Thread: To use sight glass or not

  1. #1
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes

    To use sight glass or not

    ISo the other day I had a walk in cooler low on gas. R22 to be exact, I found and fixed two leaks. Had a coworker bring me some more r22. After installing a new fan cyce control begain charging the unit. Got the box to 42° with a 20° superheat and then box was down to 38° when I left.

    Ive always been told to keep a full glass to ensure all liquid to txv. Manager says to charge to the correct superheat and not worry how full the glass is and coworker says only with R22 you should charge to a full glass

  2. #2
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    First of all, does this have a headmaster or just a fan cycling control? Also remember a sight glass is a tool, like any other tool you need to know when to use it and and what it's telling you.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    A TEV MUST have a solid column of liquid to it in order to properly meter refrigerant.

    I would install a sightglass on any equipment with a receiver.


    I would NOT "charge to superheat" This is incorrect procedures for any walk-in that I've ever worked on.



  4. #4
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes
    Thread Starter
    No headmaster just fan cycle and yes it does have a sight glass

  5. #5
    Join Date
    Jan 2009
    Location
    IRELAND
    Posts
    55
    Post Likes
    Problem with fan cycling on single units is it plays havoc with sight glasses .if fan speeds up quickly its drops condenser pressure quickly and pulls liquid back into condenser and bubbles in the sight glass,very easy to overcharge system using sight glass on this scenario.Most of the fan controls on single units i come across tend to ramp up and down very quickly

  6. #6
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by marter View Post
    Manager says to charge to the correct superheat and not worry how full the glass is and coworker says only with R22 you should charge to a full glass
    If the TXV does not have a solid column of liquid to work with, how is it supposed to maintain a 'correct superheat'?
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  7. #7
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes
    Thread Starter
    I understand this but he signs the paycheck.

  8. #8
    Join Date
    Mar 2006
    Posts
    1,135
    Post Likes
    Thread Starter
    A field installed unt no weigh in charge, you would have to have some type of head pressure control to handle low ambient tempreture though.

  9. #9
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by marter View Post
    I understand this but he signs the paycheck.
    You don't have to prove a flashing sight glass via a picture, I would hope. Why can't you properly charge the unit (clear the sight glass) AND keep the boss happy by simply saying you charged the unit to XX superheat?

    Quote Originally Posted by marter View Post
    A field installed unt no weigh in charge, you would have to have some type of head pressure control to handle low ambient tempreture though.
    Headmaster would be the way to go.
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by markettech View Post
    You don't have to prove a flashing sight glass via a picture, I would hope. Why can't you properly charge the unit (clear the sight glass) AND keep the boss happy by simply saying you charged the unit to XX superheat?
    Bingo!

    Do the right thing and tell the bossman what he wants to hear.



  11. #11
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    There's a way to respectfully argue your point to the boss who you work for. Have your facts straight (which you are trying to do by being here) and just state your disagreement and back it up with why. Explain you will make him more money by doing it the right way the first time.

  12. #12
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    If fan cycling is throttling my pressure up & down, first I make sure the fan control is set up as accurately as possible for the refrigerant being used. Then I try and maintain a head pressure of 180 (R22) maybe using a piece of cardboard to partially cover the condenser and then can watch the sight glass and clear it at this point. If I still see bubbles at a lower head say 160psi, I might add small amount more but being careful not to over charge. I don't even call the boss. I am the boss...

  13. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,576
    Post Likes
    Quote Originally Posted by marter View Post
    I understand this but he signs the paycheck.

    and when the call comes back in you were the tech who worked on it last...

    Try blocking off the condenser like Capz suggested
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  14. #14
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    3,111
    Post Likes
    All ways an interesting one.
    As stated above a sight glass is a tool and used as an aid to charging, generally speaking your pure refrigerants, are normally better than mixtures using a sightglass method. (with mixtures very small pressure drops, valves, driers etc. can cause bubbles) At times of very high load, it sometimes difficult to get a full sightglass when the valve is 100% open especially the TXV is slightly on the larger size of the required duty.
    Superheat is also a good method, but normally only when your room or product (one pass chillers) is close to set point.
    So it more down to understand at what stage your system is at and what condensing control you have. (also stated above)

  15. #15
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    The only time you cant use a sight glass is when you have a headmaster , because even after the sight is cleared you still need to add a little more , and there is a procedure for measuring that amount.

  16. #16
    Join Date
    Feb 2008
    Posts
    96
    Post Likes
    This one never goes away.......it depends on what type of system you are working on. The answer to this question is always yes. However, it depends on what type of system you are working on. The debate rages on that if you have a full column of liquid in the liquid line you should have a clear sightglass. On cap tube systems, due to may reasons, the sightglass may always flash and never clear. There is a better reason to use a sightglass on systems. And that is for moisture reasons. I have my guys install sightglasses on all refrigeration systems for this very reason. On top of that, they are a great way to visually check the refrigerant charge on any system along with any moisture issues. Although charging by superheat on cap tubes in the best way, second to weighing in the charge, I don't think charging a system by superheat, let alone sub-cooling is the correct way either. What is the correct way? By using the recommended refrigerant charge on the piece of equipment. If no tag is available, then I usually just let the system equalize after a recovery, pressurization, deep vacuum and let the refrigerant fly in under pressure until equalization occurs. You will be pretty close to a full charge. As far as sightglasses on ice machine, I recommend installing them for moisture indication purposes and a quick visual check of a refrigerant charge. MOST of the time, a clear glass is a full or overcharged system.

  17. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    I never see a sight glass on cap tubes , i usually have to bring out the crystal ball

  18. #18
    Join Date
    Feb 2008
    Posts
    96
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    I never see a sight glass on cap tubes , i usually have to bring out the crystal ball
    Smart man

  19. #19
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    I never see a sight glass on cap tubes , i usually have to bring out the crystal ball
    Crystal ball? What's wrong, don't you have x-ray vision?

  20. #20
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    Quote Originally Posted by marter View Post
    Got the box to 42° with a 20° superheat and then box was down to 38° when I left.

    Ive always been told to keep a full glass to ensure all liquid to txv. Manager says to charge to the correct superheat and not worry how full the glass is and coworker says only with R22 you should charge to a full glass
    Your statements here raise a few questions:

    Did you charge to a full sight glass, or charge to superheat as your boss requires?

    In either case, why was the system operating with 20 deg superheat?

    What does your boss want the SH to be?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •