    Talking E2 "Reclaim In"

    Hello everyone. My question is about the E2 Condenser control app. What is the strategy behind the "HEAT RECLAIM IN" I understand this is an input that is activated when the heat reclaim is staged on by the HVAC controller, but does it shift (raise) the the condenser control setpoint during heat reclaim?

    A little about myself, I have been in the refrigeration/HVAC for 10 years. I live and work here in the south working for a large grocery chain. Thanks:

  2. #2
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    599
    Yes.

  3. #3
    Join Date
    Jul 2005
    Location
    Southern California
    Posts
    583
    Yes. On the setpoints screen you will see a place where you can enter setpoint that will raise you normal setpoint when the reclaim in input is activated. For example raise your condensing pressure setpoint 20lbs above your normal setpoint when in reclaim.

  4. #4
    Join Date
    Dec 2011
    Location
    USA
    Posts
    66
    Yes, is does shift up the condenser set point to enable more heat for reclaim. Look under the condenser application to see the amount you are shifting.