    issue with breaker trip

    I'm in a situation right now were the breaker will trip after about 15 min in heat mode I'm dealing with a aruf364216ca airhandler first i thought the breaker could be the problem cause it had a 50 amp double pole and the heat kit is 10kw so i changed it to a 60 amp worked fine before i left waited about 35 min a week later customer called same issue i directly went to change heat kit but the same issue scratching my head on this one one any suggestion?

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    508
    What is the actual operating amperage of the heating elements?
    What is the wire size from the breaker to heater?

  3. #3
    Join Date
    Dec 2009
    Posts
    53
    Is the air handler and heat strip the only thing on the breaker? I've come across some that had the outside unit connected to the same breaker as the airhandler.

  4. #4
    Join Date
    Jan 2011
    Location
    Washington, D.C.
    Posts
    55
    Is this new/old install???
    Rise And Rise Again Until Lambs Become Lions!!!

  5. #5
    Join Date
    Sep 2009
    Location
    Stumptown,USA
    Posts
    1,226
    If you have an amp clamp meter with min-max you can hook up your meter and see if the circuit is exceeding the rating of the breaker. Burned or corroded busbars can cause excessive heat at your circuit breaker. In my state this is a job for an electrician. Are you a service tech? your profile doesn't say.
    Challenge yourself, take the CM test --- Certificate Member since 2004 ---Join RSES ---the HVAC/R training authority ---www.rses.org

  6. #6
    Join Date
    Dec 2011
    Location
    Houston, TX
    Posts
    13
    when i go to do the amp draw it reads 47.5
    the wire used is an #8 and the unit is on its own breaker nothing else
    it looks like a fairly new install Yes I'm a service tech Should i be looking at the blower motor?

  7. #7
    Join Date
    Dec 2009
    Posts
    53
    60 AMP Breaker and 8/3 Copper is what I use for a a10K strip. Does the Breaker get warm or emit any sound when strip is entergized? Doubt if the blower motor is tripping the the 60 amp breaker.

  8. #8
    Join Date
    Dec 2011
    Location
    Houston, TX
    Posts
    13
    this why im scratching my head on this one cause it has the proper wiring 8/3 no it does not make any sound and as far as the breaker it might be a little warm really lite

  9. #9
    Join Date
    Oct 2011
    Location
    Arkansas
    Posts
    808
    Did you try another circuit breaker? Maybe it's me, but with a 60A. circuit I use #6 copper.

  10. #10
    Join Date
    Jan 2011
    Location
    Washington, D.C.
    Posts
    55
    What size breaker is in the electrical panel and what size breaker is at the air handler for the heater kit. Check the resistance at your heater kit, look for potential grounds.
    Rise And Rise Again Until Lambs Become Lions!!!

  11. #11
    Join Date
    Dec 2011
    Location
    Houston, TX
    Posts
    13
    when i first showed up for the call it had a 50amp breaker so knowing that the amp draw would be close to that i changed to a 60amp breaker and i would not go higher, normally what i would use for a 10-hkr heat kit is a 60amp the heat kit does not have a breaker on it, it has a block panel i have changed the heat kit once already same issue

  12. #12
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,454

    Angry

    Quote Originally Posted by e-z breez View Post
    when i go to do the amp draw it reads 47.5
    the wire used is an #8 and the unit is on its own breaker nothing else
    it looks like a fairly new install Yes I'm a service tech Should i be looking at the blower motor?

    Sounds like not enough wire for the install.

    Look at the equipment label. What is the minimum circuit ampacity?

    If your continuous draw is 47 amps, you must size the conductor for 125% of that draw. Then, you must use 75C wire and have 75C terminations (at the unit AND the breaker) to use #6 wire. If you have 60C terminations, you have to go to #4.

    I would keep the amp clamp there and look to see what is happening to draw enough current to trip the breaker. BTW, you don't just upsize a breaker unless it is according to the next size up rule when installing a branch circuit.

    My bet is that this install was not inspected, and is not up to code. Once you have touched it, you "either knew or should have known" that an electrician was needed. Call one in tomorrow.

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    14,454
    Quote Originally Posted by e-z breez View Post
    when i first showed up for the call it had a 50amp breaker so knowing that the amp draw would be close to that i changed to a 60amp breaker and i would not go higher, normally what i would use for a 10-hkr heat kit is a 60amp the heat kit does not have a breaker on it, it has a block panel i have changed the heat kit once already same issue
    NO. You don't size it to be "close." This is a continuous load, and you must size the conductor for 125%, with a suitable breaker for THAT ampacity.

    Get someone out there with an electrical license.