    Carrier System vs. Luxaire System

    Hello, we live in a 1500 sq. ft. house in New Jersey. My HVAC system is about 25 years old, so I am looking to replace it and take advantage of some of the state rebates. I received a few quotes, and narrowed it down to these two:

    Quote 1 - Luxaire System:
    Furnace: TG9S080B12MP11, 95.5%, 80,000BTU
    A/C: TCJD36S41S1 3 Ton, 13 SEER
    Coil: ???

    Quote 2 - Carrier System:
    Furnace: 59SP5A080E17-16 96.5% 80,000 BTU
    A/C:59SP5A080E17-16 3 Ton, 16 SEER
    Coil: CNPVP4821

    How do these two systems compare? I'm leaning towards the Carrier system due to the price, but can't find much information on the A/C unit they are quoting. Any feedback would be appreciated.

  2. #2
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    First thing that jumps out at me is over sized for both heating and cooling.
    Did anyone do a manual J?
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  3. #3
    Join Date
    Dec 2011
    Posts
    7
    Post Likes
    Thread Starter
    One company did a manual J. The numbers came out to 32379 Btuh for heating and 22921 Btuh for cooling.

    Also, I just realized that I put the wrong part # for the A/C. The correct number is CA16NA036.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Sounds like you need 1/2 the furnace and a 2 ton A/C.

  5. #5
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,890
    Post Likes
    I would agree on the sizing. As far as the equipment, I handle Luxaire and Tempstar (ICP part of Carrier Corp) the Carrier is a little higher grade than the Luxaire, both decent equipment. It's more about proper installation than brand, all manufacturer's offer different levels of equipment.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  6. #6
    Join Date
    Dec 2011
    Posts
    7
    Post Likes
    Thread Starter
    Thanks for the advice. The only issue that was brought up by the contractor doing the manual J was that my unit is a downflow and all my ducts run in an ventilated crawlspace. I was advised not to insulate the ducts due to the amount of cold water pipes runing in the space. It doesn't look like these losses were taken into account in the J calculation, but would this have an impact on the proper equipment sizing?

  7. #7
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,626
    Post Likes
    Engine

    Ductwork in attic is not insulated?

    And dealer will stand behind installing a 95%+ condensing furnace in attic for a NJ location?

    IMO

  8. #8
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by engine15 View Post
    Thanks for the advice. The only issue that was brought up by the contractor doing the manual J was that my unit is a downflow and all my ducts run in an ventilated crawlspace. I was advised not to insulate the ducts due to the amount of cold water pipes runing in the space. It doesn't look like these losses were taken into account in the J calculation, but would this have an impact on the proper equipment sizing?
    Change the condition of the crawl space, seal and insulate the duct work.

  9. #9
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,890
    Post Likes
    In your climate, I would want the crawl space to be conditioned, what with water lines and such.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  10. #10
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    Sounds like you need 1/2 the furnace and a 2 ton A/C.

    I agree, I'm not understanding why the furnace was oversized by 2X.... unless for tax credits the needed th 4 ton fan. But you cna get a 4 ton blower on a 60k BTU unit.


    Actually, I'm also having trouble understangin how a home in Jersey that needs 2 tosn fo cooling, only needs 32k BTU of heating? that balance doesn't sound right. In that climate, the heating load should be close to 2X the cooling load.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •