Originally Posted by
Joe Harper
It all depends on who sets up the rack. You can run all the comps at the same pressure, or run a split suction header, with a common discharge. There are a few different ways to set this up. Running a common suction with regulating valves allows operator to set up defrost cycles to allow low temp cases to pull down after defrost, while med temp cases are going into defrost. The low temp cases can use a majority of the available hp to get back to setpoint.
A good example of what the op was referring to can been seen in Albertsons stores. They have an icecream cake case thathas to be kept at -20f. The low temp rack was di idwd into two main sections. A -12 group (for 0f cases), a -22f group (for -10f cases ex ice cream). The compressors used a split suction header and common liquid feed. Attached to the -22f group was a single compressor that ran the ice cream cake case. The case ran off of the common liquid, but suction was piped directly to the single compressor. Between the cake freezer and -22 suction header was a ori valve. This valve would open when the came creezer came out defrost. It would allow the -22 suction group pull on the case to bring the temp back down, and close off when the load was handled. I think this compressor ran at 10 or 12 psi. On 404a.
This whole system was flawed as the high temp rack powered a subcooler for low temp rack. If the high temp rack went down, so did the low temp. The low temp rack was under powered. Have seen this in 9 different stores. Ice cream is soft beacuse of weak valves on produce rack....