Thread: Bolier shuts down
-
02-07-2012, 08:15 PM #1
Regular Guest
- Join Date
- Feb 2012
- Posts
- 6
Bolier shuts down
We have proble that has been around for over 5 years and have had our crew try everthing but replace the controls- it is a 1992 PowerFlame buner with Honeywell control R7795 the reset trips almost every time for a few days then its gone and runs evertime for awhile and acts up allover.Have cleaned and tested all parts and appear to work right then get a call of noheat? Any thoughs would bee helpful
-
02-07-2012, 08:57 PM #2
Professional Member
- Join Date
- Mar 2003
- Posts
- 7,249
solid ground? some stray voltage on the neutral? its time for a new one?
-
02-07-2012, 09:06 PM #3
at a loss all grounds are clean, tight?
-
02-07-2012, 09:10 PM #4
Regular Guest
- Join Date
- Feb 2012
- Posts
- 6
We have installed boiler on a new ele. panel added 10agw ground and cleaned all grounded spots and toqured down all.
-
02-07-2012, 09:19 PM #5
how is the combustion on it? could the room be possibly going into a negative pressure when it goes on lockout? is it gas or oil? have they added something else to the gas lines which steals fuel supply ?
-
02-07-2012, 10:54 PM #6
Regular Guest
- Join Date
- Jan 2008
- Location
- s chester county,pa
- Posts
- 140
you forgot to clean a very important part
-
02-07-2012, 11:00 PM #7
what is the error code????????????????
-
02-08-2012, 01:20 PM #8
Professional Member
- Join Date
- May 2003
- Location
- USA
- Posts
- 180
had a boiler kick my butt for a week--replaced a lot of parts and cleaned everything-twice and it still failed to lit off--turns out the ignitor had been there for so long it actually blasted away the metal and where the spark made contact was egg shaped---replaced that--never had a call again--still have old one in tool box as a reminder
Rather be golfing!
-
02-08-2012, 08:38 PM #9
Regular Guest
- Join Date
- Feb 2012
- Posts
- 6
The problem is we have not seen any codes. as to neg pressure the room has a excellent flow of air. Its a Nat. gas supply is 2 inch feed from a high pressure line from National Grid.Worked great for 36 hours till it tripped out reset it and was working till i went home 3 hour latter. I work full time on site have three boilers in three buildings along with a 60 ton HVAC unit,also do all electic and pluming repairs.This our newest boiler with electoic start other 2 our bullet proof 1 is 60 years old other 45 years old all get NYS insection every 2 years.
.
-
02-08-2012, 08:42 PM #10
Regular Guest
- Join Date
- Feb 2012
- Posts
- 6
Have cleaned burnner and photo eye all other were cab.in fall and ran good till 2weeks ago,gas pressure is right on just stumped. would love to get rid of ele start and go back to full time piolt light.
-
02-08-2012, 08:43 PM #11
-
02-08-2012, 09:22 PM #12
Regular Guest
- Join Date
- Feb 2012
- Posts
- 6
There is no display tow lights 1 is power 1 is fuel is on this is a powerflame on a weil-maclan boiler, it trips and stores no codes that i know of.
-
02-08-2012, 10:48 PM #13
what about the gas valve does it have a (I'm at a loss for the name but) diaphragm in it and a orifice on the side to bleed the pressure out for a controlled ignition. usually inline with a solenoid gas valve.


Reply With Quote