Thread: coffin slugging??

  1. #1
    Join Date
    Dec 2005
    Posts
    32
    Post Likes
    i have been working in this supermarket for a yr now,rack is r-22,5 compressors with sattelite on left which is just part of rack. been there numorous times for oil fail,line from coffin fosted so bad makes end bells to comp frosted which then covers entires comp including oil pump to make comp fail thus making sattelite to then ice over. i have been saying we need to address this and find which case or cases are doing this, well i was told to put in epr valve which i did, and still having trouble, was there recently and found oil washed out of usual comp,am i wrong to say problem is in 1 or more coffins or am i missing something. thers 20% in receiver, head pressure good and back pressure good. it seems they dont want to put time into cases to find problem, not sure if its my boss or company i work for.
    any thoughts anyone would be appriciated

  2. #2
    Join Date
    Dec 2005
    Location
    Rockhill South Carolina
    Posts
    370
    Post Likes
    Check your superheat on case in question also look around the area of that case and make sure there are no supply ducts from store A/C blowing in and disturbing air curtain on coffin case.you may want to go through and tune up all the cases that rack serves.It is probably something very simple being overlooked.

  3. #3
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes

    Let me guess......

    Your company has a PM contract with this store that doesn't include replacement compressors.

  4. #4
    Join Date
    Feb 2006
    Posts
    63
    Post Likes
    when you force coffins into defrost does the frost on the end bell go away? if so than open those coffins up and have a look. could be something very simple. what did you set your epr for? whats the t-stat set for? hows defrost operation? Im not sure if you should bother with looking for A/C killing air cutain if these cases have been working fine for the year that you have been in the store.but I would at least have them stip the case so you can rule out the easy stuff.this would also be a great time to start checkin superheat as the captain said.

    let us know what you find. its always a pain in the arse to chase floodback

  5. #5
    Join Date
    Feb 2006
    Posts
    63
    Post Likes
    hey mr. meister ya said that you ran the ref. dept. for edwards. what are you up to now?

  6. #6
    Join Date
    Nov 2005
    Location
    Orange County Calif
    Posts
    128
    Post Likes
    They will want to put the time and $$$$ into it once the compressor take a crap...be sure to let them know it will void warranty of the problem isnt resolved if the compressor does go bad...

    But on a serious note i would go throught superheats on the cases in question. also may want to make sure epr's arent set to low or ensure that they due shut down when they are suppose to....

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Originally posted by guy in blue van
    hey mr. meister ya said that you ran the ref. dept. for edwards. what are you up to now?
    I've been doing a one-man wrench-turnin' refer gig in Florida for 15 years now. It's almost like being semi-retired compared to the old rat race.

  8. #8
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    Clean the strainer and put on a vzp pressure limiting powerhead.
    A Diamond is just a piece of coal, that made good under pressure!

  9. #9
    Join Date
    Feb 2006
    Location
    lansing mich.
    Posts
    4
    Post Likes
    is there anyway you can monitor loads on the cases. it sounds like a air flow and load demand issue. ie they fill the cases making a hot type pulldown, vapor density increases. customers empty cases unusally fast during latent heat transfers . Then the load demands change to fast causing vapor density to react almost as a restriction. End result is major frosting.,

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Originally posted by iceman373
    is there anyway you can monitor loads on the cases?
    Yes. It's called a properly sized, adjusted and maintained thermostatic expansion valve......like the one that should be in that case that's causing all the trouble.

  11. #11
    Join Date
    Nov 2005
    Location
    Orange County Calif
    Posts
    128
    Post Likes

    Lightbulb

    Well said..........

  12. #12
    Join Date
    Feb 2006
    Location
    lansing mich.
    Posts
    4
    Post Likes
    usally, there is a instore utilty mechanic that can help, or talk with the produce/frozen meats supervisior. they know whats coming in and whats on sale and where its going days in advance., If its a large chain, they even know where and how they are going to display it weeks in advance.

  13. #13
    Join Date
    Feb 2006
    Location
    lansing mich.
    Posts
    4
    Post Likes
    assuming that proper superheat and subcooling is not in disaray.

  14. #14
    Join Date
    Dec 2004
    Location
    Sunny So Cal!
    Posts
    649
    Post Likes
    I wouold add its worth noting that if the liquid line runs inside the cases you will be receiving some killer subcooling on liquid to case txvs at furthest end and those valves should be pinched down moreso than the others for this reason. Either way you slice it, you need to spend some serious time on superheats.
    theres also possibility that an internally cracked heat exchanger in case present.

    Nothing worse than changing a compressor where you knew that it was coming but you didnt prevent it. If you are drawing a blank then do your company favor by advising that theres obviously a problem and send out someone else.

    If the customer doesnt want to pay the labor - hey its on him and you can snigger when the dread reaper comes to collect that anchor....

    [Edited by thegoodhumorman on 02-26-2006 at 05:17 PM]
    Look, just do your job, stay outta my way and we'll get along fine.

    Teach your kids to respect themselves and others with your actions- these little baboons will imitate you like it or not.

  15. #15
    Join Date
    Dec 2004
    Location
    Sunny So Cal!
    Posts
    649
    Post Likes

    forgot to add...

    It only takes one TXV flooding to do this- could be more
    but-
    somebody is paying a lot for your company to drive there to reset compressor. Sounds like a Safeway contract....
    Look, just do your job, stay outta my way and we'll get along fine.

    Teach your kids to respect themselves and others with your actions- these little baboons will imitate you like it or not.

  16. #16
    Join Date
    Jan 2006
    Location
    Indiana
    Posts
    525
    Post Likes
    [QUOTE]theres also possibility that an internally cracked heat exchanger in case present.[QUOTE]

    Flooding that bad on a rack this is where I would start. But if nobody cares( until it breaks ), changing compressors is good experience- especially on nights and weekends.

  17. #17
    Join Date
    Dec 2002
    Location
    Tampa, Florida
    Posts
    706
    Post Likes

    Hmm not good . . .

    if the end bells are frosting over, you WILL be replacing or re-building a compressor in the near future. been to a couple of carrier's semi-hermetic classes. the one thing they constantly keep telling & showing pictures of is a compressor gone bad due to liquid refrigerant returning back to the compressor. even if the bell ends loose the frost after a defrost cycle, i bet there is a ton of liquid refrigerant trapped in the compressor oil.

    you seriously need to take superheat readings & sub-cooling readings. with this info, you should be able to present these facts to your boss to prove to him the system is flooding back & needs to be address. i like the idea of installing a pressure limiting txv . make sure the sensing bulb is positioned correctly, tight to the pipe and is insulated properly.

  18. #18
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    one compressor icing over or whole rack? HG defrost? check valve dinked?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •