Thread: Do I really need a 20,000 ohm, 5 watt resister to de-energize a capacitor?

  1. #21
    Join Date
    May 2009
    Posts
    520
    Post Likes
    no

  2. #22
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    First, a meter should not be used to discharge a capacitor, unless you like buying new meters often.

    Second, capacitors will hold a charge depending on how it is placed in a circuit.

    The reason a run cap doesn't hold a charge is because the motor windings discharge it very quickly. It does have low resistance, but it also has greater mass to dissipate the charge via heat.

    Unless it is placed in the circuit as a trickle charge capacitor. That is why there is a resistor on those aswell. To discharge the cap before a tech touches it. If you don't believe me, wire in a trickle circuit without a resistor across the terminals. Allow it to run, then pull the disconnect and check the voltage across the cap terminals.

    A start cap uses the bleed resistor for two reasons. One, to protect the potential relay from welding it's contacts, and two to save a tech from getting shocked.

    Yes, you need a 20kΩ 5watt minimum resistor.
    Theory... higher wattage resistors can dissipate heat better. That is pretty much what you're asking it to do, in order to discharge the cap.

    Typical caps are 370v when charging.

    Ohms law tells us E/R = I, and IE = P.

    So, when charging at 370V/20000Ω we get < 0.0185A. (charging is by reactance which is lower or < resistance of the resistor)
    When discharging to line voltage at 230V
    we get 230V * 0.0185A = 4.255W

    Using a screwdriver to discharge a cap is a good idea. Not so much for the equipment, but for you. I would much rather eat up a screwdriver or cap than get shocked. In most cases, the cap should be discharged before you have time to touch it. If it's not wired properly or an issue with the circuit, it could hold a charge. I don't know any tech that carries a 20kΩ resistor in his/her pocket. So a screwdriver is a good sacrificial alternative.
    Last edited by mgenius33; 11-30-2011 at 09:40 PM.
    "The only true wisdom is in knowing you know nothing" Socrates

  3. #23
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    The charging part of that last post is wrong. Was just going off the top of my head.
    "The only true wisdom is in knowing you know nothing" Socrates

  4. #24
    Join Date
    Oct 2004
    Location
    Texas
    Posts
    1,176
    Post Likes
    Notice the arc flash when you short the cap. For your start relay it will experience that arc flash on every start up if your start cap does not have the resistor. As for discharging when wanting drain the energy then short it or bleed it (speaking of capacitors in residential or small electric motor applications),NOT VFDs.
    Saddle Up!

  5. #25
    Join Date
    Oct 2011
    Location
    Derby, Connecticut
    Posts
    30
    Post Likes
    I don't know anyone who carries around a 20k ohm resistor either. Definitely use a screwdriver. Your teachers just tell you that because they have to give you the most professional methods available.

  6. #26
    Join Date
    Jul 2009
    Location
    Northern area between Alantic and Pacific
    Posts
    112
    Post Likes
    How big the cap is,if small charge inside I just use screwdriver.

  7. #27
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Well over 90% of the time, the run caps you will encounter on a day-to-day basis discharge themselves very quickly through the motor windings when power is removed. Most start caps have a bleeder resistor. It isn't good for an electrolytic capacitor to discharge it by direct shorting (it harms the plates and the electrolyte between them), but since most all caps are already discharged when you put your screwdriver across them anyway it doesn't really matter.

  8. #28
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    Should not direct short the cap terminals, or hook your meter to a charged cap. If you don't want to buy a resister, take one off a used or old start cap. 15k ohms is plenty. Discard the altered cap in a responsible way, please!

  9. #29
    Join Date
    Dec 2011
    Location
    Ozarks of Missouri
    Posts
    32
    Post Likes
    As an electrician for 20+ years, my 2 cents: big enough start and run capacitors, if charged, CAN vaporize a nice divot in the screwdriver and render the cap's terminal a useless stub. If you suspect the cap might have a charge, use a screwdriver you can afford to lose, and land the blade first, then complete the short with the shaft: the arc will spring from the terminal to the shaft and you'll still have a usable blade end on the screwdriver. As others have said, most caps will be fully discharged through the compressor within a few minutes of shut-down. I short them all because I'd rather replace a yard sale screwdriver for a buck than my fieldpiece meter.

    Caps encountered in residential HP equipment I'm used to aren't big enough to do much damage UNLESS you forget to pull the disconnect! An energized system can yield: 1) welded/blown equipment; 2) a screwdriver converted to a lethal missile; 3) a scorched spot on the earth where your boots where when you smoked yourself.

    I've been to more than one funeral for guys who KNEW the circuit wasn't energized.

  10. #30
    Join Date
    Dec 2011
    Location
    Chandler
    Posts
    16
    Post Likes
    what kinda cap are you trying to discharge is the right question...if its a run cap under 80mfds

    it will discharge withing 30seconds MAX

    now a car audio cap..thats a different story....or a cap bank for a diesel power back up...totally different story

    instructors at trade schools tell new techs all sorts of crazy stuff

    i had a new hire tell me i was ruining package units becuse i used a drill to take of panel screws...lmao

  11. #31
    Join Date
    Jan 2011
    Location
    IOWA
    Posts
    11
    Post Likes
    I use any tool with rubber handle to verify discharge of run or start caps . Get into habit just because the disconnect looks off doesnt mean all legs are dead bad disconnects will kill .

  12. #32
    Join Date
    Dec 2011
    Location
    Ozarks of Missouri
    Posts
    32
    Post Likes

    VERY good point!!!

    Quote Originally Posted by broc123 View Post
    I use any tool with rubber handle to verify discharge of run or start caps . Get into habit just because the disconnect looks off doesnt mean all legs are dead bad disconnects will kill .
    I will ALWAYS check the high voltage side of the contactor, either with the NCV on my meter or if I'm really paranoid, with the leads and that's BOTH legs of the supply wiring.

    You've got the service panel off: why NOT check it: the life you save may be your own!

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •