  1. #1

    Hmm

    Gentlemen!
    I posted over here, because I thought some other HO's might benefit from your answers as well.
    I'm writing this as a HO and not a Contractor. I don't do any residential work, except for my own residence.

    I recently had to replace my HP. What a chore that was with me, myself and I! The dang things are huge compared to what I had! And, the line set was the hardest part to install! Any way I digress...

    The unit I installed (Gibson 12 SEER w/ scroll comp.) does not have a CC heater (visible). It doesn't have an OD air 'stat. It doesn't have LP or HP sw's.

    I'm thinking about adding some or all to my unit. Would you do it if this was your unit? Am I over controlling?

    You know, that sucker was cycling on/off with the OD temp in the high teens/low twenties!
    I was impressed. It seemed the old unit (Janitrol) would just keep running at those temps.

    Anyway, sorry for the long post!
    What would/does your unit have on it?

    Thanks, Bob




  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    Personally....I'd put a belly-band on it and Hi/Lo pressure switches on the ports. Cheap insurance.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Mar 2001
    Posts
    276

    My unit, now 5 years old, is a Bryant 2.5 ton 650 model heat pump with FV4 variable speed air handler and Thermidistat control. I have the heat strips locked out above 15*F. DEhumidify setpoint is 50%...usually heat to 68-70 and cool 68-70...balance point WAS 17*, but has inched up to about 22* because my lazy butt has not re-weatherstripped the doors and resealed the caulking on the windows...I really should do it...I think my total cost would be about $12.

  4. #4

    Thumbs up

    Hey guy's thanks for your inputs.
    I'll be installing the controls and CC heater.
    Thanks again,
    Bob

  5. #5
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,977
    The unit probably has off cycle crancase heat by bleeding through the windings and keeping them warm. No need to add a belly band that will just use energy.

    I do not think outdoor thremostats are needed except in special conditions. Modern pumps usually do better without them.

    Being a refrigeration guy I wish all units had HP and LP controls for protection, unfortunatly the market is so down and dirty on pricing these get left out to keep the costs down.

    Gibson, for the price, is a very impressive line of equipment. Solidly built, very quiet, and reliable. One of the better budget priced lines on the market IMO.

  6. #6
    Join Date
    Jan 2006
    Location
    Dayton, Ohio [USA]
    Posts
    752
    i do like the gibson line. its simple, looks good, and it has a copeland

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    You dont need a CCH unless you have noisy compressor at start up. It wont hurt though.

    No need for an outdoor stat.

    The LPS would have to be bypassed more than likely in the heating mode unless you had the right one. If nothing else a bypass timer would need to be installed.

    Unless you are cool with the idea of replacing the compressor if the fan fails on the outdoor unit in summer, or indoor fan in winter, a HP switch would be, as someone mentioned, cheap insurance.

  8. #8
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,601
    All I do is Heat Pumps down here... and I'll bet ya a coke that the C.U. has a single pole contactor. This means you have the winding(s) on and no need for a C.H.

    Also as said before press. switch = cheap insurance. Plus I do like the outside stat to compensate for the thermostart fiddle fart syndrom!

  9. #9
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,179
    A single pole contactor does not provide crankcase heat, where is the circuit? to ground? the old GE and Trane units had a trickle circuit on the start winding, using a bleed resistor on the run cap

    Instead of a LP switch put a loss of charge switch on the liquid line

  10. #10
    Join Date
    Jun 2004
    Posts
    459

    crankcase heating

    Originally posted by swampfox
    A single pole contactor does not provide crankcase heat, where is the circuit? to ground? the old GE and Trane units had a trickle circuit on the start winding, using a bleed resistor on the run cap

    Instead of a LP switch put a loss of charge switch on the liquid line
    this issue use to baffle me also, "where is the circuit?" It's not the typical circuit arrangement we are so familiar with.......it works by applying a potential difference at the run capacitor which in itself provides the missing link. The capacitor does this by its' ability to charge and discharge every cycle of the line feeding it. This constant charging and discharging will produce, in effect, a very small current in the run winding, sufficient enough to produce just enough heat to prevent refrigerant migration to the compressor. Yes, a single pole contactor is a sure sign that the compressor run winding is the crankcase heater. To check for operation, clamp on your ammeter aroung the leg that is not disconneted at the contactor during shutdown, you will get a reading.

  11. #11
    Join Date
    Apr 2004
    Posts
    7,680
    Potential is worthless without a return path. If you read L1-T1 (assuming that is the open leg). You will read 220v. unless there is something coming from both L1 and anywhere between T1 and T3 you do not automaticly get CCH. In the case of using the bleed resister, the cpacitor would need to be fed from the L1. To verify it, as you mentioned you would need to read current on the start or common wire to the compressor. (will be very low). You also probably do not have a start cap on that gibson unit unless it had a recip.

    Since SEER has become more difficult to attain, usage of power for things like CCH are generally removed unless an absolute necessity. They are added as accessories but again, a Copeland Scroll doesnt need one unless you are trying to reduce the noise at start-up.

  12. #12
    Join Date
    Dec 2005
    Location
    Spokane Wa
    Posts
    169
    BOLOGNA ON NOT NEEDING CCH. ABSOLUTLEY CHEEP INSURANCE. YOU ARE NOT ALWAYS THERE TO LISTEN TO THE PUMP ON COLD STARTUPS. BEST $30 SPENT

  13. #13
    Join Date
    Feb 2006
    Posts
    168
    Thanks to btexpress for posting this kind of question in the residential section, but your talking your language with abbreviations. Can you explain the meaning of the shorthand? For instance, what do you mean by CC heater, OD air stat, HP and LP sw's and what is the value of installing each on this heat pump? I think I know some of the answers but wouldn't presume anything. Would rather hear from the pros.

    thanks
    jdb