Thread: Master/slave
-
12-04-2011, 05:06 PM #1
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
Master/slave
Hello everyone I am new to site. I have visited many times great site.
Ok I have two 30ra 030 aqua snaps. They both have MBB version 4.0. The problem is that my control point is getting down to 32 or so degrees because it is looking the common dual sensor and the other chiller water temp that is not running and compensating for the water temp difference in the two. The maste slave is not working correctly. I have been on phone with carrier tech support for hours the above is what they said. Any ideas on what to do. Thanks guys
-
12-04-2011, 07:23 PM #2
Professional Member
- Join Date
- Oct 2011
- Location
- La.
- Posts
- 211
Page 26 of the install/ service book that came with the unit. Labled configuring and operating dual chiller control. This is where you will find how to set up the units. Make sure that units are piped correctly, in parallel config. Then check common sensor location and make sure that you are reading correctly the water temp. One chiller must be master, and has the common water sensor. Then the two chillers are connected with the CCN bus. I have done this many times and it always works. The only problem ever was when the welders put the common sensor location in an air pocket in the piping. The master chiller makes runs like normal until it sees that the load is being lost, then the other chiller is called on by the master.
-
12-05-2011, 07:41 AM #3
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
I have got it set up correctly i believe. I have contacted carrier and they wa;k through the config tables the problem is that the control piont is floating so much. The set piont is 45. the control piont is around 32 or even lower at times. Carrier said it is the version of the MBB and the way it controls the algr. between the two. Is ther a better way to set these two up. the dual sensor is in the common loop and landed on the master.
Hope this make sense
-
12-05-2011, 07:52 PM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
-
12-05-2011, 10:07 PM #5
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
Yes parallel and it has isolation valves on both Ew and LW
-
12-05-2011, 10:37 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
-
12-06-2011, 07:57 AM #7
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
LWT=49.9 dual = 54 entering and leaving of other chiller that is not running is 57 my control point is around 32
Thanks for your help
-
12-06-2011, 08:19 AM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
12-06-2011, 09:44 AM #9
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
Ok what would the ISO vavles do? Should I turn the slave valve off and see if dual sensor is the same as LWT
-
12-06-2011, 10:38 AM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
12-06-2011, 11:18 AM #11
Regular Guest
- Join Date
- Dec 2011
- Location
- TN
- Posts
- 25
No it has manual full port ball vavles. The alarm is T116 Sorry for not clarifying the vavles
-
12-06-2011, 11:27 AM #12
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,511
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.