Automated Logic Bacnet MS/TP vs Arcnet
I need to tie in a JACE to existing ALC "SE" and "ZN" controllers via BACnet MS/TP but it appears the field bus is Arcnet. The literature for the controllers read Arcnet or BACnet MS/TP compatibility. Is there something that needs to be done to configure the ALC controllers for BACnet MS/TP?
Any help would be appreciated!!!
Thanks.
-
12-19-2011, 09:42 AM #2
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
According to page 6 of this manual, the ZN controllers have a jumper that you move between ARCnet or MS/TP positions.
Once you have it set up as MS/TP, you then have to set dip switches 1 & 2 to specify the baud rate.
I assume you'll want to cycle power after changing either the jumper or the dip switches.
-
12-19-2011, 10:04 AM #3
Why go to the trouble of having to go to every controller, why not integrate to the LGR via IP or Ethernet?
kontrol out"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
-
12-19-2011, 02:42 PM #4
If you change the jumpers on all the modules you will then have to move communication wires from the arcnet port to the MS/TP Port (S1). Also you will have to set jumper on LGR to turn on MS/TP on port S1 and change Arcnet network to MS/TP in sitebuilder.
-
12-19-2011, 09:45 PM #5
Regular Guest
- Join Date
- Nov 2007
- Location
- Phoenix, AZ
- Posts
- 256
Arcnet
Every time I have seen a ALC Arcnet it was 2 wire, I don't know how much of a problem this would be in ALC but it would be a big problem with any other MSTP installation.
I agree with the LGR integration.
Greg
-
12-19-2011, 09:49 PM #6"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue

BIG Government = More Dependents
http://threedevilskennel.com/ - not my website.
Versatile Hunting Dog Federation - www.vhdf.org/
-
12-19-2011, 10:20 PM #7
Regular Guest
- Join Date
- Nov 2007
- Location
- Phoenix, AZ
- Posts
- 256
-
12-19-2011, 10:36 PM #8
-
12-20-2011, 01:58 AM #9
My vote is integrate with the LGR unless you or you have someone else at the ready to adjust settings on the configuration of the LGR as The_USC mentioned.
Be careful not to make changes you are not knowledgeable enough or prepared to do on the fly. I don't have the exact specifics to tell you verbatim what to do even though I have worked with ALC for about a year, but I know it's a little more involved than just changing the jumpers and moving the wires.