Sizing a freezer
I have a customer who wants to increase the tonnage on his walk in.currently it has a 7.5 ton & 5 ton the dimensions are 70' x 20' x 10' he s wanting to replace the 7.5 with a 10 ton. it s a meat locker they try and hold it at -10.the 5 ton is actually a back up to the 7.5. I m not experienced in sizing freezers. 10 tons = 120,000BTU/hr. From 8am to 5pm there s alot of traffic from customers so the rate of air change is triple that of normal walk ins. I guess what I m wanting to know is the formular for sizing the equipment. 14,000 ft/3 , @ 90 degree outside ambient, -10 to 0 range.any help would be appreciated.
Blessed is he who expects nothing, for he shall never be disappointed
-
11-20-2011, 10:15 PM #2
Try this for starters. A proper load calculation needs to be done or you will likely just be spinning your wheels.
http://www.uscooler.com/?q=refrigera...izing-estimate
-
11-23-2011, 06:13 PM #3
Regular Guest
- Join Date
- Sep 2011
- Location
- Plainfield IL
- Posts
- 101
You know how I size my freezers for the most part, I call Mike Mcgovern at United Refrigeration in Bensenville IL. at 630-521-9100. He will ask you questions like the surrounding box air temps, Type of door way, cooler panel thickness, Foam type, ect. He's good. They are very nice and helpful.
-
11-24-2011, 11:01 AM #4
If you are saying the customer currently has a 5 HP and 7.5 HP compressor, he most certainly does NOT have a 5 ton and 7.5 ton systems.
Best to check the compressor capacity chart and see what your actual capacity is. You will find for your application it quite different than 1 HP per ton.
-
11-24-2011, 11:23 AM #5
There are calculators in the Educational Forums.
http://hvac-talk.com/vbb/forumdisplay.php?f=205
11-24-2011, 07:35 PM #6
Professional Member
- Join Date
- Mar 2007
- Location
- Canada
- Posts
- 76
Thanks everyone
Blessed is he who expects nothing, for he shall never be disappointed
11-29-2011, 07:13 AM #7
Professional Member*
- Join Date
- Aug 2008
- Location
- S. Grand Prairie
- Posts
- 243
I usually do the load calcs myself but anytime I'm not sure, I stop by United (sort of like Fridge Repairer) and they have a form you can fill out and they will get the proper equipment spec'd out for you.