Thread: Hussmann M5X-EP meat cases

  1. #1
    Join Date
    Feb 2003
    Location
    NH & Cebu
    Posts
    1,614
    Post Likes

    Hussmann M5X-EP meat cases

    I will be installing 32' of Hussmann M5X-EP cases in a few weeks. I did not order nor sell these. A retail grocer/wholesale grocer has ordered and purchased them. They are coming through with electric defrost. I know from looking back at the HVAC-Talk archives that some of you prefer this over air defrost for meat cases. I figure quicker is better, but what about the meat? What does it want? Currently we have 32' of Tyler case with the reversing fans for defrost.

    When I checked the data sheet on the Hussmann cases, it said hot gas and electric are not recommended. What's the thought on defrost for meat cases? They are going on a single outdoor unit. No rack.

    I doubt we can change the order to air defrost. But do we just not hook up the electric? What do you guys think?

  2. #2
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    I wouldn't hook up the heaters either. 3-4 x a day time off with fans running would Wouk just fine.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  3. #3
    Join Date
    Mar 2013
    Location
    NJ
    Posts
    414
    Post Likes
    If decide to use the electric, be sure the termination klixons are properly positioned and wired if you are using and old style clock. The old timers used to say refrigeration stats in parallel, defrost term stats in series. If you are using an energy management system the sky is the limit, some prefer to use discharge air temps for termination.

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by crackertech View Post
    I wouldn't hook up the heaters either. 3-4 x a day time off with fans running would Wouk just fine.


    Hussmann recommends off-time defrost, 30 minutes X 4 per day.

    http://www.hussmann.com/en/Technical...7_J_M5X-EP.pdf (See p.3)

    The way I see it, back in the days when meat cases ran with evap temps of around +10°F a lot of frost built up and electric or hot gas was the only way to defrost quickly. These M5X-EP cases run at 28°F evaporator for 32°F discharge air.

  5. #5
    Join Date
    May 2010
    Location
    Canada
    Posts
    1,224
    Post Likes
    I didnt know you could order them with electric heaters.

  6. #6
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    The hot gas and electric defrost specs are listed on a separate page. 20 minutes, term at 48* for this case and if it is ordered with heaters then use them.

    http://www.hussmann.com/en/Technical...iveDefrost.pdf

  7. #7
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    The meat case I service is an old aluminum coil hussman. Air defrost 4x per day. We run the case 34 F. It's a 10 degree coil so coil sees 24F. During humid months we get some frost. Air defrost works fine.

  8. #8
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    I would install an EPR and use it to control the case temp. This will keep the temp steady and also the evap temp higher so you get less frost. Most of the walmart's we install and service use air defrost and EPRs. We run 28 degree discharge air and the case tstat is set at 25 degrees so we have 100% runtime in between defrosts.

  9. #9
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    Quote Originally Posted by bob_scheel View Post
    I would install an EPR and use it to control the case temp. This will keep the temp steady and also the evap temp higher so you get less frost. Most of the walmart's we install and service use air defrost and EPRs. We run 28 degree discharge air and the case tstat is set at 25 degrees so we have 100% runtime in between defrosts.
    It's not on a rack, therefore no EPR.

  10. #10
    Join Date
    Feb 2003
    Location
    NH & Cebu
    Posts
    1,614
    Post Likes
    Thread Starter
    Thanks to everybody for your help. And thanks to mspanky for the defrost link. My electrician will be thrilled with the data, since we were provided with no specs, and we couldn't locate info on defrost

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •