Results 1 to 12 of 12
Thread: What's wrong here?
12-19-2011, 10:55 PM #1
What's wrong here?
Went to do a pm on this system. Found the flue disconnected from the inducer (this picture is after I connected it) causing CO to spill in the attic, as well as H20 all over the electrical compenents. Does anyone else see what else the problem is?
12-19-2011, 10:58 PM #2
i know what it is! the picture is in the wrong position. its a vapor humidifier.....duh
12-19-2011, 10:58 PM #3
what did the combustion results show?
12-19-2011, 11:08 PM #4
12-19-2011, 11:16 PM #5
yea its a good thing to have. cant give you too much crap about it b/c myself didnt own one for 6 years while checking furnaces. been testing for 2 years now. it is a must have tool though. can your company buy you one?
12-19-2011, 11:20 PM #6
- Jun 2003
- 3,640
that pressure switch hose to the collector box should be attached to the lower fitting so that if the drain plugs the furnace will shut down.
12-19-2011, 11:22 PM #7
12-19-2011, 11:32 PM #8
So, Inducer condensate lines are plumbed wrong( path of least resistance), Flue pipe disconnected. I moved the flue pipe and water came pouring out and spilled into the gas valve. Ended up shorting gout the gas valve and the pressure switch all because the stupid flue pipe wasn't clamped to the inducer.
12-19-2011, 11:46 PM #9
Upper drain is done incorrectly.
Wheres the goodman 90 fitting?"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Just get it done son."
Dad adjusted
12-20-2011, 12:01 AM #10
12-20-2011, 08:35 AM #11
Pressure switch tubing should've moved to the bottom. The whole secondary would need to fill with water before the switch opens.
12-20-2011, 04:46 PM #12
usually, on a left side down, you leave the fitting in place and come out the top. You drain off the side of the 90, instead of the bottom. The side port has a curled lip, to catch condensate flowing down the flue, while the bottom port collects from your secondary.
Find that 90!
Agreed about the PS."Better tell the sandman to stay away, because we're gonna be workin on this one all night."
Dad adjusted