Heat exchanger
Results 1 to 13 of 13

Thread: Heat exchanger

  1. #1
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40

    Heat exchanger

    I have a 30 ra030 with a scaled heat exchanger planning on cleaning it Saturday. Carrier says use 5% hydrocloric acid. Has any one had any luck cleaning one. Chiller is about 7 years old with no water treatment.

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,699
    Did you check the strainer?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40
    Yes check pump curve also. Pump is doing more than it needs The approach was over 15 degrees if I remember correctly. Have a 10 psi psi drop across heat exchanger

  4. #4
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    If your pumping more than it needs, then your approach and pressure drop across heat exchanger is going to be high. Also, you can have an oil logged heat exchanger. Is this a shell and tube heat exchanger, or a plate frame heat exchanger?

  5. #5
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40
    This is a plate heat exchanger.

  6. #6
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,699
    Quote Originally Posted by Jeremy325 View Post
    This is a plate heat exchanger.
    Ou should be able to pop the Vic's off and take a peek in there and see if anything looks bad.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  7. #7
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40
    Quote Originally Posted by thegoodlistener View Post
    Ou should be able to pop the Vic's off and take a peek in there and see if anything looks bad.
    U can take it apart?

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    Quote Originally Posted by Jeremy325 View Post
    U can take it apart?
    No, you can pull the Victolic fittings off (chilled water connections), and look inside.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    What is the design pressure drop across the heat exchanger? What is the design delta T?

  10. #10
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40
    The design pressure drop is 5-1/2 to 6 psi The design delta is 10 degrees

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    Try slowing your flow down to achieve design pressure drop, load chiller to 100%, and see if you achieve design delta T and check for an improvement in your approach.

  12. #12
    Join Date
    Dec 2011
    Location
    TN
    Posts
    40
    Will do thank you. I spent all day up there to day running a hydrocloric solution Did not get a lot out of it. I don't have balancing valves I have full port valves on both in and out. Which one do suggest throttling down?

  13. #13
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,288
    Quote Originally Posted by Jeremy325 View Post
    Will do thank you. I spent all day up there to day running a hydrocloric solution Did not get a lot out of it. I don't have balancing valves I have full port valves on both in and out. Which one do suggest throttling down?
    Outlet of chiller.