Results 1 to 4 of 4
Thread: Goodman Gas Pack
-
02-26-2006, 07:18 PM #1
Just wondering if anyone else is having a problem with this. You get the no heat call and board tells you a bad pressure switch. You check it and it works every time.
If you take a drill bit or paper clip and go into the connector on the comb.blower housing you will feel it stop like there is a metal bur or something and then it goes on and falls out......anyone else having this problem?????
I prefer Trane but they are pricing theirselves for the rich only.What we have here, is a failure to communicate........
-
02-26-2006, 07:44 PM #2
Have not seen this on that particular unit but that is an issue that has come up with IDB before. Hopefully you just lucked out and got the ones with the debris
Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
03-07-2006, 12:20 PM #3
I think the fact that it is a Goodman explains a lot of it.
What we have here, is a failure to communicate........
-
03-07-2006, 01:03 PM #4
This is a problem with all brands, not something Goodman bashers can have fun with. There was a post recently about a dealer finding this with Lennox. Years ago Fasco caused us problems with the paint flaking off their inducers clogging pressure switch ports. TRANE used only Fasco inducers back then.


Reply With Quote