    Confused trane 4TWX4024A1000AA

    When I first came to the house the T-stat was blank went to the airhandler the breaker was triped ,so I reset the breaker. After that turned the system to heat but only the airhandler came on. Then switched system to cool and whole system came on. When the system was on in cool 168LP 200HP ODT60 IDT73. Im new at this, If anyone can help.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    are you sure the rev valve slid?

    did you take temps across rev valve?

    were ID & OD fans running?

    are you saying suction was 168 in cooling, with a 200 head?


    got to be clearer than mud for assistance
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    fix your control issue first

  4. #4
    no not sure rev valve slid

    & I didnt check the temp across rev valve

    only the ID fan would come on in heat

    yes the suction was 168 and head 200 on 60 ODT & 73 IDT in cool 410a

    tommorrow I will be back there to check what was mentioned

    thanks for the help dont know anywhere else to ask these questions

  5. #5
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    What Tstat does it have, and does it have an outdoor sensor with hp locked out?

  6. #6
    Join Date
    Oct 2011
    Location
    south al.
    Posts
    111
    ODT should not have it locked out, be sure settings on stat arent back to default due to power outage and pressure seems ok for lp but way to low on hp. Get system working right then recheck.

  7. #7
    Join Date
    Nov 2011
    Location
    USA
    Posts
    390
    The suction pressure is way high. The SST for 168 psi is around 60F. For that to be normal, the ID would have to be 100F .

    The head pressure is 25 or so, low for 60F OD.

    There are obviously some other things going on with the system, and with warrior00's deficiency in diagnostic skills, I'm half-way wondering if the compressor was even running when he read the pressures.

  8. #8
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,732
    that unit as a recip compressor so it could be bad valve

  9. #9
    Join Date
    Mar 2004
    Location
    Oklahoma City
    Posts
    108
    Did you solve your problem today?

  10. #10
    Join Date
    Aug 2011
    Posts
    1,245
    warrior,did u solve the problem,care for share?thanks