switch in series with the fan set too low or stuck? Something is not right.

  10. #9
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Quote Originally Posted by man from trane View Post
    Running the condenser fan without a compressor is pointless unless you're trying to get your electric bill up. Surely that cannot be what the engineer planned. Is there maybe a pressure switch in series with the fan set too low or stuck? Something is not right.
    Tell that to Silver King. Their condensor fans are wired to run 24/7. I think it might be planned obsolescence. You know the quicker the condensor gets packed with dirt. The more likely the cap tube gets plugged that leads to compressor failure. Or their just looking out for us service techs. Keeping us employed.

  11. #10
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    882
    Post Likes
    Quote Originally Posted by kbghdg View Post
    Tell that to Silver King. Their condensor fans are wired to run 24/7. I think it might be planned obsolescence. You know the quicker the condensor gets packed with dirt. The more likely the cap tube gets plugged that leads to compressor failure. Or their just looking out for us service techs. Keeping us employed.
    Wow...at our new lowered rate of 34 cents per Kw (4x what I paid in the states) that could also add up over time running those fans continuously. I wonder what they were thinking? It would be interesting to hear their engineer try and explain that one. Maybe they are thinking that most of the wear of the fan motor occurs at startup so just keep them running, but if that's the case then the planned obsolescence theory is out the window. Either way I don't like it.

  12. #11
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    There is nothing in the circuit but the master switches and the relay. It is a single condenser (and fan) with two compressors. It is designed to be built in, so the ventilation needs to be good. That said, it is a fifteen-year-old unit, and may simply be an older design less focused on efficiency.

    It seems that it would be fairly straightforward to wire it so that the fan would only got on when one of the compressors did, but I don't want to do this if it is a bad idea. Does anyone know if the current UR48 models use the same design?

  13. #12
    Join Date
    Nov 2007
    Posts
    162
    Post Likes
    If the fan is wired to run all the time my guess is that your case has a non heated condensate pan and they are using the air flow off the condensor fan to speed the evaporation of the condensate. I have seen this in quite a few self contained cases.

  14. #13
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    There is a heated consensate pan on the bottom of the unit. The condenser fan is on the top.

  15. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    This is a Traulsen design. At the time they were trying to compete with Sub-Zero for the residential market.

    The first design used a static condenser mounted on the back with a 1” X 6” squirrel cage fan on a rheostat blowing from the top down. (Without the fan the compressors were over heating.) This same model had the freezer evaporator in the walls of the freezer. It was a lot of fun telling a customer that just paid 4g’s (mid 80’s $) that the freezer was a manual defrost. Along with the compressor noise issue this model was soon put to rest.

    The new design used Tecumseh AE4440 & 4430 pumps (I believe) with a 2 circuit condenser coil-1 fan. These are not Tecumseh condensing unit’s just there compressors. Everything wrapped with insulating sheets to keep the noise down. (even they learned by there mistakes and did away with the in wall evaporator)Unfortunately they couldn’t compete with Sub-Zero and the others and the entire line was dropped.

    Old man Traulsen, yes that was his name, started as a tech (mechanic as us old farts used to be called) and built the company. He took pride in seeing his name all over the world.
    As a young mechanic I was sent to his apartment on 5th Ave in Manhattan. Getting off the service elevator there was no question which door was his. All Stainless Steel with the same Traulsen label.

    There is no better manufactured piece of refrigeration equipment out there. Compressors, Fans, Controls etc will always fail but the Traulsen cabinets were built like a tank. I still see and service units 30 and 40 years young.

  16. Likes trippintl0, bacciagalupe liked this post.
  17. #15
    Join Date
    Dec 2008
    Posts
    8
    Post Likes
    Thread Starter
    The relay problem is fixed -- it was simply wired backwards. Now the fan goes on whenever either side is on. I am still trying to figure out if it would screw things up to rewire it to run the condenser fan in line with the compressors. Otherwise, I might think about BLDC fan motors for this thing.

    Thanks for the interesting history. You can still get the 48 inch version (now, the "Space Saver" line), although no longer with an ice maker. I don't think they can get them efficient enough to market them to the residential market, even though that is really what they were designed for.

  18. #16
    Join Date
    Jul 2011
    Posts
    2
    Post Likes

    Thread closest to my problem: condenser fan runs constantly

    Hi all: I'm hoping some of the solvers of the last issue with a similar can help me here. I have a URS48DT, and the way the condenser fan relay is wired, for the life of me I can't see how the fan is supposed to ever go off. Surely it is supposed to though, when neither compressor is runnign?

    I have a wiring diagram Traulsen sent me for the UR48DT, and it correctly shows the relay coil energized by the thermostat. But my URS has such a different rats nest, I can't tell if it's supposed to be like that, or if it was wired wrong. I've tried trial-and-error swapping of the relay coil, NO and NC connectors, but the fan keeps running, independent of the thermostats being on or off.

    a) There wouldn't be a relay if the fan on the URS was supposed to keep running, right?
    b) Does anyone have a URS48DT wiring diagram?

    Help?!

  19. #17
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    Quote Originally Posted by pecmsg View Post
    This is a Traulsen design. At the time they were trying to compete with Sub-Zero for the residential market.

    The first design used a static condenser mounted on the back with a 1” X 6” squirrel cage fan on a rheostat blowing from the top down. (Without the fan the compressors were over heating.) This same model had the freezer evaporator in the walls of the freezer. It was a lot of fun telling a customer that just paid 4g’s (mid 80’s $) that the freezer was a manual defrost. Along with the compressor noise issue this model was soon put to rest.

    The new design used Tecumseh AE4440 & 4430 pumps (I believe) with a 2 circuit condenser coil-1 fan. These are not Tecumseh condensing unit’s just there compressors. Everything wrapped with insulating sheets to keep the noise down. (even they learned by there mistakes and did away with the in wall evaporator)Unfortunately they couldn’t compete with Sub-Zero and the others and the entire line was dropped.

    Old man Traulsen, yes that was his name, started as a tech (mechanic as us old farts used to be called) and built the company. He took pride in seeing his name all over the world.
    As a young mechanic I was sent to his apartment on 5th Ave in Manhattan. Getting off the service elevator there was no question which door was his. All Stainless Steel with the same Traulsen label.

    There is no better manufactured piece of refrigeration equipment out there. Compressors, Fans, Controls etc will always fail but the Traulsen cabinets were built like a tank. I still see and service units 30 and 40 years young.
    Cool story.

  20. #18
    Join Date
    Nov 2012
    Posts
    2
    Post Likes
    Could I possibly get the wiring diagram from you. Thank you

    Manuel

  21. #19
    Join Date
    Jul 2011
    Posts
    2
    Post Likes
    Attached. The (rather untidy) blue add-ins are for the relay I added to stop the condensor fan running when both compressors were off. Good luck.
    Quote Originally Posted by mxavierr View Post
    Could I possibly get the wiring diagram from you. Thank you

    Manuel
    Attached Images Attached Images

  22. #20
    Join Date
    Nov 2012
    Posts
    2
    Post Likes
    Thank you.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •