  1. #14
    Join Date
    Nov 2011
    Posts
    22
    @ beenthere,
    Actually, I did not get a reply from post #6

    I can changed the time --- I have built and programmed my own control board.

    pilko

  2. #15
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    barbar. Read this post.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #16
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    Quote Originally Posted by pilko View Post
    @ beenthere,
    Actually, I did not get a reply from post #6

    I can changed the time --- I have built and programmed my own control board.

    pilko
    I believe he means the "average guest" would have the probes to check temps to make the graphs you did.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    Quote Originally Posted by pilko View Post
    @ beenthere,
    Actually, I did not get a reply from post #6

    I can changed the time --- I have built and programmed my own control board.

    pilko
    So why would you want to shut off the indoor fan, and then make a timer to make it run in defrost even longer yet, using more electric for defrost? A bit counter productive to what you would want.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    Only the Thread starter, and pro members that have an * in their titles may post in a thread in the AOP forums.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #19
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    This is from the AOP forums rules.


    THE ONLY PEOPLE allowed to REPLY in the Owner Assistance Forums will be a Pro Member with a * by their user title and the one who started the thread. No others may post a reply.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #20
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    barbar.

    You have worn out your newb grace. If you continue to post in this thread, I will take action. And that action will cost you your posting privileges.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #21
    Join Date
    Nov 2011
    Posts
    22
    In an attempt to settle the argument I have recorded a defrost at 1000 CFM and a second defrost at 500 CFM.

    Red = Discharge air temp From "A" coil
    Dark blue = Return air temp to "A" coil
    Green = Outdoor temp
    Light blue = Frost level on outdoor coil
    Attached Images Attached Images  

  9. #22
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    What did you use to measure the amount of frost on the coil?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #23
    Join Date
    Nov 2011
    Posts
    22
    I designed the sensor myself. Have been using it for about 8 years.

    pilko

  11. #24
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    And it senses/measures how?

    Has anyone taken pressure and temp readings while its in defrost with the indoor fan running, and without the indoor fan running.

    Is that other guy comparing a unit designed/made to defrost without the fan running to your unit which is designed/made to defrost with the fan running.

    The Japanese brands are designed to shut off the fan, your Carrier isn't. With the indoor fan off, your compression ratio is higher the longer its in defrost then if the fan was running. So the compressor uses more electric during defrost, and will run in defrost longer.

    Keep in mind, that the COP in defrost is not as high as you were told it would be. Since the indoor coil isn't getting a full head of liquid. You can listen to the refrigerant flow, and hear the surging. The surging will be from vapor entering the indoor coil along with liquid during defrost.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  12. #25
    Join Date
    Nov 2011
    Posts
    22
    @ beenthere,
    thanks for the response.

    And it senses/measures how?
    sorry, cannot disclose that info.

    Has anyone taken pressure and temp readings while its in defrost with the indoor fan running, and without the indoor fan running.
    I have only taken air temp readings as per the chart at 1000 CFM and 500 CFM


    Is that other guy comparing a unit designed/made to defrost without the fan running to your unit which is designed/made to defrost with the fan running.
    I will ask

    pilko

  13. #26
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,699
    So you may also be doing a lot of un-needed defrost then.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event