    Quote Originally Posted by Canadaq View Post
    Hi all,

    No, no more info. waiting to hear from management. Do you guys have any band aid recommendations? extra weatherstripping somewhat improved the situation, but I still get some smells coming from the fresh air vent (although it's hard to say, it is pretty close to the front door). Whoever thought of putting fresh and exhaust vents both in the balconies of tiny apartments was a real genius.

    btw, if the fans are off, does wind blow in air through the exhaust vents?
    Exhaust fans should have dampers to prevent intrusion of air when the fan is not running.

    Is it possible air being exhausted from a balcony near yours contains cooking odors that are being ingested by your ERV?
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  2. #28
    Join Date
    Dec 2011
    Posts
    17
    Post Likes
    Thread Starter
    also, approximately how long does it take for the air to completely exchange with all the ventilation off and the balcony door open, assuming no wind and just the stack related air exchange from the balcony door?

  3. #29
    Join Date
    Dec 2011
    Posts
    17
    Post Likes
    Thread Starter
    yes, that is also a problem, but not as bad as the corridor.

    do fresh air vents have dampers too? (I mean do you get fresh air blown in with the erv off if it's windy?)

  4. #30
    Join Date
    Dec 2011
    Posts
    17
    Post Likes
    Thread Starter
    How do I check if they do have dampers or not?

  5. #31
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    Dampers.... They work when they work. Most spring loaded butterfly dampers are great when they are new. Add real world stuff like several years of exhaust 'crud', and they stick open, or closed. My experience is that they should be inspected periodically to ensure they are indeed functioning as designed.

    Gravity operated 'flappers' have to be positioned properly, or they don't work at all. Again, house maintenance personnel usually don't really care or know - you have to be your own advocate, and informed when you are a tenant. I hope we're providing some direction here for you.

    Where are they? Anywhere in line with the exhaust duct. That needs to be established, and notated for future reference.

  6. #32
    Join Date
    Dec 2011
    Posts
    17
    Post Likes
    Thread Starter
    I don't know. I'm not really sure what a damper is to go look for them!

  7. #33
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    Here is a common butterfly damper showing how it works on a you tube video.

    Here is what one looks like before it is installed. When installed, they are almost hidden in-line, so you have to 'feel' for them if they are in flex duct.

  8. #34
    Join Date
    Dec 2011
    Posts
    17
    Post Likes
    Thread Starter
    oh, so they are right behind the fan, rather than near the exhaust vent outside. I see. Thank you.

Page 3 of 3 FirstFirst 123

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.