Results 14 to 26 of 32
    Oct 2011
    When you hear the first click, are the defrost heaters energized at that point or are they energized on the second click? It sounds like the defrost timer is working correctly and you have a defrost termination swich location problem or faulty sensor, is the "X" wire hooked up in the timer? if so, try unhooking for a day or so and see if defrost completes, if so, than sensor problem.
    N.J.
    The system is time initated temp. terminated. The timer should advance thru unassisted.The 60 min. setting you speak of is a fail safe setting and should not be looked at as a primary defrost time.The uneven frost pattern you mention could be caused by many different things.You must do alot more trouble shooting on this system for a proper diagnoses!!
    Oct 2011
    Chicagoland Area
    What brand evaporator coil is it? Heaters on the bottom only or heaters on the bottom and back? In most cases the defrost should only last 20-25min then terminate via the defrost termination switch(X) terminal on the clock. The fact that you have a door that is not being closed with warm WIC air blowing into the WIF will also be an issue. Also check pipe chases and the box seams for air infiltration. You say the heaters only stay on a couple minutes? What's causing them to deenergize? A heater limit? The DFTS(sometimes they short internaly)? Are these switches located on the utubes or attached to a bracket? I have always set timers in WIF in restaurants to defrost every 6hrs and set the backup for 45min.
    Nov 2011
    The heaters energize after the second click, after the pump down. The unit is time initiated and temp terminated. That fact may resolve one of my concerns that the heaters do not stay on long enough. Once that coil reachs 50F the defrost termination switch will denergize the heaters and energize the solenoid. There are two heaters one loops through the coil and the other is a drain pan heater. Its a Heatcraft evap. The timer is set for 60 min every 6 hours. There are deffinetly more problems with this unit, I just wanted to understand how the timer works. If its set for 60 mins and the heaters heat up that coil to 50F within 20 mins will it cycle the heaters on and off or is the defrost over once the defrost termination switch closes?
    Oct 2011
    Chicagoland Area
    Defrost termination switch/fan delay switch energizes the X terminal on the time clock which is connected to a soleniod that switches the NO to NC and the NC to NO and the freeze cycle begins again.
    Edit: The heater safety and termination/fandelay are affixed to the side support located on the outlet side of the coil approx 1/2 way up from the bottom. This would explain why you continue to see ice on the top half of the coil if one or both the switches are bad. The drain pan heater may not be working causing the bottom half of the coil to stay frozen. Both heaters should draw the same #of amps. With the info given, I'd be wiiling to bet the warm air infiltrtion is the main issue which iswhy the front (outlet) of coil is freezing.
    Maven445,
    You need to look at the system as a whole rather than focusing on JUST the timer.
    The frost pattern you are describing is somewhat unusual and not likely caused by a timer problem.
    Check your charge and superheat.
    Oct 2011
    Chicagoland Area
    Maven445,
    Based on what the OP described
    The front freezes up really bad with soft ice on top and solid ice on the bottom. The back freezes up just on top.
    I also agree it's probably not a defrost issue.
    Do you really think it's a SH or Charge issue? I understand your thought process to a point but the fact that the entire front of the coil freezing up makes ke think it's due to high humidity levels or air infiltration. It's been my experience that a charge or metering device issue would freeze the bottom or inlet portion of the coil, but shouldn't have an effect on the entire face of the coil. No? Could be a combination of issues.
    OP, Have you checked fan rotation? Aftermarket Heatcraft fan blades have the hub on the opposite side as the OEM fans.(when installed the hub is on the motor side of the blade rather than the fan guard side of the blade) It's possibe someone could have replaced a fan blade and installed it backwards, reducing airflow across the coil.
    British Columbia, Canada
    Old thread but the following info still applies...
    Defrost coil completely with hot water/ice cutting gun.
    Shut the door. Problem solved. Have seen this same situation all too often. Put buzzer on freezer door switch if staff can't be trusted to shut it completely.
    IF door HAS been confirmed shut and problem still exists, Airflow checks, Heater checks, DTFD checks(proper #'s for that evap-have seen someone replace with what they had-not good enough), Adjust duration to LESS than 60 minutes, all as explained above.
    Apr 2012
    Northern Virginia
    You need to make sure that the defrost termination thermostat is opening and closing at the correct temperatures. After that the only other issue would be the defrost clock and or a wiring issue. Nobody's perfect man. We've all done it before. Just double check your wiring diagram.
    Danville, IN
    Quote Originally Posted by Maven445 View Post
    I posted this in the wrong section before maybe someone here can help me. I have a problem with a walk in freezer. The evap coils keeps freezing up, about 1-2" a week. The front freezes up really bad with soft ice on top and solid ice on the bottom. The back freezes up just on top. During the defrost when the arm first hits the pin, nothing happens. The pump down doesnt start until the second click, by then there is about 10 - 20 minutes left on the defrost. The defrost is set to 60 minutes. The heaters only stay on for a couple minutes after that. I've replaced timers before, but I dont know the actual sequence and what the terminals are associated with. Any help would be great.
    Well is it truly time defrost termination.... or temperature or pressure?
    Mar 2015
    Medford, N.Y.
    Something sounds like 2 different Maven445.
    Oct 2014
    GA
    Soft ice on top is moisture from somewhere. The soft ice is melted buy
    T doesn't achieve proper run off and freezes to hard ice below. Must fix the infiltration of air first. 60 minutes sounds like a lot move defrost to 15-20 minutes 3-4 times day. Start there but sounds like infiltration is your problem.
    Jun 2013
    N. Canada
    I may have figured out the multiple click fiasco:
    Doesn't Heatcraft have some condensers eqpt with a defrost contactor controlled thru a NC contact on the comp. contactor??
    In other words...no defrost until pumpdown is complete ( 2 clicks before defrost).