Results 1 to 13 of 14
Thread: Insulated Vent?
    Aug 2011
    Fort Mcmurray,Ab
    Insulated Vent?
    I have a client who wants me to insulate a flexible chimney vent (7/4) for a gas fireplace because he is worried about condensation where it passes through a cold space before hooking up to the fireplace. I told him it can't be done because I need to keep my clearance to combustibles and insulation is combustible, he says he had one installed before and they used foil back ins. with the foil against the vent and then wrapped again with the foil on the outside . Is this right or am I right in sticking to keeping clearances ? Thanks.
    S.E. Pa
    Cool
    the code prohibits you from wrapping vents and connnectors. Also, wrapping vents with anything, no matter the fire worthiness, restricts the flow of cooling air thus voids the warranty and listing. You need that air flow to reduce temps. Insulation works--it keeps hot things hot. We want to cool them.
    HTH
    Aug 2011
    Ontario
    No need to insulate 7& 4 will only cause problems. I have hundreds running through unheated attics etc., never been a problem. And its cold here.
    There is no bad beer, some just taste better than others.
    Jun 2008
    Madison, WI
    wood stove exhaust usually is hot enough to not condense. If it was a problem (like you have a low temperature boiler) you could use double-wall exhaust duct. (I'm not sure this is the correct word, but you create an airgap between two pipes that insulates. since both pipes are metal, no issue with combustion). that actually may be necessary to protect any surrounding material from heat. Especially where humans could touch it. Obviously nothing should touch the exhaust duct.
    Aug 2011
    Ontario
    Quote Originally Posted by kaleun View Post
    Not the question. It is a fireplace.
    Aug 2011
    Fort Mcmurray,Ab
    Thanks MANACO I've used ceramic fibre blanket before on welded exhaust duct for a kitchen and It wasn't the easiest material to work with but If that's what he wants, the customer is always right? right!
    Aug 2011
    Ontario
    You best check with manufaturer to see if that may void any warranty.
    S.E. Pa
    Exclamation don't wrap the pipe unless listed that way!
    It will void the warranty and listing. I sit on the UL Standards Technical Panel that writes the UL listing stds so please trust me--wrapping listed venting is a fire hazard! It isn't so much a matter if the insulation can take the heat or not but that it prevents the venting from cooling. This makes the entire fireplace hotter. Don't do it!!!!
    BTW, most ceramic fiber blanket is rated to about 2,150F before it begins to degrade substantially. CF blankets are routinely wrapped around stainless steel chimney liners and factory chimney listed to UL 1777 and UL 103HT respectively which are 2,100F listings.
    A gas direct vent, which is what the OP described runs about 500-600F--when the pipe is allowed to cool by ambient air.
    S.E. Pa
    Exclamation
    Manaco, I must advise you, you are giiving out falty hazardous advice here that goes directly against codes, standards, listings and fire science. I am reporting your post and asking you to temper yourself to these stds. You may go freestyle in your own job but this site does not condone advice that contradicts these principles so blatantly with procedures that are known causes of unfriendly fires.
    Again, this is a direct vent gas fireplace that does not and cannot use double walled factory chimney.
    Aug 2011
    Ontario
    Listen to the hearthman, he knows what he speakath.
    Under review.
    Nov 2011
    vancouver island canada
    Manufacturers specifications rule! The customer is not always right whcih is why we are called.
    ryan