    I have a problem with the CIR A on the 30RBA unit, the EXV remains open 100% all the time, there is adequate refrigerant in the system, checked all the transducers and thermistors and found to be OK. Tested the EXV on test mode and it appears to be working OK on both 0% and 100%. As of now I dont have any answers to the problem. Appreciate if someone can give me some indicators for troubleshooting.

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,845
    Post Likes
    I would ask that you post a complete set of logs of the chiller. In return this will help us help you.