    what should my superheat be for 404a at 38 f box temp

  2. #2
    Join Date
    Dec 2009
    Location
    Montreal,Québec, Canada
    Posts
    9
    For med temp. 6 to 8 Degree of superheat as a general rule. OEM sometimes publish a value.

  3. #3
    Join Date
    May 2011
    Location
    Upstate New York
    Posts
    17
    Hello, I am new to the site, but just wanted to clarify that your superheat is being taken at the evaporator out let and not the compressor inlet??

  4. #4
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    471
    Quote Originally Posted by Btech View Post
    Hello, I am new to the site, but just wanted to clarify that your superheat is being taken at the evaporator out let and not the compressor inlet??
    Yes, that is correct. At the bulb location for the TXV to be exact.

  5. #5
    Join Date
    May 2011
    Location
    Upstate New York
    Posts
    17
    Quote Originally Posted by Tremblay View Post
    For med temp. 6 to 8 Degree of superheat as a general rule. OEM sometimes publish a value.
    I agree, make sure box is within temp range 10 degree max..

  6. #6
    Join Date
    Dec 2011
    Location
    USA
    Posts
    66
    On a medium temperature application the 6-8 is correct. The closer you get to the 6 the better the efficient the unit will run saving the costumer energy.

  7. #7
    Join Date
    Dec 2009
    Location
    Montreal,Québec, Canada
    Posts
    9
    The problem with Superheat is that you can only get a range. As technician we tend to have a fix value but there are too many variables: TD, liquid temperature, evaporator's dynamic.

    So a superheat amplitude of 6-8 is the target but it may vary with applications.

  8. #8
    Join Date
    Sep 2011
    Location
    BC, Canada
    Posts
    34
    I was told from an old tech in trade school that rule of thumb was to go with 5 degree for low temp applications, 10 degree for med temp applications, and 15 for high temp applications.

  9. #9
    The best way to do this is by checking your superheated at the compressor.
    Depending on how far the compressor is from the case or box, the condition of the insulation on the suction line and were the pipe is ran ( overhead under the roof or underground).
    This is why superheated does not matter. What matters is the proper cooling of the compressor. I had to work with several systems where the superheat needed to be set to 1 df in order to provide proper cooling to the compressor
    Check your comp specs. It's usually 60-65 df max suction line temp at compressor on the medium temp and 25df on low temp

  10. #10
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,568
    Quote Originally Posted by .:JJ:. View Post
    This is why superheated does not matter. What matters is the proper cooling of the compressor.
    Superheat at the coil is VERY important. Imagine you have a system with a long piping run in a ceiling under a roof. On a sunny hot day, you check compressor superheat and find it too high. To compensate, you open the TXV farther. Now compressor superheat is good. However, you may have just set the valve to 0 degrees superheat and are feeding liquid into the suction line. Under the current operating conditions this is OK because it al vaporizes before getting to the compressor. However, as soon as the temp in the ceiling drops, the load on the line is going to go down and you will have floodback.


    Its important to set the TXV at the superheat recommended for the application, then verify the superheat at the compressor is within manufacturers recommendations. If it is too high it should be addressed with additional insulation, a desuperheating valve, or other measures.

  11. #11
    Join Date
    May 2003
    Location
    Utah
    Posts
    743
    Quote Originally Posted by .:JJ:. View Post
    The best way to do this is by checking your superheated at the compressor.
    Depending on how far the compressor is from the case or box, the condition of the insulation on the suction line and were the pipe is ran ( overhead under the roof or underground).
    This is why superheated does not matter. What matters is the proper cooling of the compressor. I had to work with several systems where the superheat needed to be set to 1 df in order to provide proper cooling to the compressor
    Check your comp specs. It's usually 60-65 df max suction line temp at compressor on the medium temp and 25df on low temp
    I will respectfully disagree with your position here.

    The TEV is not designed to regulate superheat at a location that is downstream from the sensing bulb location. It is impossible for any valve requiring temperature and pressure to regulate its adjustment to maintain a condition somewhere other than where it is sensing temperature and pressure at.....that would be the height of lunacy to expect a valve to regulate at some location in the system other than where it is sensing the condition it is attempting to regulate.

    In addition, there are so many variables (load, ambient conditions, etc) that will change the refrigerant mass flow requirement necessary to properly feed the evaporator that what might seem to be a decent compressor superheat at one operating condition might be extremely low at another....again, the TEV is not designed to regulate superheat at a location other than the bulb location.

    To repeat.....the TEV is designed to maintain superheat at the bulb location only. Once this is set correctly, IF the compressor superheat is too high it must be addressed in another manner such as liquid injection.

  12. #12
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,853
    Quote Originally Posted by bunny View Post
    I will respectfully disagree with your position here...

    .....that would be the height of lunacy...



    Quote Originally Posted by bunny View Post
    To repeat.....the TEV is designed to maintain superheat at the bulb location only. Once this is set correctly, IF the compressor superheat is too high it must be addressed in another manner
    This
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  13. #13
    Join Date
    May 2003
    Location
    Utah
    Posts
    743
    Quote Originally Posted by 2sac View Post




    This
    Well, don't beat around the bush. If you've got a problem with the content of my post then spell it out.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event