    Is it normal all the lights dim then my HP goes to the 2nd stage? And electrical panel makes some noise also for a few seconds; breaker does not get hot though. It's 5 or 4.5 ton HP 40amp breaker

  2. #2
    Join Date
    Jun 2004
    Location
    Maryland's Eastern Shore
    Posts
    892
    I would call a NATE certified service company, the situation doesn't sound quite right, BUT, I am not there to see if it is normal or not. You can look up a NATE certified service company in your area by going to natex.org

  3. #3
    Join Date
    Jul 2001
    Posts
    3,112
    I would call a certified ELECTRICIAN to check your panel. A NATE certified technician is NOT certified to troubleshoot your POWER panel. Leave that to the QUALIFIED ELECTRICIAN.

  4. #4
    Join Date
    Jul 2004
    Location
    midwest
    Posts
    2,868
    Originally posted by cde72
    I would call a NATE certified service company, the situation doesn't sound quite right, BUT, I am not there to see if it is normal or not. You can look up a NATE certified service company in your area by going to natex.org
    The last time I checked on that site there were none in my area. Do you think a common tech has a chance of getting it right.

  5. #5
    Join Date
    Jul 2001
    Posts
    3,112
    trane, since we constantly advise others to contact those that are qualified, we need to take our own advice. In your situation, your own superior skills and abilites will be sufficient.

  6. #6
    Join Date
    Mar 2005
    Location
    Suppy NC
    Posts
    4,513
    this is not normal and you need to call a licenced electrician to check the panel. a tech {nate or not} can only check the equipment and should stop at the panel.


  7. #7

    Lights dimming seems to be a common complaint with AC/HPs.
    Weak ground is a culprit sometimes.
    However , the box "making noises" indicates the posibility of arcing, usually a bus bar going bad which means you need to call a trician ASAP.
    The arcing will continue up the bar and potentially kill other breakers.

  8. #8
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    just for the record: my 100a breaker for my elec furn has buzzed for 5y. but it is NOT an arcing sound. I have checked the breaker for heating= none, inspected the terminals= ok, triggered all breaker ea 6 months, and expect no further problems.

    but then, I am qualified -- just letting you know that all MAY not be bad.

    be worried if the breaker triggers 2- 3 times. Do NOT reset it after that. Do not look at any breaker when resetting.



    [Edited by cem-bsee on 02-12-2006 at 08:19 PM]
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  9. #9
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    2,729
    The reason your lights dim and the breaker box hums when your heat pump goes to 2nd stage is because I assume you have 2nd stage electric heat elements.
    Those heat strips pull a lot of amperage. All is probably fine, but if your worried have an Electrician check it out.

  10. #10
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,024
    Originally posted by trane
    Originally posted by cde72
    I would call a NATE certified service company, the situation doesn't sound quite right, BUT, I am not there to see if it is normal or not. You can look up a NATE certified service company in your area by going to natex.org
    The last time I checked on that site there were none in my area. Do you think a common tech has a chance of getting it right.
    No not a chance. Not even an Experior certified Master Mechanic. (Required to pull permits in my area)
    Beware of advice given by some guy on the Internet.

  11. #11
    Originally posted by cde72
    I would call a NATE certified service company, the situation doesn't sound quite right, BUT, I am not there to see if it is normal or not. You can look up a NATE certified service company in your area by going to natex.org
    I would put more trust in a competent tech, than one that relies on his patches to back his experience or knowledge.

  12. #12
    Join Date
    Jan 2004
    Posts
    60
    Originally posted by rsmith46
    The reason your lights dim and the breaker box hums when your heat pump goes to 2nd stage is because I assume you have 2nd stage electric heat elements.
    Those heat strips pull a lot of amperage. All is probably fine, but if your worried have an Electrician check it out.
    No actually it's 2stage HP with gas AUX (3rd stage)

  13. #13
    Join Date
    Apr 2004
    Posts
    7,680
    Can you be more specific? Or would you like an answer as ambiguous as your question? Are there two compressors (Like a trane) is it one that has to stop before it goes into second stage? Or does it shift on the fly?

    Since were guessing, I go with the weak ground.

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event