Another belt question
Seeing all the threads about belts made me think of a job I had a few years back.
Unit had a habit of chewing belts up. Appear to be getting overheated due to damage, cogs being torn off and rubber dried out and hard. Leads me to believe they were slipping.
1. 60 ton RTU, forward curve supply fan, controlled by VFD, no return fan. 2"WC at outlet, 1.5 duct static during normal operation, VAVs within normal CFM range. Can see as low as 1"WC duct pressure and VFD at 60HZ during unocc recovery.
2. Belts, pulleys, motor all original sizes and specs. Grooves not worn. Tension checked and aligned. Don't remember sizes.
3. Installed new belts, checked tension, everything normal till about 57 HZ and then the belts would start floating, then squealing. Belts getting warm.
4. Rechecked tension and alignment.
5. Belts fine up to 55HZ.
6. During this time fan outlet and duct pressure lower due to VAVs being open.
7. Checked the duct work, no restrictions, fire dampers open.
7. Calculated fan RPM from pulley diameters and motor RPM and well below max RPM and within units manufacturer specs.
Seems to me that RPM was too high. I had contacted a local motor shop that does laser alignment and vibration analysis and they has no idea either.
-
11-23-2011, 12:19 AM #2
New Guest
- Join Date
- Nov 2011
- Posts
- 4
At 57HZ you are at near full rpm of the motor. The VAVs are full open. Could the fan be loading up too much and spinning/skipping the belt? Did you take an amp draw of the motor to see how loaded it was?
-
11-23-2011, 06:16 AM #3
Professional Member*
- Join Date
- Dec 2002
- Location
- SouthEast NC ICW & Piedmont Foothills
- Posts
- 7,254
are the sheaves worn?
It`s better to be silent and thought the fool; than speak and remove all doubt. 
-
11-23-2011, 08:56 PM #4
Professional Member
- Join Date
- May 2004
- Location
- SE Pennsylvania
- Posts
- 515
Amperage was close to FLA at 60HZ. My thought was that the fan was at the end of its curve but during this time static pressure at unit was less then when VAVs and duct static reached normal operating conditions. In a CW rotation, motor to the left, the upper length of belts would start lifting a good 3 inches or more and slapping and the lower length would remain taunt.
No they are not see #2
-
11-23-2011, 10:56 PM #5
Regular Guest
- Join Date
- Nov 2011
- Posts
- 7
-
11-24-2011, 01:49 AM #6
If this unit has an adjustable motor pulley and it has been used with cogged belts and is more than 3 years old it is time for a new motor pulley. And you might want to measure it and go with a fixed pulley this time. Since it has a vfd you don't need an adjustable pulley. You may need to adjust those belts a little tighter than your tension tool tells you to. Last week the senior service tech and I replaced a 35 horsepower motor for a supermarket main store A/C and I tensioned the belts with my Gates tension tool and they were not tight enough to stop the screeching sound. Go ahead and tighten them a little at a time until the squeeling stops. (after you replace that motor pulley!)
Challenge yourself, take the CM test --- Certificate Member since 2004 ---Join RSES ---the HVAC/R training authority ---www.rses.org
-
11-24-2011, 02:11 AM #7
What kind of belts are you using?
What is the diameter of the smaller sheave?
What is the maximum RPM of the motor?
How many horsepower is the motor?
Adjustable or fixed sheave?
Check the sheaves very carefully. There may not be a groove, but the angle can be worn to a different angle or worn concave slightly. This may not be really easy to see. There are plastic gauges you can get that may help you see if they are truly the right specs.
-
11-24-2011, 07:13 AM #8
Professional Member
- Join Date
- May 2004
- Location
- SE Pennsylvania
- Posts
- 515
Its been over a year since I have been to that job. I think 40 HP, 1750 RPM, had cog belts, fixed sheaves, motor side was replaced, first thought of what problem was, had very slight wear. I would have to do scrounging through records to see if I could find the pulley sizes and more info. I ended up increasing the belt tension, setting VFD max HZ to 55, leaving a note for next guy and haven't been back.
-
11-24-2011, 06:18 PM #9
Make sure both pulleys are compatible with the type belts you’re using.
-
11-24-2011, 09:01 PM #10
Professional Member
- Join Date
- May 2004
- Location
- SE Pennsylvania
- Posts
- 515
-
11-26-2011, 06:37 PM #11
Regular Guest
- Join Date
- Feb 2011
- Location
- OH
- Posts
- 149
with out seeing belt and location . i had a machine shop with extream oil in the air and the oil effected the belts so bad went to a belt that lasted a few months longer .