    Why does not enough sub-cooling cause flash gas in
    rhe liquid line ?? Is there more than one reason?

  2. #2
    Join Date
    Oct 2005
    Posts
    2,044
    Post Likes
    pressure drop or temp rise in the liquid line,

    but theoretically not enough subcooling in the liquid line will not cause flashing,,, If you have one degree of subcooling it will not flash unless the pressure drops further or the temperature of the liquid increases,

  3. #3
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    As the liquid refrigerent flows through the piping the pressure in the piping will decrease over the run of the pipe. If the refrigerent is near the saturation point, this reduction in pressure will reach the point to which the refrigerent will flash.

  4. #4
    Join Date
    Dec 2001
    Location
    Chicago, N/W burbs
    Posts
    8,146
    Post Likes
    yep...what they said. ^^^^^^^^^^^^^^^
    R2B4BTU

  5. #5
    Join Date
    Nov 2005
    Location
    netherlands\europe
    Posts
    2,880
    Post Likes
    Try to understand the Mollier charts, it is a helpfull tool.

  6. #6
    Join Date
    Nov 2004
    Location
    South Carolina
    Posts
    1,864
    Post Likes
    Thread Starter
    Thanks for your help in understanding this

  7. #7
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    That's a cool "connect the dots" shark fin.
    Training is important!
    Practical Training is a must!

  8. #8
    Join Date
    Jul 2004
    Location
    Victoria,Tx
    Posts
    6,691
    Post Likes

    Smile Dutchcool

    That chart is for R22 right? All liquids or gasses behave differantly at given temptures and pressure. Just for fun, if you taken Hexane, pressure it up to 3500# drop it to 100# it will heat up. But pressure it up to 3500# drop it to 0# it will cool down. Funny how things behave when there under pressure! Roy

    [Edited by oroy54 on 02-18-2006 at 03:05 PM]

  9. #9
    Join Date
    Jan 2005
    Posts
    3,585
    Post Likes
    I get flash gas but thats only after I eat at Taco Bell and have a lighter

  10. #10
    Join Date
    Nov 2005
    Location
    netherlands\europe
    Posts
    2,880
    Post Likes
    Originally posted by papa_jo
    Thanks for your help in understanding this
    I am sorry!i hadent had enough time when i first posted.
    I dont know if you in the U.S. are using the same type of chart, i think you might use a differend one, and makes this one look upsidedown perhaps.
    I will try to explain what i know of it, [dont expect to much, hihi]i have to translate my thoughts becouse normaly i speaka the dutch.
    The area what we are talking about is in the orange cirkel.
    If that point moves to the area inside the ,,shark fin" [the left part shows the saturated liquide line] you will have flash-gas,it is no longer 100% liquide but there is some vapor in it as well.
    The sat.liq curve represents heat in liq.refrigerant at differed pressures befor it starts to vaporizing.
    I hope this is of some help.
    I ask others to confirm or tell it wright.

  11. #11
    Join Date
    Nov 2004
    Location
    South Carolina
    Posts
    1,864
    Post Likes
    Thread Starter
    thanks Ducthcool I am in the US southern us south carolina

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •