Results 1 to 13 of 22
Thread: Short cycling
    Sep 2003
    Ocean County, N.J.
    Got a " short cycling " call yesterday. Brand new 1950 sq. ft. home in a gated adult community. Furnace was a Goodman GMS90453BXA, t/stat Honeywell programable { found absolutely nothing wrong with either one }. O.D. temp 30 degrees. I.D. t/stat set point 65 degrees. Furnace runs for six minutes, off for three, and this cycle just keeps repeating. I'm sorry if I didn't mention that the system is maintaining the t/stat set point, and when the furnace cycles off { for 3 minutes }, it's because the t/stat has satisfied. What would you have done? Is anything actually wrong? I'll read some of your posts and then tell you {right or wrong} how I wrote the invoice and billed this call out { regular service rate }. I'm trying to see if I did the right thing.
    Jul 2005
    it could be the Tstat's "cph" setting needs adjustment due to a 'slipped/loosened rotator screw'.
    what type ,model is this t stat?
    Some ,(not all) can be adjusted.
    Some need to be thrown away and replaced.
    leland nc
    alot of honeywell stats have a screw or dip switch on the back the need to be set for high eff units
    this alows them to be universal to all systems
    change the settings and it should make a differance
    Sep 2003
    Ocean County, N.J.
    Thanks for your responses. How many cycles per hour are we looking for with 30 degree O.D. and 65 degree I.D. set point? It is a 45,000 B.T.U. hi efficiency furnace in a 1900 plus sq. ft. home. Again, how many cycles per hour are we looking for?
    Jan 2006
    i wonder if a load calc was ever done 45,000 btu furnace with a nearly 2000 sq ft home?sounds a little undersized.
    Sep 2003
    Ocean County, N.J.
    jeffshvac no arguement from me on the sizeing, but I'll repeat the question: how many cph are we looking for?
    leland nc
    that would pepend on the house and the loss
    there is no set rate that can be given with out this info
    Jan 2006
    i would look for 4-5 cph but it could vary.
    Canada
    3CPH is the general opinion of many on this board.
    Having said that it does not mean much if furnace is not sized correctly. IMHO
    Jan 2006
    3 cph is ideal but with an undersized furnace its not realistic. jmo thanks
    Apr 2005
    Kingston Ontario Canada
    Certainly does sound undersized. A furnace that small in a 2000 sq ft home should be running almost all the time, right?
    Thorton
    Jan 2006
    im sure everyone in this gated community got an undersized furnace this is what happens when a builder takes the lowest bid and the contractor installs the bare minimum equipment.the only people that suffer are the homeowners.and it figures they each got a goodman.jmo thanks
    Sep 2003
    Ocean County, N.J.
    I agree with all of your posts. I wrote on the service invoice:" Checked t/stat and furnace, found both to operating normally. No further diagnostics possible until load calculations have been performed." Articulating the invoice in this way I felt I was not entering an opinion either way, but pointing out a foundation had to be established before you could go foward. Having said that, for my own information can anyone tell how to adjust the CPH on a Honeywell T812D t/stat?