    Carrier Infinity 4 Ton - will I ever be happy

    I've been complaining about my 4 ton Carrier Infinity (24ANA748 condenser, Infinity thermostat) for years. Basic complaint - its just doesn't seem as cold as the old Goodman R22 system that it replaced, but I don't have any facts to back that up - I didn't obsess over the old system, it seemed to work fine, until I had to have it replaced.

    I've had a couple of different companies come out, but I guess I'm being stubborn.

    Had someone come out yesterday on a good hot day, and I asked for a good check and that I wanted to record the numbers.

    Outdoor dry bulb: 92.7F
    Outdoor humidity: 55%
    Evaporator return air temp: 79F
    Evaporator supply air temp: 65F
    Indoor wet bulb: 64F
    Indoor humidity: 53%
    Suction Pressure: 158psig
    Hi side Pressure: 360psig
    Suction Line Temp: 71F
    Liquid Line Temp: 94F
    Vapor Line Temp at the outlet of the evaporator: 66.5F
    1400 CFM (from the infinity Thermostat)
    Blower RPM: 1400 (from the Infinity thermostat)
    Static Pressure: .77 (from the Infinity thermostat)

    Required subcooling for this unit: 15F

    Calcuations based on figures above:
    Subcooling: 15
    Superheat (system): 16F
    Superheat(at the evap): 10F

    He took evaporator return/supply air temps near the air handler.

    So, as usual, he said everything is right on, but I can't understand the following:

    1) I guess that evaporator delta T is OK based on what he told me and from what I've read, but my downstairs R22 system sure does better
    2) That liquid line temp has always been at or just above outdoor ambient. This is subjective, but it just bugs me that when I reach over and "feel" the suction and liquid lines on my R22 condenser (downstairs unit), the liquid line is very warm and the vapor line is very cold (and sweating much more than the Carrier). Is that just a function of R22 vs R410a.
    3) Lastly should they be measuring air flow instead of just looking at the Infinity thermostat? I don't think I've ever seen anyone take a CFM measurement. More than one has said that the Carrier Inifinity adjusts blower RPM to maintain proper CFM.
    4) I've been told that these high efficiency units are designed that way (not as cold), but that just doesn't make sense either.

    Bottom line, if they are getting good subcooling and superheat values, is that the best I'll get out of this thing?

  2. #2
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    What is the model number of the indoor unit? What are the diameters of the refrigerant lines and the length? Is the indoor unit above / below the outdoor unit and how far?

    Let's start there.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter

    Carrier Infinity 4 Ton - will I ever be happy

    (Subject should have been: "Carrier Infinity 4 Ton - will I ever be happy)

    Air Handler/Furnace: 58VA110-1-20
    Evaporator: CNPVP4821ACA

    7/8 Suction Line
    3/8 Liquid Line
    (these were previously used for the R22 system, installer seemed to do a proper install job in 2008)

    Indoor unit about 25-30 feet above. I've estimated the lineset length to be about 60 feet.

    I've had concerns about the lineset:
    1) Two short radius 90degree elbows
    2) Two 45 elbows
    3) One mild kink. My main HVAC contractor said it probably wasn't hurting anything, but would fix for about $$$$. (I posted pictures of that kink here a few months ago - I think most said don't worry about it)

    Suction line is insulated well, I've check that (at least where I can see it).
    Last edited by jpsmith1cm; 06-22-2012 at 11:47 AM. Reason: Pricing

  4. #4
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    Couple more questions - During the hottest days what is the temp difference of the liquid line where it leaves the condenser VS where it enters the TXV?

    What was the room temp on the User Interface when he took the readings and is the system maintaining setpoint?
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  5. #5
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by rogressem View Post
    I've been complaining about my 4 ton Carrier Infinity (24ANA748 condenser, Infinity thermostat) for years. Basic complaint - its just doesn't seem as cold as the old Goodman R22 system that it replaced, but I don't have any facts to back that up - I didn't obsess over the old system, it seemed to work fine, until I had to have it replaced.

    I've had a couple of different companies come out, but I guess I'm being stubborn.

    Had someone come out yesterday on a good hot day, and I asked for a good check and that I wanted to record the numbers.

    Outdoor dry bulb: 92.7F
    Outdoor humidity: 55%
    Evaporator return air temp: 79F
    Evaporator supply air temp: 65F
    Indoor wet bulb: 64F
    Indoor humidity: 53%
    Suction Pressure: 158psig
    Hi side Pressure: 360psig
    Suction Line Temp: 71F
    Liquid Line Temp: 94F
    Vapor Line Temp at the outlet of the evaporator: 66.5F
    1400 CFM (from the infinity Thermostat)
    Blower RPM: 1400 (from the Infinity thermostat)
    Static Pressure: .77 (from the Infinity thermostat)

    Required subcooling for this unit: 15F

    Calcuations based on figures above:
    Subcooling: 15
    Superheat (system): 16F
    Superheat(at the evap): 10F

    He took evaporator return/supply air temps near the air handler.

    So, as usual, he said everything is right on, but I can't understand the following:

    1) I guess that evaporator delta T is OK based on what he told me and from what I've read, but my downstairs R22 system sure does better
    2) That liquid line temp has always been at or just above outdoor ambient. This is subjective, but it just bugs me that when I reach over and "feel" the suction and liquid lines on my R22 condenser (downstairs unit), the liquid line is very warm and the vapor line is very cold (and sweating much more than the Carrier). Is that just a function of R22 vs R410a.
    3) Lastly should they be measuring air flow instead of just looking at the Infinity thermostat? I don't think I've ever seen anyone take a CFM measurement. More than one has said that the Carrier Inifinity adjusts blower RPM to maintain proper CFM.
    4) I've been told that these high efficiency units are designed that way (not as cold), but that just doesn't make sense either.

    Bottom line, if they are getting good subcooling and superheat values, is that the best I'll get out of this thing?
    Your system is not performing anywhere near its capacity. Can you re-post the kink?

    Running low airflow your delta T should be with 53% rh closer to 18 and you suction line is picking up 6 degrees of SH

  6. #6
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    Today:
    Outdoor ambient: 91.5
    Liquid line temp @ condenser: 92-93
    Liquid line temp @ evap (just before entering casing): 92

    Used my old k-type, which seems to be accurate when compared to the fluke that the tech used because we compared them yesterday.

    Room temp yesterday on the User Interface when he took the readings was about 79-80. As far as holding set point, on those hot days, I would say no. Set to 78 and it drifts up to 79/80 and holds all day.

    I try to keep the downstairs thermostat set 1 degree below upstairs (very open area - both thermostats are in line of site of each other). It does a good job.

    Quote Originally Posted by comfortdoc View Post
    Couple more questions - During the hottest days what is the temp difference of the liquid line where it leaves the condenser VS where it enters the TXV?

    What was the room temp on the User Interface when he took the readings and is the system maintaining setpoint?

  7. #7
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    3,039
    Post Likes
    As second opinion posted the system does not seem to be operating at capacity. If the measurements are accurate, it is not at capacity. Are the LL temps you posted while the system is running? Does not make sense to me that the insulated suction line absorbs 5-6°, but the un-insulated LL does not change at all.

    I would be looking for leaking ducts - probably return, and temp increases in the LL. It is a long run not insulated.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    1400 CFM on a 4 ton should have a lot higher delta across the indoor oil.

    1400RPM? Its running on the governor. Not sure your control is giving accurate info.

  9. #9
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Required subcooling for this unit is 15 degrees f?

    Where did you get this number? The charging instructions should be on the condensing unit, so I would double check that 15 degrees sub-cooling. The sub-cooling required may vary depending on various conditions.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  10. #10
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    Yea, good catch, I typo'd that. RPM was 1036


    Quote Originally Posted by beenthere View Post
    1400 CFM on a 4 ton should have a lot higher delta across the indoor oil.

    1400RPM? Its running on the governor. Not sure your control is giving accurate info.

  11. #11
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    I'll double check those line temperatures tomorrow afternoon after the outdoor ambient warms up. Yea, those were running temps (I've questioned that LL temp at the condenser for a long time)
    I double checked my notes from what he got yesterday. (but he didn't get the LL temp up at the evap).

    I'll get LL and suction line temps at both places and post.

    Quote Originally Posted by comfortdoc View Post
    As second opinion posted the system does not seem to be operating at capacity. If the measurements are accurate, it is not at capacity. Are the LL temps you posted while the system is running? Does not make sense to me that the insulated suction line absorbs 5-6°, but the un-insulated LL does not change at all.

    I would be looking for leaking ducts - probably return, and temp increases in the LL. It is a long run not insulated.

  12. #12
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    Yea, thats what he told me, and I see it here (attached)

    Quote Originally Posted by tipsrfine View Post
    Required subcooling for this unit is 15 degrees f?

    Where did you get this number? The charging instructions should be on the condensing unit, so I would double check that 15 degrees sub-cooling. The sub-cooling required may vary depending on various conditions.

  13. #13
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    Here are the three pics from the original thread:
    1. http://hvac-talk.com/vbb/attachment....1&d=1330740981

    2. http://hvac-talk.com/vbb/attachment....1&d=1330740991

    3. http://hvac-talk.com/vbb/attachment....1&d=1330741003


    The contractor that installed this system (they didn't create the kink), said it was probably not worth fixing, but would do it for about $

    Got another quote, he would not fix it (its in the crawl space), but would run a new line set up the side of the house into the attic for about $ or so. That was reasonable, but I wasn't excited about the downspout dressing on the side of the house.



    Quote Originally Posted by second opinion View Post
    Your system is not performing anywhere near its capacity. Can you re-post the kink?

    Running low airflow your delta T should be with 53% rh closer to 18 and you suction line is picking up 6 degrees of SH
    Last edited by beenthere; 06-22-2012 at 09:45 PM. Reason: price

  14. #14
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by rogressem View Post
    Yea, good catch, I typo'd that. RPM was 1036
    Are you saying that the controller was reading 1036 cfm?

  15. #15
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    101
    Post Likes
    Thread Starter
    No, that was blower RPM
    CFM always reads 1400CFM, except when running 1st stage (can't remember that off the top of my head)

    Quote Originally Posted by second opinion View Post
    Are you saying that the controller was reading 1036 cfm?

  16. #16
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    In 2nd stage, with the return air conditions you posted, the temperature drop through the system should be right about 20ºF, give or take a couple of degrees, for a system moving 400 cfm/ton.
    According to your controller, the system is moving 350 cfm/ton, nominal airflow for a 4 ton system being 1600 cfm.
    At that airflow, I'd expect the temperature drop to be more in the range of 20 to 22ºF with the return air conditions given.

    Assuming all of the readings are correct, your system is operating way under capacity.
    Has it been determined beyond any doubt that the compressor is actually running in 2nd stage?
    The suction pressure is significantly higher than I'd expect to find in 2nd stage, it is more in line with what you would get with first stage compressor operation, and 2nd stage airflow.
    The head pressure seems a tad low for the outdoor temperature, another indication that the compressor may not be operating in 2nd stage.

    Is this one of the units with the Bristol TS compressor, or does it have the Copeland 2 step compressor?

  17. #17
    Join Date
    Nov 2004
    Location
    Austin, TX
    Posts
    909
    Post Likes
    The Infinity system is capable of giving you a temp drop of approximately 27 degrees when operating in comfort mode. It seems high but I've observed in on multiple occasions. The 1400cfm indicates it is operating in comfort mode. (350cfm per ton).
    360psi indicates a 107-108 p/t. With a 96 deg liquid line temp the subcooling = 11-12 deg.
    The report stated 15 degrees.

    You may be a little low on refrigerant since the data plate specifies 15 degrees.

    I'm not trusting his numbers. I've taken measurements at different points at the duct work and had a large variation. Eddies in the airflow near the evaporator coil can create cold spots. I've found checking supply air further downstream will sometimes point out a cold spot and thus an erroneous supply temp.
    I'd recheck the return temperature at the furnace and at the return grill. You could be drawing in air from leaking return duct. The relative humidity drop of only 2%? Hmm,

    A leak in the supply duct work can dump air outside of the conditioned space. To make up for the air loss the building will draw outside air into the structure. This will increase the load on the system and your ac will not hold setpoint on hotter days.
    This could explain a relative humidity drop of only 2 degrees.
    “I am for doing good to the poor, but...I think the best way of doing good to the poor, is not making them easy in poverty, but leading or driving them out of it. I observed...that the more public provisions were made for the poor, the less they provided for themselves, and of course became poorer. And, on the contrary, the less was done for them, the more they did for themselves, and became richer.”
    ― Benjamin Franklin

  18. #18
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by mark beiser View Post
    In 2nd stage, with the return air conditions you posted, the temperature drop through the system should be right about 20ºF, give or take a couple of degrees, for a system moving 400 cfm/ton.
    According to your controller, the system is moving 350 cfm/ton, nominal airflow for a 4 ton system being 1600 cfm.
    At that airflow, I'd expect the temperature drop to be more in the range of 20 to 22ºF with the return air conditions given.

    Assuming all of the readings are correct, your system is operating way under capacity.
    Has it been determined beyond any doubt that the compressor is actually running in 2nd stage?
    The suction pressure is significantly higher than I'd expect to find in 2nd stage, it is more in line with what you would get with first stage compressor operation, and 2nd stage airflow.
    The head pressure seems a tad low for the outdoor temperature, another indication that the compressor may not be operating in 2nd stage.

    Is this one of the units with the Bristol TS compressor, or does it have the Copeland 2 step compressor?
    It's the Bristol. A psychrometric calculation puts his capacity at somewhat less than 2 tons. I agree, it's running in first stage.

  19. #19
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    It's the Bristol. A psychrometric calculation puts his capacity at somewhat less than 2 tons. I agree, it's running in first stage.
    Yeah, I was thinking either a Bristol TS in 1st stage, or a 2 step scroll with a borked unloader.
    I'm not a Carrier guy, so don't know by the model numbers what they came with.

    The only 2 Infinity systems I've delt with were well after the customer gave up on the installing contractor. In both cases it was just minor stupid installation/setup details that were giving the system fits.

  20. #20
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by mark beiser View Post
    Yeah, I was thinking either a Bristol TS in 1st stage, or a 2 step scroll with a borked unloader.
    I'm not a Carrier guy, so don't know by the model numbers what they came with.

    The only 2 Infinity systems I've delt with were well after the customer gave up on the installing contractor. In both cases it was just minor stupid installation/setup details that were giving the system fits.
    It is the Bristol TS

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •