    Tecumseh comressor mn. caj4492y
    I need to select a txv for this cap tube system conversion. I was told by the manufacturer of the case (royal pd06lscb) that I need a 1/2 ton txv.My supplyhouse engineer says the same.Is there a rule of thumb to go down in size when its in between?

  2. #2
    Join Date
    Nov 2005
    Location
    Orange County Calif
    Posts
    128
    Most Txv's feed plus or minus 50% of rated tonnage

  3. #3
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,982
    TXv's should be sized to the evaporator coil, not the compressor. BUT,,,since you're replacing a cap tube you may not have any numbers to work with. Under the circumstances I would use a 1/2 ton valve and I think you'll be fine. Just check your superheat afterward and make any neccesary adjustments to get it within parameters.

  4. #4
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    so a 12,000 btuh coil used with a 24,000 Unit should
    have a 1 ton TXV. thaT JUST DOESN'T CUT IT

    this situation is that the 12,000 btuh coil will handle
    24,000 btuh of the unit at 20 deg TD, which would be
    normal for a meat prep room. so this coil, which has to
    handle 24,000 btuh at 20 deg TD needs a 2 ton TVX

    always rating coils a 1 deg TD will lead to better sizing
    of TXV and also the dismissal of the myth that coils produce btuh

    NOW, TO ANSWER YOUR QUESTION
    when in between sizes
    sporlan with tell you to go down
    alco will tell you to go down
    I will tell you to go down
    many on this board, like "size to coil" guy, will tell you
    to go up, the next bigger size. Just contact your local
    sporlan and/or alco rep and ask.

  5. #5
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,982
    many on this board, like "size to coil" guy, will tell you
    to go up, the next bigger size.

    Actually I advised him to go down. The compressor is a 3/4 ton and I advised a 1/2 ton valve.

    And I respectfully disagree with your comments regarding sizing.

  6. #6
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    depending on coil usage, the desired TD will vary
    shouldn't the TXV be sized to the load ?

    desired TD coil rated at 12,000 btuh coil is
    5 to 7 TD flowers @7 TD 8,400 btuh 3/4 ton TXV
    cooler 10 TD @10 TD 12,000 btuh 1 ton tvx
    wine 15 TD @15 TD 18,000 btuh 1-1/2 ton txv
    meat prep 20 TD @20 TD 24,000 btuh 2 ton tvx

    or do we size all TXV at 12,000 btuh 1 on
    (after all, it is a 12,000 btuh coil)

  7. #7
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,982
    Originally posted by rocket
    depending on coil usage, the desired TD will vary
    shouldn't the TXV be sized to the load ?

    desired TD coil rated at 12,000 btuh coil is
    5 to 7 TD flowers @7 TD 8,400 btuh 3/4 ton TXV
    cooler 10 TD @10 TD 12,000 btuh 1 ton tvx
    wine 15 TD @15 TD 18,000 btuh 1-1/2 ton txv
    meat prep 20 TD @20 TD 24,000 btuh 2 ton tvx

    or do we size all TXV at 12,000 btuh 1 on
    (after all, it is a 12,000 btuh coil)
    Maybe we're spliting hairs here, but you're still sizing by the evaprator size, not the compressor size. Sure you're factoring in the TD, but you're still sizing by the evap BTU at that TD. Also most TXV's have enough range to cover all but possibly the 20 degree TD.

    What if you get into a multiple evap set up or a mismatch and try to size by the compressor? Yeah, trouble!

  8. #8
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    nobody but you said "size by the compressor"
    size by the load is what was stated

    what load a given evaporater should handle
    is part of the sizing process

    Again you do not size by the evaporator, but you
    size TXV for the load the evaporator will handle

    that 24000 btuh evap at 10 TD may be sized for
    12000 btuh at 5 TD or 48000 btuh at 20 TD. its your
    job to know which.

    the compressor is an important part of that load
    in fact it is the only part that produces btuh.

    which portion of the compessor btuh will be handled
    by which of the multiple evaporators is your job to
    know and to size for.

    the relationship between the compressor and the
    evaporator is the TD

    Good idea to check out page 16 of HeatCraft Engr manual
    (actually good idea to check out complete manual)
    here's link to download
    http://www.heatcraftrpd.com/resource...ms/H-ENG-2.pdf





  9. #9
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,982
    Tke your arguement pills today Rocket??

    You kinda fired the first shot when you misquoted me about sizing up the valve and now you're taking the discussion way beyond where it needed to be for the OP who is not yet ready for that much info.

    So I'll let you finish without me.

    BTW, I occasionally do field consulting for the company whos link you posted.

  10. #10
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    wannafreeze
    my guess is that this appears to be a MT R12 system
    1/2 ton TXV probably OK, no problem there
    you should size and add a receiver as well

    but main point is why are you converting this
    to TXV, what problems are you having. If you
    are converting to solve a problem, chances
    are that conversion may be the wrong answer.

  11. #11
    Join Date
    Jul 2004
    Location
    NJ
    Posts
    1,781
    Originally posted by rocket
    wannafreeze
    my guess is that this appears to be a MT R12 system
    1/2 ton TXV probably OK, no problem there
    you should size and add a receiver as well

    but main point is why are you converting this
    to TXV, what problems are you having. If you
    are converting to solve a problem, chances
    are that conversion may be the wrong answer.
    Well this guy has 4 fridges he wants to put their condensors in the basement.They are all pretty new and he was told by the tech. support when he bought them that he could get them remoted easyly if he wanted.I talked to the same tech.sup.guy and was told I have to buy new condensors,txv,solenoid valve,LPC etc.On my previous post I talked about this job that I may do.I am gonna check that heatcraft manual.Sizing units, btu calculations in refrigeration,evap selections and details have been my weakest areas, I need to educate myself so badly on these issues.At shool they didn`t talk about them and no boss let me in on these issues now that I am on my own I am forced to learn all these.

  12. #12
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    good, the Heatcraft manual will be helpful

    be careful on remoting units to basement, make sure
    you have adequate makeup air or you will wind up
    recirculating air. if you don't have make up air,
    it will not work. Romting units is fine, remoting
    units to closde space as a basement is DISASTER.

    check around your area for someone that can help
    (sub-contract) you, as what your customer is asking
    may not be feasible. Don't get stuck !!!!!

  13. #13
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,753

    wannafreeze.......

    Rocket's advice about proper ventilation is correct. That heat that's generated has to have some place to go. If the basement area is underground, sizable and the amount of refrigeration is relatively small (like around 1000 sf/hp) and you're in the north with low ground temperatures you may need no additional ventilation at all. To be safe though, it's best to provide positive ventillation....exhaust and makeup.

    To figure how much air you need, you'll need to know how much heat will being generated by the condensing units. Start by gathering the performance data on your equipment from manufacturer's info. For the Tecumseh compressor you listed, the AJ4492Y, pick the Tecumseh unit with that compressor on it......AJA4492YXDXC using Tecumseh's site:
    http://www.tcc-nacg.com/

    Do a detailed search on that unit, pull up the performance data and go to the conditions you expect to run at.....say +20ºF evap and 90ºF ambient and you'll find that it'll do 5120 btu/hr and draws 940 watts at that condition. To calculate the total heat of rejection (THR) convert the power in watts to btu/hr by multiplying by 3.412 and add this to the cooling capacity:

    THR = 5120 + (3.412 x 940) = 8325 btu/hr

    The amount of air for ventilation is typically based on a 10ºF temperature rise so using the formula for sensible cooling:

    ( Q = 1.08 x CFM x TD), the CFM required would be:

    CFM = Q / (1.08 x TD) or 8325 btu/hr / ( 1.08 x 10ºF) = 770.8 CFM.

    There's an old-timer's rule-of-thumb of 1000 CFM per HP that is fairy common as well. This is where it came from.