Results 1 to 13 of 17
    Nov 2011
    Heat Pump Outdoor Fan Cycling (Not defrost)
    I have an AUX mini-split heat pump. The outdoor fan seems to cycle on and off when in heating mode. Any idea what this is about? BTW, I'm not talking about defrost and it seems to heat perfectly fine.
    AUX KFR-32W, 12,966 BTU/hr (heating), R-22, installed in 2003.
    For the full specs sticker, see the pic.
    Saint Augustine, Florida, United States
    Jeez, what's the matter? You can't read that?
    I would GUESS it is some weird controls deal. Good luck.
    Nov 2011
    Quote Originally Posted by JWB View Post
    Thanks - but nothing is broken (I don't think...). Just curious.
    Apr 2001
    Over Here
    I am not familiar with their design, or that particular unit, but for heat pumps, some manufacturers regulate high pressure by cycling the OD fan in heat mode.
    If this is not normal to you for this unit, and that is the case, check the filter or indoor coil. It or they may not be moving adequate air causing higher than acceptable discharge pressure. Another cause of this would be operating heat when outside ambient air temp is 'warm', but inside conditions require heating.
    Nov 2011
    Quote Originally Posted by thermojohn View Post
    I am not familiar with their design, or that unit, but for heat pumps, some manufacturers regulate high pressure by cycling the OD fan in heat mode.
    I moved in during the summer, so I have no idea about what the "normal" is for this unit in heating mode. But like I said, it seems to heat fine.
    I cleaned the indoor coil with foaming coil cleaner/disinfectant (less than 2 months ago) and clean the washable filters regularly.
    Right now it is just above freezing at 3c outside and indoor temp set at 24.
    Apr 2001
    Over Here
    Quote Originally Posted by Jim1977 View Post
    I thought I could barely make out 50hz on that data plate. Maybe you can find a manual online that would explain the operation in layman's terms what is going on. If it's heating fine, I would suspect the cycling fan is what I originally posted. If it ices over, and does not defrost, then you have a defrost issue.
    Your indoor coil may be impacted inside. Coil cleanings can be misleading if you can't pull and clean it.
    Nov 2011
    Sorry, but this site really limits the size of pictures...
    Here is the nameplate again but larger and a pic of the coils.
    you have a ductless/mini-slipt system.
    this unit converts a/c to d/c and DOES cycle the fan and/or compressor.
    I would also guess that it was not from a local dealer, probably online order or "seconds" by looking at that label!!
    Nov 2011
    It's local to me -- I'm in China.
    Tallahassee, FL
    And most of us are in N America! We cant read Chinese!
    Although we may have to one day. :/
    Nov 2011
    Quote Originally Posted by SBKold View Post
    You don't have to know Chinese to understand (most) of the specs
    Model: KFR-32W
    Indoor units: 1
    Voltage/Frequency: 220V / 50 Hz
    Capacity (Cooling/Heating): 3.20 kW / 3.80 kW
    Draw (Cooling/Heating): 6.0A / 6.2A
    Consumption: 1.28kW / 1.32 kW
    Pressures (min/max): 0.8MPa / 2.8MPa
    Refrigerant: R-22
    Charge: 0.85 kg
    Air Volume: 520m^3/h
    Noise (Indoor/Outdoor): <41 / 51 dB
    Weight (Indoor/Outdoor): 10.5 kg / 38 kg
    Manufactured: 2003.08.31 (Ningbo, China)
    Need a local tech to check it. Thats not a unit that most of us would know how its configured to work.
    Nov 2011
    I'm not sure it would be worth the money to have it checked out. I am thinking of just replacing it with a Hitachi RAS/C-36 before it gets too cold.
    Links to diect purchase sites are not permitted
    Capacity (Cooling/Heating): 3.60 kW / 4.20 kW
    Consumption: 1.07kW / 1.20 kW
    Air Volume: 600m^3/h
    Noise (Indoor/Outdoor): 27-39 / 50 dB