    Aaon with a Honeywell t-stat

    Looking at a AAON heat/cool rtu that won't run in heating mode. The t-stat is a Honeywell T7350m1008 which is now obsolete according to Honeywell.
    The wholesale is no help....they can't cross-reference it.....anybody?

  2. #2
    Join Date
    Jan 2005
    Location
    steeler nation
    Posts
    2,339
    Post Likes
    http://customer.honeywell.com/honeyw...spx/T7350M1008

    Modulating output thermostat. I buy these in a communicating version all the time. If you can't find one locally pm me. I can hook you up with my distributor.

    In reality you could probably use any modulating stat.

    Viconics and many others make modulating stats.
    Are you sure it is a thermostat problem?

    http://www.google.com/products/catal...ed=0CEEQ8wIwAw

    Google returned a gazillion for sale on line.
    IV IV IX

    use your head for something other than a hat rack.......Gerry


    We have freedom because somebody fought for it.
    We keep it because we are willing to fight for it.
    We lose it because we are not willing to fight for it.

  3. #3
    Join Date
    Aug 2003
    Location
    S.W. Ontario,Canada
    Posts
    622
    Post Likes
    VICEMAN......thanks for your help.

  4. #4
    Join Date
    Jan 2008
    Location
    Ottawa, Canada
    Posts
    167
    Post Likes
    Even if the unit has a modulating burner it should heat on a call for W1 from a regular stat. As long as it's a model with a terminal strip and stand alone mod gas board. You just have to set your discharge reset dip switches to your desired discharge air temp. If it's a Wattsmaster system you'd have to connect to the forced heating input on the board and necessary programming done via a handheld or system manager. Essentially on a call for heat the burner comes on and if it's not receiving a modulating signal from the stat it will see that as a 0 VDC signal and fire to whatever your reset on the mod gas board is set to, you reset limit is basically not used. Clear as mud??