Gas fireplace fire goes out after @20 minutes but pilot stays on
Heat-n-glo fireplace, fire goes out after a while (after 20 min or sometimes up to 1 hour) but pilot stays on. Problem started after Gas to the house had been turned OFF for the day. That was a month ago. Often it's not even fully warmed up (eg. 15-20 minutes) and other times an hour or two. So guessing it's not a heat sensor. Any air in the line should be looooong gone. Replaced thermopile 13 months ago. How can I eliminate the most likely possibilities?
-
12-13-2011, 09:43 PM #2
A few more details would help. Model # ? is it an insert or direct vent. ? Thermostat or switch ? Main valve is dropping out and pilot remains lit than I would lean towars wiring or gas valve. How old is the unit and when was it last serviced by a pro. ??
There is no bad beer, some just taste better than others.
-
02-19-2012, 09:44 PM #3
Regular Guest
- Join Date
- Jun 2010
- Posts
- 16
-
02-22-2012, 06:39 PM #4
Professional Member
- Join Date
- Dec 2011
- Location
- PA
- Posts
- 158
check all wire connections, reconnect all spade connectors, if you have a "light switch" on the wall for turning the unit on and off. you may wanna replace that as well
-
02-23-2012, 12:26 PM #5
Regular Guest
- Join Date
- Mar 2007
- Location
- north carolina
- Posts
- 31
it may have a O2 sensor cutting it off. check to make sure it is getting enough air for combustion
-
02-23-2012, 12:56 PM #6
Deon, O2 sensors are "oxygen depletion sensors" which are special safety pilots used on ventfree gas appliances. The only ventfree appliances Heat&Glo makes are electric.
Keep the fire inside the fireplace.
-
03-15-2012, 01:04 AM #7
Professional Member
- Join Date
- Mar 2012
- Location
- Pacific NW
- Posts
- 16
Have you checked for a vent safety switch?
-
03-31-2012, 01:31 PM #8
Professional Member
- Join Date
- Oct 2008
- Location
- Brewster, MA
- Posts
- 121
Gas Pressure:
Have you checked the gas line pressure to the gas valve? If it started after the gas meter was turned off, it could be a bad gas regulator in the gas meter.
It could ne any of the things mentioned but you should make sure that you have adequate gas pressure. Is it Nat. Gas or LP?
Its unusual that the burner stops but the pilot stays lit. If the thermocouple senses no flame, it shuts down everything. Its not supposed to leave itself burning.