I have a air handler in the attic, part of a Hyrdo Air system, not quite sure of the size. The unit short cycles, comes on for 10 seconds or so, goes off, does it again, then on for a short period of time.
The unit also produces a whistling noise in some of the rooms in the second floor. I had my service company out to look at it, they added a return, but the problems seem to be getting worse. Any suggestions!
-
02-19-2006, 10:32 PM #2
Regular Guest
- Join Date
- Sep 2004
- Posts
- 3,157
have a competant hvac contractor out to do a manual J and a ,manual D to determine if you have an oversized unit and to determine the proper duct size for your unit. It sounds like you have an oversized unit and ductwork that is to small
-
02-21-2006, 12:44 PM #3
Regular Guest
- Join Date
- Sep 2004
- Posts
- 654
Short cycling of air handlers can be many reasons, but if the fan is controlled by an aquastat, making a tuning adjustment to that will eliminate short fan cycles. Thermostat settings can reduce or eliminate short cycling as well. Call a pro.
-
02-22-2006, 12:49 AM #4
Professional Member
- Join Date
- Feb 2006
- Location
- New England
- Posts
- 135
Make sure the aqua stat is on the hot water in line and not the water out line also see if you can set the differencial on the aquastat to at least 20*
Air flow and ducts being too small and or not sealed tight cause noisy operation. Also cheap return registers can sing