    multi level hussman deli case

    call came in as top shelf temping too high. other tech was out said it was because there was a register in ceiling above it and blowing heat down on it, recommended moving duct. I went there the case was at 50. found t stat set for 35 and open. turned down, cycled on.

    did find that the fan motor closest to sensing bulb seized up causing that part of coil to get colder with no air movement over it causing stat to cycle off. Replaced motor and cleaned out returns and even pulled case apart to clean off the deflectors going up the center. cycled case came down to temp several times. had mgr put product in and would return in morning.

    returned this morning and case at 37-38 but mgr says top tier is still temping at 41-48.
    I did not get the case model, bad me, but it is very similar to the RIN3 case

    Anything Im missing? any suggestions to get more air flow up to the top level.
    BTW there are 4 motors @ 12 watts ea.

    Thanks guys

  2. #2
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    sorry some info that was forgotten
    R-22 case with clear site glass running at 44psi couldnt get liquid pressure due to leaking stem on receiver..... which is going to be replaced in the morning

  3. #3
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Can you somehow cover or close off the air duct that is blowing hot air onto the top shelf? And let them try it for another day? Just because the other tech missed the fan motor doesn't mean he's wrong about the air duct.

  4. #4
    Join Date
    Dec 2011
    Location
    Southern Oklahoma
    Posts
    55
    Post Likes
    I have had some heater vent problems in cases but it seems it only affected old cases with missing honeycomb at the top. Island "coffin" cases seem really sensitive to heater air.

  5. #5
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    he disconnected the duct. and i relocated it down 4 feet or so. nothing blowing down on the case at this time

  6. #6
    Join Date
    Dec 2011
    Location
    Southern Oklahoma
    Posts
    55
    Post Likes
    Quote Originally Posted by mpr73 View Post
    call came in as top shelf temping too high. other tech was out said it was because there was a register in ceiling above it and blowing heat down on it, recommended moving duct. I went there the case was at 50. found t stat set for 35 and open. turned down, cycled on.

    did find that the fan motor closest to sensing bulb seized up causing that part of coil to get colder with no air movement over it causing stat to cycle off. Replaced motor and cleaned out returns and even pulled case apart to clean off the deflectors going up the center. cycled case came down to temp several times. had mgr put product in and would return in morning.

    returned this morning and case at 37-38 but mgr says top tier is still temping at 41-48.I did not get the case model, bad me, but it is very similar to the RIN3 case

    Anything Im missing? any suggestions to get more air flow up to the top level.
    BTW there are 4 motors @ 12 watts ea.

    Thanks guys
    Did you temp the top shelf high? I would probably put a logger in the case and inquire as to how he was temping it. If he uses an IR gun they can read bad wrong on shiny deli meat type packaging. If all your fans are good, coil isn't freezing, and the back is clear, you should have good airflow.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Your case is too friggen warm


    Set it down to 32 supply air or so.


    While you're at it, make CERTAIN that the product stocked is cold enough (below 35F)

    If it isn't you're BOTH wasting your time.



  8. #8
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    She was reading off of the dial thermometers that the store puts in. Not the most accurate but that is what they use. I placed my thermometer on the top shelf near the " column" or center part where the air comes up. I was reading 31. but as you move forward it is temping at 41, which is where they are leaving their thermometer. the top shelf is also noticeably warmer than the middle and low shelf, but of course the surface area for cool air to escape is twice the size of the upper

  9. #9
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    i have case set down to 28 or so on the stat to hold a mid 30 reading and i re stocked the case with product from the walk in at is at temp

  10. #10
    Join Date
    Dec 2011
    Location
    Southern Oklahoma
    Posts
    55
    Post Likes
    I usually run deli at about 32 which keeps me between their mandatory 35-41 range as long as they dont pack the shelves to tight.

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    OK. Since you don't have a model number, tell me more about this case.

    Describe it to me.

    Multi-deck deli describes a LOT of different cases.

    Is it a high-back case with 4 or 5 shelves? An island type case with 2-3 shelves?

    I need some more details to help you.

    While you're at it, try to remember the defrost schedule.

    Did you check SH?



  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by mpr73 View Post
    i have case set down to 28 or so on the stat to hold a mid 30 reading and i re stocked the case with product from the walk in at is at temp
    Not trying to be a jerk, but did you VERIFY that?

    If not, then it wasn't at temp.



  13. #13
    Join Date
    Mar 2010
    Location
    plano,IL
    Posts
    28
    Post Likes
    Thread Starter
    island style with 3 total levels. defrosts 6 times a day for 30 mins. I arrived on site 2 hours after the last defrost. and the clock was set fro the proper time.

    defrosts at 4, 8, 12 a/p

    the case is a hussman and very closely resembles the RI3N model

    I did check the supply temp getting down to 29-30 and middle and low shelf were at 35-36. Product came from the WIC which was also at 35

  14. #14
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    First off, I'm going to say too much defrost.

    A case like that will do fine with 4 a day, although you might need to stretch them out to 35 minutes or so.


    Those can be a royal pain to get to hold temp.

    You MUST cover all of the bases. Get your superheat down, your suction pressure is a bit high for a case like that. I'd like to see an evap down closer to 15-18 rather than 21.



  15. #15
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Did you check the honeycombs themselves? They can get a nice blanket of crap on top of them that will impede airflow quite a bit. I'd think the week holes in the back of the case may be able to keep the lower shelves at temp? Maybe?

  16. #16
    Join Date
    Sep 2006
    Posts
    186
    Post Likes
    Call hussmann and get case specs

  17. #17
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Here's the case specs for the RIN3:


    If the case in question is a different model, go to their search page here and enter the case model you have.

    The RIN3 calls for a 20ºF evap temp and 27ºF discharge air with 4 defrosts/day, time terminated at 20 minutes.

    Verify your store conditions are at or below 75ºFdb/55%RH.

    Also, the shelf sizing and load limits are critical on these cases.

  18. #18
    Join Date
    Oct 2009
    Location
    WI
    Posts
    112
    Post Likes
    We recently removed one of these cases because it would not hold temp on the ends.

    I agree with jp. Reduce the defrosts to 4x a day. 30min duration is plenty.

    As icemeister indicated, shelf sizing/placement and load limits are very critical in these island cases.

  19. #19
    Join Date
    Nov 2009
    Posts
    392
    Post Likes
    If you believe this case to be a Hussmann "RI" island case, the supply air spec is 26 - 27. In addition, there are several supply air metering plates inside the case that get plugged solid and need cleaned.
    Also, the defrost spec is 6 times (every 4 hours) / day for 20 minutes. I set the duration for 25 minutes given the region I am in. It is not "too much" defrost if the case is set down to the proper supply air temp and it builds the expected frost load on the coils.
    Last edited by thefreezerguy; 01-31-2012 at 01:55 AM.
    "Don't wish it were easier, wish you were better"

  20. #20
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    Quote Originally Posted by thefreezerguy View Post
    If you believe this case to be a Hussmann "RI" island case, the supply air spec is 26 - 27. In addition, there are several supply air metering plates inside the case that get plugged solid and need cleaned.
    Also, the defrost spec is 6 times (every 4 hours) / day for 20 minutes. I set the duration for 25 minutes given the region I am in. It is not "too much" defrost if the case is set down to the proper supply air temp and it builds the expected frost load on the coils.
    x2. These cases plug up with dirt faster than any other case in a supermarket. There is a horizontal baffle mounted in the 'tower' the same height as the pans and I would bet money it's plugged solid. You will need to remove all the bottom product and wash it out with a hose. A velometer is a must-have tool for working on cases.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •