    I have 3-zoned hot water baseboard heating system via a Burnham gas boiler. Recently I have been having to bleed my upstairs zone line of large amounts of air about once a month. It will bleed fine and I won't hear any gurgling in the pipes for a month or so, then all of sudden when the heat kicks on, it will sound like I'm in an aquarium. It also only does this in the one zone (upstairs). Would anyone happen to know where I could possibly be getting so much air into the line?? And if so, how to fix it.

  2. #2
    Join Date
    Nov 2004
    Posts
    240
    You have a leak somewhere. Find it and fix it.

  3. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,260
    Originally posted by djmodracek
    .. 3-zoned hot water baseboard heating system via a Burnham gas boiler.

    It also only does this in the one zone (upstairs).
    Add a few auto vent valves on this loop.
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,338
    find the leak.

  5. #5
    Join Date
    Sep 2004
    Posts
    654
    Originally posted by t527ed
    find the leak.
    Start at the boiler if you know what I mean.

  6. #6
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157
    Originally posted by dan sw fl
    Originally posted by djmodracek
    .. 3-zoned hot water baseboard heating system via a Burnham gas boiler.

    It also only does this in the one zone (upstairs).
    Add a few auto vent valves on this loop.
    yea & put the auto vents in at the highest point .. as air does rise u know..

  7. #7
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    672
    Call a pro and have them find and repair the leak. Could be a combination of failures. Maybe a leak and a bad auto bleeder or leaky coin vent.
    I am the "Wally". All others are meer imitations of the original.

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157
    i never did quite understand how a leak on a positve pressure line could introduce air .. can i be enlightened ...wouldnt the water just leak out ? i have worked on boilers many many times & have had systems with excess air problems .. even ones with major leaks .. but after repairing them leaks & pressure testing with all ok .. there was still an issure .. we added vents in all the right places & all is well .. also if the auto feed isnt working proper u will get air

  9. #9
    Join Date
    Jun 2000
    Location
    WYO
    Posts
    2,019
    water introduced to system contains absorbed air.When the water is heated,air is removed.
    never say never

  10. #10
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,491
    possible the pressure isnt high enough
    height and presure go together. you should be about 12 to 15 pounds pressure some times it can be nessasary to raise it to 20 it the loop is over 28 ft
    are there any vents on the system if not the the air will always be there. have some installed or replace if they are because they may be defective

  11. #11
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    672
    Originally posted by contactor
    water introduced to system contains absorbed air.When the water is heated,air is removed.
    Yep. Major leak, major air released when the water is heated. Get leak fixed and have a Spirovent installed to remove excess air. I never use auto bleeders over finished areas because I've seen too many leak causing damage.
    I am the "Wally". All others are meer imitations of the original.

  12. #12
    Join Date
    Jun 2003
    Location
    New Hampshire
    Posts
    2,663
    Make sure the pressure is about 15- 20 psi. And temp is not over 200 degrees f. on the gauge when boiler shuts off on high limit. Steaming when the temp gets 220 or more will cause air in the highest floors. Also make sure air elimination devices are working correctly.
    If the pressure is really low then the circulator will pull in air from hyvents etc.
    Have you ever noticed when purging (with the circulator running) and the pressure gets low and the hyvent starts sounding off. But it is pulling air in. Keep the pressure around 20 psi with a 3 story building. 15 - 20 psi with a 2 story building.

  13. #13
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,157

    Smile

    everyone here has great input ... i even learned something .. learning is awesome lol