    trane install problem

    installer called me today couldnt get new trane 90% two pipe system to fire. had pressure switch failure. walked him thru a few things and we got it fired by pulling the intake air pipe. dont understand why,both intake and exhaust pipes are new, and each total 70' total length w/90s added into that total. installation manual allows 100'. gonna call trane in the morning but woul like to hear any of your ideas on this
    thanks,
    scott

  2. #2
    Join Date
    Oct 2006
    Posts
    23
    Post Likes
    What size pipe did you use?

  3. #3
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes

    :)

    That's what she said

  4. #4
    Join Date
    Oct 2007
    Location
    Mount Gilead, Ohio
    Posts
    170
    Post Likes
    Thread Starter
    3" pipe. h/o had same problem with old furnace. Called trane and they are stumped, they are coming out to look. Ill let you all know what the verdict is
    Thanks

  5. #5
    Join Date
    Mar 2003
    Location
    North St Paul MN
    Posts
    857
    Post Likes
    Was the pipe stored outside prior to install? It could be plugged from birdnest, or debris, and installers didn't notice an obstrution before they put it in.
    I'd rather have a bottle in front of me, than a frontal lobotomy.

  6. #6
    Join Date
    Nov 2004
    Location
    Cincinnati, Ohio
    Posts
    74
    Post Likes
    Quote Originally Posted by in-trane-ing View Post
    3" pipe. h/o had same problem with old furnace.


    Here is a big clue.....I assume you are also using existing pvc flue.

  7. #7
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    If the old furnace had the same problem it should make it easy to find. It has to be something in the pipe, or the way it was installed.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  8. #8
    Join Date
    May 2005
    Location
    Western Kansas
    Posts
    267
    Post Likes
    Make sure the vents are correct, then use a magnhelic gauge to test the pressure switch. With that length of a run, it may be as simple of a fix as a high altitude pressure switch. I live at around 3000 feet and was having a problem with one during a low pressure storm system. Called Trane and they said I was on the border line, they sent out a different one and it worked. Went back a few days later and just for giggles tried the old one after the system moved out and it worked fine.

  9. #9
    Join Date
    Oct 2006
    Location
    Vallejo, CA
    Posts
    154
    Post Likes
    Quote Originally Posted by tinmantu View Post
    Make sure the vents are correct, then use a magnhelic gauge to test the pressure switch. With that length of a run, it may be as simple of a fix as a high altitude pressure switch. I live at around 3000 feet and was having a problem with one during a low pressure storm system. Called Trane and they said I was on the border line, they sent out a different one and it worked. Went back a few days later and just for giggles tried the old one after the system moved out and it worked fine.
    DITTO!

  10. #10
    Join Date
    Oct 2007
    Location
    Mount Gilead, Ohio
    Posts
    170
    Post Likes
    Thread Starter
    Quote Originally Posted by markco View Post
    Was the pipe stored outside prior to install? It could be plugged from birdnest, or debris, and installers didn't notice an obstrution before they put it in.
    cut pipe to look for obstructions but found none,
    thanks

  11. #11
    Join Date
    Oct 2007
    Location
    Mount Gilead, Ohio
    Posts
    170
    Post Likes
    Thread Starter
    Quote Originally Posted by sinsee View Post
    Here is a big clue.....I assume you are also using existing pvc flue.
    new pipe

  12. #12
    Join Date
    Oct 2007
    Location
    Mount Gilead, Ohio
    Posts
    170
    Post Likes
    Thread Starter
    Quote Originally Posted by tinmantu View Post
    Make sure the vents are correct, then use a magnhelic gauge to test the pressure switch. With that length of a run, it may be as simple of a fix as a high altitude pressure switch. I live at around 3000 feet and was having a problem with one during a low pressure storm system. Called Trane and they said I was on the border line, they sent out a different one and it worked. Went back a few days later and just for giggles tried the old one after the system moved out and it worked fine.
    never heard of this but something to look into, but not sure if that is it because when they did get it to fire w/ the pipe on the burners wouldnt like right due to starvation of combustion air. I havent heard if Trane has showed up yet to the job. Ill let you all know when I find out
    Thanks again

  13. #13
    Join Date
    Mar 2007
    Location
    Kansas City
    Posts
    32
    Post Likes
    What about running the last third of pipe in 4 inch diamater
    How many 90's? Were they long radius?

  14. #14
    Join Date
    Sep 2006
    Posts
    41
    Post Likes

    Hmm

    A short radius elbow is equivalent to 10' of 3" pipe. A long radius is equivalent to 6' of 3" pipe. Do you still come up with your 70'?

  15. #15
    Join Date
    Oct 2007
    Location
    Mount Gilead, Ohio
    Posts
    170
    Post Likes
    Thread Starter
    4 long radius 90s figured at 5' each so w/ your formula 74' I have not seen the install yet but im sure im gonna end up w/ this one. Install dept always turns there problems over to service

  16. #16
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Quote Originally Posted by tinmantu View Post
    Make sure the vents are correct, then use a magnhelic gauge to test the pressure switch.
    Absolutely.

    I find it hard to believe TRANE is sending a factory guy out without someone at least giving up actual pressure measurements. What is your pressure and what is the switch rated at?

    Look, by pulling the fresh air you actually would decrease the negative pull on the furnace's HX, not improve it. However if your vent is restrictive, you may have hit full blower curve on the inducer indicating something is wrong with either a sag, an obstuction, short sweeping ells, or simply too long. You may also be trying to vent into a head wind.
    Last edited by docholiday; 11-09-2007 at 10:43 PM.

  17. #17
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes

    Pipe termination

    Many installers today dont look at instructions. I would guess that if all the piping is new, then the problem is how the piping terminates, IE exaust to close to intake, causing reduced pressure differential to satisfy the pressure switch.

  18. #18
    Join Date
    Nov 2007
    Location
    NC
    Posts
    145
    Post Likes
    Is it possible that on the new installation a screen of some sort was added to the end of the flu pipe. I've had a install crew put a screen on that did not allow enough air to flow out and kept kicking out the pressure switch.

  19. #19
    Join Date
    Mar 2003
    Location
    North St Paul MN
    Posts
    857
    Post Likes
    Quote Originally Posted by sandpipertech View Post
    Is it possible that on the new installation a screen of some sort was added to the end of the flu pipe. I've had a install crew put a screen on that did not allow enough air to flow out and kept kicking out the pressure switch.
    A good point sandpipertech, but if they haven't fixed it by now, theyr'e probably froze to death......this thread is 1 1/2 years old.
    I'd rather have a bottle in front of me, than a frontal lobotomy.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •