Thread: Heat exchanger

  1. #1
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes

    Heat exchanger

    I have a 30 ra030 with a scaled heat exchanger planning on cleaning it Saturday. Carrier says use 5% hydrocloric acid. Has any one had any luck cleaning one. Chiller is about 7 years old with no water treatment.

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Did you check the strainer?

  3. #3
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    Yes check pump curve also. Pump is doing more than it needs The approach was over 15 degrees if I remember correctly. Have a 10 psi psi drop across heat exchanger

  4. #4
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    If your pumping more than it needs, then your approach and pressure drop across heat exchanger is going to be high. Also, you can have an oil logged heat exchanger. Is this a shell and tube heat exchanger, or a plate frame heat exchanger?

  5. #5
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    This is a plate heat exchanger.

  6. #6
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    This is a plate heat exchanger.
    Ou should be able to pop the Vic's off and take a peek in there and see if anything looks bad.

  7. #7
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by thegoodlistener View Post
    Ou should be able to pop the Vic's off and take a peek in there and see if anything looks bad.
    U can take it apart?

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    U can take it apart?
    No, you can pull the Victolic fittings off (chilled water connections), and look inside.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    What is the design pressure drop across the heat exchanger? What is the design delta T?

  10. #10
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    The design pressure drop is 5-1/2 to 6 psi The design delta is 10 degrees

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Try slowing your flow down to achieve design pressure drop, load chiller to 100%, and see if you achieve design delta T and check for an improvement in your approach.

  12. #12
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    Will do thank you. I spent all day up there to day running a hydrocloric solution Did not get a lot out of it. I don't have balancing valves I have full port valves on both in and out. Which one do suggest throttling down?

  13. #13
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    Will do thank you. I spent all day up there to day running a hydrocloric solution Did not get a lot out of it. I don't have balancing valves I have full port valves on both in and out. Which one do suggest throttling down?
    Outlet of chiller.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •