    Core tool help

    Need help on any ideas with a Rheem heatpump shearer core leaking. Valve core tool is too long and hits the suction line when trying to pull core out. Don't want to loose system pressure. Do they make any stubby versions of the vcrt?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Brass Cap?

  3. #3
    Join Date
    Oct 2007
    Location
    Broward County, FL.
    Posts
    675
    Post Likes
    Can you pump the system down and change the core?
    I miss you mom and dad.

  4. #4
    Join Date
    Jul 2010
    Location
    in a service van down by the river...........
    Posts
    564
    Post Likes
    Two pinch off tools???


    Sent through Tapatalk, even though they ruined it with "upgrades"...
    It's All about Heat.............................to a degree

  5. #5
    Join Date
    Nov 2008
    Location
    Piney Flats, Tn.
    Posts
    2,282
    Post Likes
    suction this time of year, just run it in cooling your suction pressure can't be more than 40#'s so with it running pull out the valve core, plug hole with one finger while getting new valve core ready and then install it. I did it this way for years before I found the valve core tool. Liquid line was a lot harder back then we were running high 200 to mid 300# pressures and some valves were not reusable (open only) plus being liquid it burnt. what you did then was turn off system and let pressures equalize, then change out valve core.

  6. #6
    Join Date
    Mar 2010
    Location
    Sunny SoCal
    Posts
    854
    Post Likes
    If this is on the line set access valves, can you unscrew one or the other assembly's from the unit (both if necessary) to gain adequate clearance?

  7. #7
    Join Date
    Mar 2010
    Location
    Rochester, NY
    Posts
    750
    Post Likes
    I have had the same problem with the VCRT on rheem units.What I did was unscrewed the service valves from the cabinet and carefully lift them up and out so I can get my VCRT on the schrader

  8. Likes beenthere, SkullMonkey liked this post.
  9. #8
    Join Date
    May 2004
    Location
    California
    Posts
    793
    Post Likes
    Quote Originally Posted by perfectionist View Post
    I have had the same problem with the VCRT on rheem units.What I did was unscrewed the service valves from the cabinet and carefully lift them up and out so I can get my VCRT on the schrader
    bingo.

  10. #9
    Join Date
    Jan 2013
    Location
    DFW (Texas)
    Posts
    398
    Post Likes
    I second the brass cap suggestion. Sometimes, it's the only immediate solution without getting into a load of other work.

  11. #10
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    550
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Brass Cap?
    x3
    If its easy to change use your core tool. If not a brass cap is a good solution. I recommend to the customer that it be replaced, but not all go fot it.
    I have recently started marking the troublesome caps with a paint marker.
    This also serves as a good reminder to wear gloves when taking caps off and hooking up gauges.

  12. #11
    Join Date
    Feb 2011
    Location
    Peoria, IL
    Posts
    3,002
    Post Likes
    x4 brass cap and put a o-ring in it. I put in Ruud trust me they suck for VRT's esp weatherking's

  13. #12
    Join Date
    Mar 2015
    Posts
    6
    Post Likes
    If it's a rheem classic then the only way I know is to pump the system down and then replace it with a short schrader core remover. One of the few features I don't like about the rheem Classic.

  14. #13
    Join Date
    Mar 2010
    Location
    Sunny SoCal
    Posts
    854
    Post Likes
    Quote Originally Posted by garychance View Post
    x4 brass cap and put a o-ring in it.
    I have to think that a copper flare gasket would work better.

  15. #14
    Join Date
    Jul 2013
    Location
    upstate NY
    Posts
    135
    Post Likes
    A flare nut with a bonnet works for me. Everyone finds their own way to the end.

  16. #15
    Join Date
    Mar 2007
    Location
    South Texas
    Posts
    239
    Post Likes
    if there is room install a swival tee with new schraders in the tee's

  17. Likes buford, SkullMonkey liked this post.
  18. #16
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    X2 on above, you cannot add a 90 deg access fitting on there? I do that all the time instead of pumping it down, just put on a add fitting with new core.make life simple. Then when and if you have to do major repairs deal with it then.

  19. Likes CleterD liked this post.
  20. #17
    Join Date
    Mar 2015
    Posts
    6
    Post Likes
    Not a bad idea fellas.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •