    Outdoor section will only run about 30 seconds and then loud compressor growl and board locks the low voltage out.

    The first time it did this the suction went to zero, so I added refrigerant and it did it again with suction on 100psi. This is 410a refrigerant. Compressor amps were 14 on a 4 ton unit.

    Stumped.
    "And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,257
    where:

    is the low psi switch in relation to where you are getting low pressure reading?

    got a mod #

    you running in heat or cool?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Nov 2011
    Location
    USA
    Posts
    197
    Quote Originally Posted by dandyme View Post
    where:

    is the low psi switch in relation to where you are getting low pressure reading?

    got a mod #

    you running in heat or cool?
    Yeah, you may have started out with a low pressure trip, and now having a high pressure trip after adding refrigerant. Switch cycles and see what happens.

    You really need to troubleshoot the original low pressure issue. Maybe a TXV problem.