    Heat pump indoor coil freezing up.

    I have a 3 ton Trane Weathertron 1200 XL that froze the indoor coil to where it completly blocked all airflow. When I discovered it I turned the system off but kept the blower running until it thawed out. I opened the air handler and removed the filters to make sure it was completely thawed then turned the system back on and the heating resumed as normal. I called my AC Tech and he said it sounds like a defrost control problem where the system would initiate a defrost cycle but not terminate it. He came out and tested the defrost control. It is a demand type system that uses a temperature differential between two sensors. The control board checked ok by doing the "Forced Defrost" and the blinking light on the board indicated normal. The sensors were removed and resistance checked ok at three different temps. The refrigerant pressures checked good and the filters are clean. He left saying everything is normal. That night it froze again! The next day he again checked the defrost control and cycled the reversing valve several times but could not duplicate the problem. Again it froze up.
    I live in the mountains in TN and we tested it during the day with 40-45 temps. It gets in the high 20's at night when the coil freezes.
    Primary heating is with wood using a fireplace insert. The heat pump is a backup but I leave the indoor blower running continuous to help circulate the heat. Thanks in advance for any help.

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,062
    What model Tstat do you have?

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,599
    The defrost system is to defrost the OUTDOOR coil, not the indoor coil. The indoor coil should be warm in the winter, not cold. If it is getting cold and freezing, you are in cooling mode which you shouldn't be in cold weather.

  4. #4
    Trane 3AAT8081A1

  5. #5
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,062
    That does not look to be a good #

  6. #6
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,841
    It's definitely sticking/hanging up in the defrost mode. Since it's so intermittent and nobody can duplicate the problem, it's time to R&R. I'd start with the defrost board and sensors. If that doesn't do it, you're like in for a reversing valve. Not a good project in cold weather. Electric heaters? You might want to use them if it's not the board or sensors.

  7. #7
    Join Date
    Jan 2010
    Location
    Central Texas
    Posts
    167
    Forgive my confusion, but how can the Indoor Coil freeze up with the Heat Pump in the Heat mode? The Indoor Coil is where the High Pressure/Temp Refrigerant Gas goes to be cooled down to become a High Pressure Liquid. Thus giving off its heat to warm the Indoor air.

    The only senerio I can see that the Indoor Coil Freezing up is during a Defrost Cycle that terminates, but the Reversing Valve does not cycle back into the Heat Mode. That would cause the system to be in the Cooling Mode. Where the Indoor Coil would be absorbing heat, but due to the low temp Inside/Outside. It would drop the coil below freezing and Freeze Up. So I would expect a sticking Reversing Valve to be the issue.

  8. #8
    That is the number on the t'stat however the second 8 may be a B... it is hard to tell. The other info on the label is as follows:

  9. #9
    Sorry...the message took of before I was finished. The other info on the label is:
    Cat # BAYSTST240
    30 VAC 1.5 A
    Tyler, Tx
    It has Trane Weathertron on the cover so I believe it to be the original.

  10. #10
    Join Date
    Mar 2010
    Location
    UT
    Posts
    126
    I don't deal with train so im not sure. Is that a Programable Stat. Maybe it is calling for cooling in the middle of the night for some reason?

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Next time it freezes up, turn your thermostat's system switch to off, and then go out and see if the outdoor unit really shut off.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,928
    DeltaT,

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.

  13. #13
    Join Date
    Dec 2007
    Posts
    4,767
    how about this scenario,

    main source of heat is wood and stat is auto, room gets too hot and the A/C comes on to cool to set temp.

    just a thought
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event