    Training

    hvaceric doing training on combustion analysis. We took a Heil 80 that we removed from a home. The competition said it had cracks but the HX was sound as can be. We hooked it up to our gas line and vented in 5" single wall to the 4" b-vent for our tube heater.

    Picture 2 shows the 5" flue about 80% blocked. Did it bother the pressure switch?

    Picture 3 says no. Pressure switch opens at .65" WC while the manometer says .81 so despite the horribly blocked flue, furnace kept purring along.

    Picture 4 shows the draft gauge after the block. Very strong draft. Between the inducer and the block, the flue went positive meaning exhaust could come out any joints in the pipe. CO production went up with this blockage too.

    Picture 5 shows a hole Eric drilled in the HX. It affected nothing. CA readings stayed the same as did draft. We had the burner door on top of the outlet providing some static pressure.

  2. #2
    Join Date
    Apr 2001
    Location
    Over Here
    Posts
    1,105
    Post Likes
    That is education at its funnest. I would have liked to been there. I wonder what the tolerance of those switches is new? We also see many of these pressure switches that are out of spec in the field. Is it cheap manufacturing, or self-limiting caused by the application?

    Thank you for sharing.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Thread Starter
    The PS in the furnace tended to drop out at .7" so slightly quicker than the .65 rating.

  4. #4
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    very good info! hopefully the vent switch works.just goes to show why CA is so important

  5. #5
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    i used to breeze thru gas furnace PM's. Now that i am more educated and have more tools to do the job correctly it takes me about 45-60 mins on a PM

  6. #6
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Great hands on training!

  7. #7
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,434
    Post Likes

    Talking easy fix

    Just common vent this 80%'er to a natural draft water heater with a draft hood. That way, when the flue is blocked it can vent out of the draft hood and not shutdown the furnace.

    I hope ya'll realize I'm being facetious here but it makes a point:
    when you common vent an 80% furnace with a water heater, you bypass three primary safety controls on the furnace to a water heater that has NONE-pressure switch, flame rollout and high limit.

    Great training by The Bald One! I hope ya'll see the value of in-house training in addition to formal outside training by agencies. Now, keeping Loonie's point in mind, do YOU test safety controls and compare to spec?

    Now, if you have a WH common vented, how do you propose to protect the occupants?

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Thread Starter
    Gotta give this credit to hvaceric. He's got all the tools and taken lots of training.

  9. #9
    Join Date
    Oct 2007
    Posts
    239
    Post Likes
    What was the rating printed on the pressure switch? Sounds to me the pressure switch was bad.

    The rating on the pressure switch is the pressure at which the switch makes. It should break .15 above that rating. So if the rating was .65 than .8 is where it should have opened.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Lot of guys will condemn a HX after they put on a new PS and or inducer and it still doesn't work.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •