03-04-2006, 06:06 PM #1
Tecumseh comressor mn. caj4492y
I need to select a txv for this cap tube system conversion. I was told by the manufacturer of the case (royal pd06lscb) that I need a 1/2 ton txv.My supplyhouse engineer says the same.Is there a rule of thumb to go down in size when its in between?
-
03-04-2006, 06:45 PM #2
Professional Member - bad email address
- Join Date
- Nov 2005
- Location
- Orange County Calif
- Posts
- 128
Most Txv's feed plus or minus 50% of rated tonnage
-
03-05-2006, 01:48 PM #3
TXv's should be sized to the evaporator coil, not the compressor. BUT,,,since you're replacing a cap tube you may not have any numbers to work with. Under the circumstances I would use a 1/2 ton valve and I think you'll be fine. Just check your superheat afterward and make any neccesary adjustments to get it within parameters.
-
03-05-2006, 02:13 PM #4
Regular Guest
- Join Date
- Feb 2004
- Location
- Medford Oregon
- Posts
- 807
so a 12,000 btuh coil used with a 24,000 Unit should
have a 1 ton TXV. thaT JUST DOESN'T CUT IT
this situation is that the 12,000 btuh coil will handle
24,000 btuh of the unit at 20 deg TD, which would be
normal for a meat prep room. so this coil, which has to
handle 24,000 btuh at 20 deg TD needs a 2 ton TVX
always rating coils a 1 deg TD will lead to better sizing
of TXV and also the dismissal of the myth that coils produce btuh
NOW, TO ANSWER YOUR QUESTION
when in between sizes
sporlan with tell you to go down
alco will tell you to go down
I will tell you to go down
many on this board, like "size to coil" guy, will tell you
to go up, the next bigger size. Just contact your local
sporlan and/or alco rep and ask.
-
03-05-2006, 02:22 PM #5
many on this board, like "size to coil" guy, will tell you
to go up, the next bigger size.
Actually I advised him to go down. The compressor is a 3/4 ton and I advised a 1/2 ton valve.
And I respectfully disagree with your comments regarding sizing.
-
03-05-2006, 03:13 PM #6
Regular Guest
- Join Date
- Feb 2004
- Location
- Medford Oregon
- Posts
- 807
depending on coil usage, the desired TD will vary
shouldn't the TXV be sized to the load ?
desired TD coil rated at 12,000 btuh coil is
5 to 7 TD flowers @7 TD 8,400 btuh 3/4 ton TXV
cooler 10 TD @10 TD 12,000 btuh 1 ton tvx
wine 15 TD @15 TD 18,000 btuh 1-1/2 ton txv
meat prep 20 TD @20 TD 24,000 btuh 2 ton tvx
or do we size all TXV at 12,000 btuh 1 on
(after all, it is a 12,000 btuh coil)
-
03-05-2006, 05:04 PM #7Maybe we're spliting hairs here, but you're still sizing by the evaprator size, not the compressor size. Sure you're factoring in the TD, but you're still sizing by the evap BTU at that TD. Also most TXV's have enough range to cover all but possibly the 20 degree TD.Originally posted by rocket
depending on coil usage, the desired TD will vary
shouldn't the TXV be sized to the load ?
desired TD coil rated at 12,000 btuh coil is
5 to 7 TD flowers @7 TD 8,400 btuh 3/4 ton TXV
cooler 10 TD @10 TD 12,000 btuh 1 ton tvx
wine 15 TD @15 TD 18,000 btuh 1-1/2 ton txv
meat prep 20 TD @20 TD 24,000 btuh 2 ton tvx
or do we size all TXV at 12,000 btuh 1 on
(after all, it is a 12,000 btuh coil)
What if you get into a multiple evap set up or a mismatch and try to size by the compressor? Yeah, trouble!
-
03-05-2006, 05:25 PM #8
Regular Guest
- Join Date
- Feb 2004
- Location
- Medford Oregon
- Posts
- 807
nobody but you said "size by the compressor"
size by the load is what was stated
what load a given evaporater should handle
is part of the sizing process
Again you do not size by the evaporator, but you
size TXV for the load the evaporator will handle
that 24000 btuh evap at 10 TD may be sized for
12000 btuh at 5 TD or 48000 btuh at 20 TD. its your
job to know which.
the compressor is an important part of that load
in fact it is the only part that produces btuh.
which portion of the compessor btuh will be handled
by which of the multiple evaporators is your job to
know and to size for.
the relationship between the compressor and the
evaporator is the TD
Good idea to check out page 16 of HeatCraft Engr manual
(actually good idea to check out complete manual)
here's link to download
http://www.heatcraftrpd.com/resource...ms/H-ENG-2.pdf
-
03-05-2006, 05:42 PM #9
Tke your arguement pills today Rocket??

You kinda fired the first shot when you misquoted me about sizing up the valve and now you're taking the discussion way beyond where it needed to be for the OP who is not yet ready for that much info.
So I'll let you finish without me.
BTW, I occasionally do field consulting for the company whos link you posted.
-
03-05-2006, 07:54 PM #10
Regular Guest
- Join Date
- Feb 2004
- Location
- Medford Oregon
- Posts
- 807
wannafreeze
my guess is that this appears to be a MT R12 system
1/2 ton TXV probably OK, no problem there
you should size and add a receiver as well
but main point is why are you converting this
to TXV, what problems are you having. If you
are converting to solve a problem, chances
are that conversion may be the wrong answer.
-
03-05-2006, 09:59 PM #11Well this guy has 4 fridges he wants to put their condensors in the basement.They are all pretty new and he was told by the tech. support when he bought them that he could get them remoted easyly if he wanted.I talked to the same tech.sup.guy and was told I have to buy new condensors,txv,solenoid valve,LPC etc.On my previous post I talked about this job that I may do.I am gonna check that heatcraft manual.Sizing units, btu calculations in refrigeration,evap selections and details have been my weakest areas, I need to educate myself so badly on these issues.At shool they didn`t talk about them and no boss let me in on these issues now that I am on my own I am forced to learn all these.Originally posted by rocket
wannafreeze
my guess is that this appears to be a MT R12 system
1/2 ton TXV probably OK, no problem there
you should size and add a receiver as well
but main point is why are you converting this
to TXV, what problems are you having. If you
are converting to solve a problem, chances
are that conversion may be the wrong answer.
-
03-05-2006, 10:33 PM #12
Regular Guest
- Join Date
- Feb 2004
- Location
- Medford Oregon
- Posts
- 807
good, the Heatcraft manual will be helpful
be careful on remoting units to basement, make sure
you have adequate makeup air or you will wind up
recirculating air. if you don't have make up air,
it will not work. Romting units is fine, remoting
units to closde space as a basement is DISASTER.
check around your area for someone that can help
(sub-contract) you, as what your customer is asking
may not be feasible. Don't get stuck !!!!!
-
03-06-2006, 11:10 AM #13
wannafreeze.......
Rocket's advice about proper ventilation is correct. That heat that's generated has to have some place to go. If the basement area is underground, sizable and the amount of refrigeration is relatively small (like around 1000 sf/hp) and you're in the north with low ground temperatures you may need no additional ventilation at all. To be safe though, it's best to provide positive ventillation....exhaust and makeup.
To figure how much air you need, you'll need to know how much heat will being generated by the condensing units. Start by gathering the performance data on your equipment from manufacturer's info. For the Tecumseh compressor you listed, the AJ4492Y, pick the Tecumseh unit with that compressor on it......AJA4492YXDXC using Tecumseh's site:
http://www.tcc-nacg.com/
Do a detailed search on that unit, pull up the performance data and go to the conditions you expect to run at.....say +20ºF evap and 90ºF ambient and you'll find that it'll do 5120 btu/hr and draws 940 watts at that condition. To calculate the total heat of rejection (THR) convert the power in watts to btu/hr by multiplying by 3.412 and add this to the cooling capacity:
THR = 5120 + (3.412 x 940) = 8325 btu/hr
The amount of air for ventilation is typically based on a 10ºF temperature rise so using the formula for sensible cooling:
( Q = 1.08 x CFM x TD), the CFM required would be:
CFM = Q / (1.08 x TD) or 8325 btu/hr / ( 1.08 x 10ºF) = 770.8 CFM.
There's an old-timer's rule-of-thumb of 1000 CFM per HP that is fairy common as well. This is where it came from.