Page 1 of 4 1234 LastLast
Results 1 to 20 of 68
Thread: Carrier Infinity - poor performance high stage
    Just an update on this, or lack of update. (Carrier Infinity supply air temp goes up from low to high stage, suction pressure goes up - good performance at low stage) Original thread:
    http://hvac-talk.com/vbb/showthread.php?t=1113821
    My original installer (from 2007) is waiting on a response from the local Carrier technical representative. In the meantime, I've been taking careful return/supply air temps at the air handler (return duct at air handler and a few feet downstream of evaporator). I've taken them almost every day, early morning and middle of these hot afternoons and the numbers are pretty consistent. BTU performance from low to high stage is essentially constant. This morning:
    LOW STAGE:
    Return Dry Bulb: 71.8
    Return Wet Bulb: 58.7
    Supply Dry Bulb: 48.7
    Supply Wet Bulb:47.4
    Following 3 readings from Infinity Controller
    CFM: 882
    Blower RPM: 599
    Static Pressure: .24
    HIGH STAGE:
    Return Dry Bulb: 71.5
    Return Web Bulb: 59
    Supply Dry Bulb: 55.4
    Supply Wet Bulb: 52.7
    CFM: 1400
    Blower RPM: 960
    Static Pressure: .61
    Jul 2005
    The compressor isn't switching to second stage. Have your contractor correct the fault.
    Yea - long thread on that topic, and I guess that is what has prevented them from being able to quickly fix this. (and going to local Carrier for help). They've already noted that compressor amp draw goes from 5A to 10A (rough numbers) and head pressure goes up a few (<5) psig, suction pressure goes up about 10pisg. High stage contactor engages. So it seems to be switching, but just not performing as designed.
    I may have to ping on them again - haven't heard anything since Tuesday, but I'm sure they've been swamped with more critical repairs during this heat wave. At least it "sort of" works. Wish I could figure out how to make it stay in low stage, because I'm wasting money letting it run high stage.
    Quote Originally Posted by hvacrmedic View Post
    leland nc
    have they tried to slow the blower down to 1200 cfms and lower the sat temp in high stage
    sounds like an air flo problem more then a compressor problem IMO
    Quote Originally Posted by tinknocker service tech View Post
    I think on the Infinity systems with Infinity controller, that 1400 is by design, and is not adjustable other than 350cfm/ton when set to efficiency, 400cfm/ton when set to maximum. (this is a 4 ton system).
    SE Iowa
    I know on the newest version of Infinity controller there is a setting to force the unit to run only in low stage. You could then also set it to run at 400CFM (Maximum) with no dehumidification for a little more capacity for now.
    SE Iowa
    Do you mean airflow at the condenser?
    Airflow at he evaporator looks just fine. The blower isn't anywhere near maximum RPM. Static is probably <0.8".
    THe lowest you could force the indoor blower is 1300CFM unless you remove the infinity controller and use a regular thermostat and dip switches. However, if it's a ANA1, I think it will only run with an Infinity controller.
    SE Iowa
    Quote Originally Posted by rogressem View Post
    That CFM setting, on my system at least, can vary as well depending on outdoor temperature and humidity level. Mine runs an even lower CFM/ton on high stage over about 85F it seems.
    Jul 2005
    Efficiency is 400 cfm per ton. Maximum is 450 cfm per ton. Comfort s 350 cfm per ton. That's irrelevant since there's very little change in total capacity between those air flow settings. Your system is producing 2 tons in both first and second stage. If the high speed contactor is energized, then the compressor is broken, period. Another thread won't fix it.
    The Bristol 2 speed runs one piston in low stage and two pistons in high. In high stage the compressor rotation reverses and picks up the second piston, doubling its pumping capacity. When the mechanism is broken you get low stage capacity in both modes.
    Interesting thought there - I knew that about the Bristol/reverse direction compressor, but never thought about the mechanism that picks up the 2nd cylinder - being broken. I wonder if the amp draw would still double?
    At any rate, I will let them figure it out and I'll post the outcome here. Its been one of those where I've had a hard time convincing them something is wrong. (and no one took wet bulb temps until I did it and started doing comparisons between stages)
    p.s., my Infinity controller documentation reads:
    EFFICIENCY -- fixed airflow used to achieve specified ratings --
    no dehumidification airflow reduction. This is nominally 350
    CFM/ton, but will vary if a 2--stage outdoor unit is used.
    MAXIMUM -- 400 CFM/ton. No dehumidification airflow
    reduction
    But as you said, thats irrelevant for this issue.
    Will let everyone know what the outcome is.
    Jul 2005
    CFM/ton, but will vary if a 2--stage outdoor unit is used.o
    reduction
    Yes, I forgot for a moment that the cfm settings depend upon the indoor model. It's been a very long week, heck, make that a very long couple of months.
    Hope you get it worked out. I've only seen this fault twice, but I can just about guarantee that this is what has happened to yours, assuming that all of your data is accurate.
    leland nc
    didnt see the size of the unit so spoke to soon on cfm
    i do tend to feel there is an airflo issue
    Jun 2006
    Richmond, VA
    The bristol I found like that had the same amps in either stage.
    "Decidedly Superior in a twisted pathetic way".....
  14. #14
    Jul 2005
    Quote Originally Posted by beshvac View Post
    It could be that instead there's a busted discharge valve on the second cylinder. Either way the second piston doesn't seem to be providing any refrigeration effect.
    If any of you pros don't have or have access to a psychrometric program or calculator, then you should think about locating one. It'll save a lot of head scratching. I have one posted in the educational forums, and there are several psychrometric apps available from itunes and the android market. You could also just use a wet bulb/enthalpy table and the total capacity formula
    btuh total = 4.5 x cfm x ΔH
  15. #15
    SE Iowa
    I don't see a airflow problem. Even if it was the condenser fan not going to high speed, you're still get a significant increase in capacity, but high head pressures and high amp draw.
    IF inside airflow was a problem, you'd have low discharge air temps, not higher.
    It seems clear to me that it's not generating capacity.
  16. #16
    After all these service calls, if the intalling contractor hasn't figured out that the compressor is broken by now, Carrier should cut them off and not sell them anything more complicated than a single stage system until they get some remedial training for their technicians from an outside source...
  17. #17
    Jun 2005
    SW Wisconsin
    LOW STAGE:
    CFM: 882
    Blower RPM: 599
    HIGH STAGE:
    Return Web Bulb: 59
    CFM: 1400
    Blower RPM: 960
    Using the wet bulb temps & enthalpy chart I get 42,071.4-Btuh Low Stage &, 39,690-Btuh High Stage.
    Hope I didn't make an error...it's easy to do...4.5* CFM * enthalpy change. The Low Stage should not be higher than the High stage; maybe I made a mistake somewhere?
    If not; you got a real problem!
    Last edited by udarrell; 07-07-2012 at 03:48 PM. Reason: Low stage was a bit lower...
  18. #18
    Quote Originally Posted by udarrell View Post
    I think you got the enthalpy change to high.
    With the conditions listed, the first stage enthalpy change is 6.7 btu/lb, and 2nd stage is 3.927 btu/lb.
    Using that equation, 1st stage would be at 26,592 btu/hr, and 2nd stage would be at 24,740 btu/hr.
    The psychrometrics app I use is corrected for my local conditions, but the variation from standard should only be slight.
    The psychrometrics process calculator app I use, instead of that equation, gives slightly lower total capacity numbers, but they are within 1,500 btu/hr of the simplified equation.
    I like using the process calculator because it breaks out sensible and latent capacity.
    The way the system is operating now, it has higher total and latent capacity in 1st stage than in 2nd stage.
    In 2nd stage the sensible capacity is slightly higher, but there is almost no latent cooling being done.
    If there is a way to lock the system into only using 1st stage, I'd highly recommend doing so until the compressor is replaced.
  19. #19
    I got similar numbers (about 26,000 btu/hr) for both. I'm using that Psychometrics app for iphone/android (maybe the same one your using), which also seems to match the regular enthalpy charts that I see. I'm pretty much at sea level (+14 feet I think)
    I've been trying to figure out how to lock it in 1st stage until its fixed...not seeing a way to do that.
  20. #20
    Beginning to wonder that myself. I know this company has had some turnover lately, so I'm not sure how good their Carrier expertise is anymore (not a big company, so I know that must be a challenge).
    I've already been looking at the other factory authorized Carrier dealers in my area, but I was hesitant with starting over with somebody new. I've also been giving them a break during this heat wave - at least I have some cooling!