    Could one of the pro's do a quick comparison test with their manual j calcs to answer a question I have? Take any house that you have a manual j done on and leave everything the same except for the attic (with no ducts or air handler in attic) and see what happens to the load when you change from a vented attic with traditional insulation levels of fiberglass or cellulose on the attic floor(whatever the R-level is for your area) to an attic spray foamed at the roof with 3 inches of foam (closed cell and/or open cell). Which method results in a higher cooling load? Remember, no ducts in attic. Thanks to anyone willing to do this.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  2. #2
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    There is a button on the wrightsoft software called encapsulated. It always reduces the load in Florida heat to eliminate duct gain completely. R-8 flex reduces substantially the load on a conventionally insulated home.

  3. #3
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,755
    Post Likes
    It also depends on the sealing level of the air ducts and equipment.
    Another factor is the climate.

    The Manual J v.7 which I use for retrofits, assumes a 15% duct heat gain for ducts in the attic. That served me well for the past 30 years. I did get bit one time on a flat roof house that I downsized 1/2 ton. The problem was excessive duct leakage and the ducts were not accessible. I had to replace the unit with the original size. (before Aeroseal.)
    "I have never let my schooling interfere with my education."
    Mark Twain
    NEVER STOP LEARNING.

  4. #4
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    ummm, he said nothing about ducts, well the op did. there are no ducts nor equipment in attic.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  5. #5
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Thread Starter
    Quote Originally Posted by tipsrfine View Post
    Could one of the pro's do a quick comparison test with their manual j calcs to answer a question I have? Take any house that you have a manual j done on and leave everything the same except for the attic (with no ducts or air handler in attic) and see what happens to the load when you change from a vented attic with traditional insulation levels of fiberglass or cellulose on the attic floor(whatever the R-level is for your area) to an attic spray foamed at the roof with 3 inches of foam (closed cell and/or open cell). Which method results in a higher cooling load? Remember, no ducts in attic. Thanks to anyone willing to do this.
    ?
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by tipsrfine View Post
    ?
    that's what I was screaming, you said no ducts or equipment in attic, and have 2 answers that factor duct leakage in the attic. People are quick to answer yet fail to read and comprehend.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  7. #7
    Join Date
    Sep 2008
    Location
    New York
    Posts
    167
    Post Likes

    attic insulation

    1300 sf attic
    R38 in the ceiling S=12705 btuh L= 2916
    R35 encapsulated S=12172 L= 2916

    Climate zone 6A

  8. #8
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Thread Starter
    Quote Originally Posted by tipsrfine View Post
    Could one of the pro's do a quick comparison test with their manual j calcs to answer a question I have? Take any house that you have a manual j done on and leave everything the same except for the attic (with no ducts or air handler in attic) and see what happens to the load when you change from a vented attic with traditional insulation levels of fiberglass or cellulose on the attic floor(whatever the R-level is for your area) to an attic spray foamed at the roof with 3 inches of foam (closed cell and/or open cell). Which method results in a higher cooling load? Remember, no ducts in attic. Thanks to anyone willing to do this.
    R-35 with 3 inches of foam sprayed at the roof???????
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  9. #9
    Join Date
    Sep 2008
    Location
    New York
    Posts
    167
    Post Likes

    3" R6 foam

    1300 sf attic
    R38 in the ceiling S=12705 btuh L= 2916
    R18 encapsulated S=12637 L= 2916 (3" of R6 foam)

    Climate zone 6A

  10. #10
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Thread Starter
    Quote Originally Posted by tlj000 View Post
    1300 sf attic
    R38 in the ceiling S=12705 btuh L= 2916
    R18 encapsulated S=12637 L= 2916 (3" of R6 foam)

    Climate zone 6A
    Thanks, I appreciate it. It really makes me think I need to buy the software and learn it well. It seems one could use it as a sort of learning tool simply by making small changes such as you did with this, and then investigate WHY the program made the changes to the loads.
    I wonder how the program interpreted "3 inches of foam". Does it consider that the raftors are completely encased in 3 inches also, and not factor in the conductive gains through them? I mean, take all the raftors and put them together and you have a large area that only has an R-1.
    I can see why this tool, like all other tools, is only as good as the person using it. I certainly can't see relying on a calc prepared by someone who has little experience using it. Thanks again.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  11. #11
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Interesting thread... I have done a few 'foam' homes.

    The homes I did had either 2x10 or 2x12 roof rafters, filled. The difference was amazing!

    One thing to be careful with foam homes: MUA! Is there enough air to allow the fireplace to draft? Is there enough air to allow the kitchen vent to exhaust? Is there enough air to allow the bath fans to exhaust? When one opens or closes a door, will it fight you because the house is too tight?

    We had to use ERV's (one for each system) to make up for an over tight house... worked well.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  12. #12
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Interesting thread... I have done a few 'foam' homes.

    The homes I did had either 2x10 or 2x12 roof rafters, filled. The difference was amazing!

    One thing to be careful with foam homes: MUA! Is there enough air to allow the fireplace to draft? Is there enough air to allow the kitchen vent to exhaust? Is there enough air to allow the bath fans to exhaust? When one opens or closes a door, will it fight you because the house is too tight?

    We had to use ERV's (one for each system) to make up for an over tight house... worked well.
    When dealing with very air tight homes, I would suggest using make-up air ventilation instead of balanced ventilation to give the clothes drier, kitchen hood, and bath fans a chance of getting some air to function. Balanced flow ERV exhaust as much as they supply. This does nothing to help exhaust devices.
    Most occupants do not realize the importance of continuous fresh air ventilation for purging the pollutants and renewing oxygen. They tend not operate the ventilating during the warm months when it is needed the most. Properly ventilated homes will be damp during the shoulder seasons unless you have a whole house dehumidifier to maintain <50%RH during low/no cooling loads.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  13. #13
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    1,221
    Post Likes
    These foam houses really do not impress me so far. Especially if u need an ERV or even worse a dehumidifier. Seems u just need more equipment to deal with the tightness of the home. Then u got to maintain / repair this additional equipment.

    If I built again dont think I would use foam. JMO

  14. #14
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by Timber View Post
    These foam houses really do not impress me so far. Especially if u need an ERV or even worse a dehumidifier. Seems u just need more equipment to deal with the tightness of the home. Then u got to maintain / repair this additional equipment.

    If I built again dont think I would use foam. JMO
    Here in the Atlanta area... I know a couple of spec builders.

    They do the roof (under the roof) with foam, then use conventional insulation in the walls. The result seems to work out as a good compromise.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  15. #15
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    1,221
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Here in the Atlanta area... I know a couple of spec builders.

    They do the roof (under the roof) with foam, then use conventional insulation in the walls. The result seems to work out as a good compromise.
    Do you still need the ERV's / vetalation / or dehumidifiers ? If not, then I would consider that option.

  16. #16
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by Timber View Post
    Do you still need the ERV's / vetalation / or dehumidifiers ? If not, then I would consider that option.
    Mostly no. Depends on how tight one builds the house... but generally no.

    The main thing about a foamed attic (under the rafters) is not having that 'oven' just above the ceiling of the upper floor.

    Hope this helps.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  17. #17
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by Timber View Post
    These foam houses really do not impress me so far. Especially if u need an ERV or even worse a dehumidifier. Seems u just need more equipment to deal with the tightness of the home. Then u got to maintain / repair this additional equipment.

    If I built again dont think I would use foam. JMO
    Any well built home needs fresh air ventilation to pruge indoor pollutants and renew oxygen during the calm warm weather. Even worse, supplemental dehumidication is needed in green grass climates if you want the best in comfort and avoid growing mold/dust mites.
    ASHRAE, American, Lung ASS, EPA and most modern building codes suggest mechanical fresh air ventilation for the above reasons.
    The posters on this site represent traditional opinion not the building research community. Check out the above IAQ experts or researchers like Building Science.com for the state of the art specifications.
    It hard to part with tradition when dealing a changing industry.
    I have been involved with IAQ for 25 years and find is hard to believe how difficult is has been to get the concept of controlled fresh air ventilation and real humidity control in a modern well built home.
    Good luck on getting a quality home to live in.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  18. #18
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    TIPS, I've yet to see load, modeling or any cost/benefit software that can accurately reflect the energy or load impact of foam.

    As you may be seeing in these threads, guys talk about going to foam houses on 100f days and the equipment doesn't run once the whole time they are there. That indicates gross oversizing to me, how about you?

    Quote Originally Posted by teddy bear View Post
    Good luck on getting a quality home to live in.
    Regards TB
    Since you were considerate enough to respond I guess I'll drop in behind you.

    I think when people don't do or ask what the numbers are, they're defining their ability to make smart decisions.

    Some would rather pay $2 per sf/year for energy than $0.25 per sf/year for energy and $0.50 per sf/year for the increased mortgage for the better home. To me that's living in a crappy home and throwing away $1.25 per sf a year.

    The difference between ignorance and stupidity is ignorance doesn't yet know, stupidity doesn't have the capacity to know.

  19. #19
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by tedkidd View Post
    TIPS, I've yet to see load, modeling or any cost/benefit software that can accurately reflect the energy or load impact of foam.

    As you may be seeing in these threads, guys talk about going to foam houses on 100f days and the equipment doesn't run once the whole time they are there. That indicates gross oversizing to me, how about you?



    Since you were considerate enough to respond I guess I'll drop in behind you.

    I think when people don't do or ask what the numbers are, they're defining their ability to make smart decisions.

    Some would rather pay $2 per sf/year for energy than $0.25 per sf/year for energy and $0.50 per sf/year for the increased mortgage for the better home. To me that's living in a crappy home and throwing away $1.25 per sf a year.

    The difference between ignorance and stupidity is ignorance doesn't yet know, stupidity doesn't have the capacity to know.
    Sometimes stupidity knows and does not care... I hate to see that... but it is out there.

    I cannot tell you the number of folks that say: Gee, it will not pay back in a year... why bother. Amazing IMO.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  20. #20
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    The homes we have done were so tight they really needed a dehumidifier to remove moisture. An 85 degree day was simply not enough to cause the units to run with the stat set at 78. Gross oversizing?

    Well even 2 stage units are "grossly oversized" on a light load day with a homeowner who doesn't have thermostat set as low as the "design conditions" were determined in the load calc.

    Not to mention that big oak tree on the west side of the house that reduces the load by 3/4 ton in some circumstances. Needless to add, the load calc is a great tool, but it does not answer all things.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •